Posted: Tue Jul 27, 2010 10:05 pm Post subject: MODERATE EXPOSURE CONDITIONS AS PER IS:456-2000 |
|
|
Table-3 of IS:456 2000 describes Environmental Exposure Condition. in the same table the MODERATE exposure condition is explained as follows:
Concrete surfaces sheltered from severe rain or freezing whilst wet
Concrete exposed to condensation and rain
Concrete continuously under water
Concrete in contact or buried under non-aggressive soil/ground water
Concrete surfaces sheltered from saturated salt area in coastal area.
As per Table -5 of IS:456-2000
Minimum Grade of Reinforced Concrete for Moderate exposure is M25.
I have observed that some Engineers suggest
M25 concrete for Foundation,External columns,Peripheral beams and Roof slab and M2O concrete for Internal columns,internal beams and slabs other than roof slab in case of Moderate Exposure.
Do you agree or disagree ? _________________ P.K.Mallick
p.k.mallick1962@gmail.com
|
|
| Back to top |
|
 |
drnsmani General Sponsor


Joined: 26 Jan 2003 Posts: 1941 Location: Gaithersburg, MD, U.S.A.
|
Posted: Thu Jul 29, 2010 12:16 am Post subject: Re: MODERATE EXPOSURE CONDITIONS AS PER IS:456-2000 |
|
|
Dear Er Mallick,
As per ACI the min concrete strength is 27.5 MPa and as per BS it is M30(for moderate exposure). It may be difficult to adopt different grades of concrete for different elements of the building such as internal columns, beams, external beams, columns,etc. But it is common to have high strength column and normal strength beams and slabs.
Regards,
Subramanian
| P.K.Mallick wrote: | Table-3 of IS:456 2000 describes Environmental Exposure Condition. in the same table the MODERATE exposure condition is explained as follows:
Concrete surfaces sheltered from severe rain or freezing whilst wet
Concrete exposed to condensation and rain
Concrete continuously under water
Concrete in contact or buried under non-aggressive soil/ground water
Concrete surfaces sheltered from saturated salt area in coastal area.
As per Table -5 of IS:456-2000
Minimum Grade of Reinforced Concrete for Moderate exposure is M25.
I have observed that some Engineers suggest
M25 concrete for Foundation,External columns,Peripheral beams and Roof slab and M2O concrete for Internal columns,internal beams and slabs other than roof slab in case of Moderate Exposure.
Do you agree or disagree ? |
|
|
| Back to top |
|
 |
thirumalaichettiar General Sponsor


Joined: 26 Jan 2003 Posts: 1775
|
Posted: Thu Jul 29, 2010 5:13 am Post subject: |
|
|
Dear Er Mallick,
Technically what you stated is viable and can be made use of but as Dr.N.S pointed out the use of different grade to different elements in a structure will be a confusing and trouble some to control. But careful execution is possible.
There is no question of AGREEING OR DISAGREEING. It is a technical solution as per CODE and acceptable one.
If the soil is a contaminated with sulfate or other salts then use of SULPHATE RESISTANCE cement for footing and other grades for the rest of the structure is being used in GULF to take effective resistance to the sulfate contain soils.
It is good to use higher grade of concrete for axial members say columns and the lower grades for the beams and slabs. Specially use of higher grade for SLAB will be of little use due to the restriction of the spacing of reinforcement.
T.Rangarajan. |
|
| Back to top |
|
 |
hemal SEFI Member

Joined: 01 Apr 2008 Posts: 16
|
Posted: Fri Jul 30, 2010 7:14 am Post subject: MODERATE EXPOSURE CONDITIONS AS PER IS:456-2000 |
|
|
Dear Subramanian sir,
If we have different concrete grade for column and beam (say high grade for column and lower for beam), then how we can maintain higher grade for beam-column junction (joint) which is a critical part of column?
Regards
hemal
--- On Wed, 28/7/10, drnsmani <forum@sefindia.org> wrote:
| Quote: |
From: drnsmani <forum@sefindia.org>
Subject: [SEFI] Re: MODERATE EXPOSURE CONDITIONS AS PER IS:456-2000
To: general@sefindia.org
Date: Wednesday, 28 July, 2010, 1:46 PM
Dear Er Mallick,
As per ACI the min concrete strength is 27.5 MPa and as per BS it is M30(for moderate exposure). It may be difficult to adopt different grades of concrete for different elements of the building such as internal columns, beams, external beams, columns,etc. But it is common to have high strength column and normal strength beams and slabs.
Regards,
Subramanian
P.K.Mallick wrote: Table-3 of IS:456 2000 describes Environmental Exposure Condition. in the same table the MODERATE exposure condition is explained as follows:
Concrete surfaces sheltered from severe rain or freezing whilst wet
Concrete exposed to condensation and rain
Concrete continuously under water
Concrete in contact or buried under non-aggressive soil/ground water
Concrete surfaces sheltered from saturated salt area in coastal area.
As per Table -5 of IS:456-2000
Minimum Grade of Reinforced Concrete for Moderate exposure is M25.
I have observed that some Engineers suggest
M25 concrete for Foundation,External columns,Peripheral beams and Roof slab and M2O concrete for Internal columns,internal beams and slabs other than roof slab in case of Moderate Exposure.[/color:94cba95561]
Do you agree or disagree ?
|
Posted via Email |
|
| Back to top |
|
 |
rajmane SEFI Stars


Joined: 26 Jan 2003 Posts: 101 Location: Chennai
|
Posted: Fri Jul 30, 2010 11:41 am Post subject: MODERATE EXPOSURE CONDITIONS AS PER IS:456-2000 |
|
|
Normal 0 false false false MicrosoftInternetExplorer4 <![endif]--> <![endif]--> /* Style Definitions */ table.MsoNormalTable {mso-style-name:"Table Normal"; mso-tstyle-rowband-size:0; mso-tstyle-colband-size:0; mso-style-noshow:yes; mso-style-parent:""; mso-padding-alt:0pt 5.4pt 0pt 5.4pt; mso-para-margin:0pt; mso-para-margin-bottom:.0001pt; mso-pagination:widow-orphan; font-size:10.0pt; font-family:"Times New Roman"; mso-ansi-language:#0400; mso-fareast-language:#0400; mso-bidi-language:#0400;} <![endif]-->
Friday, 30 July 2010
Dear sefians
I feel it is too minor a point to discuss whether we should use M20 or M25. I feel we must use concretes with strengths as much higher as possible. Modern cement plants produce such good cements that we can get M35 and above easily with w/c ratio of about 0.50. Hence lower than M35 could mean higher w/c ratio which is not good for durability. To make the quality control measures meaningful particularly with reference to w/c, we must use very high strengths not from load carrying capacity but for denser microstructure considerations which would make the concrete to last for more number of years.
N P Rajamane
Secretary, Indian Concrete Institute, Tamil Nadu Centre, Retired Head, Advanced Materials Laboratory, CSIR-Structural Engineering Research Centre
--- On Thu, 29/7/10, drnsmani <forum@sefindia.org> wrote:
| Quote: |
From: drnsmani <forum@sefindia.org>
Subject: [SEFI] Re: MODERATE EXPOSURE CONDITIONS AS PER IS:456-2000
To: general@sefindia.org
Date: Thursday, 29 July, 2010, 0:16
Dear Er Mallick,
As per ACI the min concrete strength is 27.5 MPa and as per BS it is M30(for moderate exposure). It may be difficult to adopt different grades of concrete for different elements of the building such as internal columns, beams, external beams, columns,etc. But it is common to have high strength column and normal strength beams and slabs.
Regards,
Subramanian
P.K.Mallick wrote: Table-3 of IS:456 2000 describes Environmental Exposure Condition. in the same table the MODERATE exposure condition is explained as follows:
Concrete surfaces sheltered from severe rain or freezing whilst wet
Concrete exposed to condensation and rain
Concrete continuously under water
Concrete in contact or buried under non-aggressive soil/ground water
Concrete surfaces sheltered from saturated salt area in coastal area.
As per Table -5 of IS:456-2000
Minimum Grade of Reinforced Concrete for Moderate exposure is M25.
I have observed that some Engineers suggest
M25 concrete for Foundation,External columns,Peripheral beams and Roof slab and M2O concrete for Internal columns,internal beams and slabs other than roof slab in case of Moderate Exposure.[/color:94cba95561]
Do you agree or disagree ?
|
Posted via Email |
|
| Back to top |
|
 |
vikram.jeet SEFI Stars

Joined: 26 Jan 2003 Posts: 854
|
Posted: Fri Jul 30, 2010 12:13 pm Post subject: MODERATE EXPOSURE CONDITIONS AS PER IS:456-2000 |
|
|
Respected PK Mallick sir,
Since at site ,it is the Foremen and labour which work under tiring conditions and
specifying different grades of concrete for internal and external columns
may increase the chances of error on part of human and may not be
encouraged. However for beams and slabs on floor ,one mix, different than
column mix may not trouble .
Even as regards reinforcements for slabs, some design engineers , prefer to use
only one type dia of bars in RCC slabs on a floor to avoid chances of mixing of bars
by labour. (If 10mm dia is used for slabs ,its spacing is varied ).
These cares are being taken by designers due to fact that supervision is never
upto the desired standards and it is considered as QA measure at design
stage itself.
with kind regards
vikramjeet
-- ญญ
Posted via Email |
|
| Back to top |
|
 |
drnsmani General Sponsor


Joined: 26 Jan 2003 Posts: 1941 Location: Gaithersburg, MD, U.S.A.
|
Posted: Fri Jul 30, 2010 7:06 pm Post subject: Re: MODERATE EXPOSURE CONDITIONS AS PER IS:456-2000 |
|
|
Dear Dr Rajamane,
Glad to see your posting after a long gap. What you say is absolutely correct and important. Unless BIS specifies the minimum concrete strength as M30 or M35, people will continue to use M20 only.
Regards
Subramanian
Dear sefians
I feel it is too minor a point to discuss whether we should use M20 or M25. I feel we must use concretes with strengths as much higher as possible. Modern cement plants produce such good cements that we can get M35 and above easily with w/c ratio of about 0.50. Hence lower than M35 could mean higher w/c ratio which is not good for durability. To make the quality control measures meaningful particularly with reference to w/c, we must use very high strengths not from load carrying capacity but for denser microstructure considerations which would make the concrete to last for more number of years.
N P Rajamane
Secretary, Indian Concrete Institute, Tamil Nadu Centre, Retired Head, Advanced Materials Laboratory, CSIR-Structural Engineering Research Centre |
|
| Back to top |
|
 |
drnsmani General Sponsor


Joined: 26 Jan 2003 Posts: 1941 Location: Gaithersburg, MD, U.S.A.
|
Posted: Fri Jul 30, 2010 11:33 pm Post subject: Re: MODERATE EXPOSURE CONDITIONS AS PER IS:456-2000 |
|
|
Dear Er Hemal,
we have discussed about it earlier. Please browse.
You may also read my paper in ICJ
Subramanian, N., Transmission of HSC column loads through NSC slabs, The Indian Concrete Journal, Vol.80, No.1, Jan 2006, pp.44-49.
Best wishes,
NS
| hemal wrote: | Dear Subramanian sir,
If we have different concrete grade for column and beam (say high grade for column and lower for beam), then how we can maintain higher grade for beam-column junction (joint) which is a critical part of column?
Regards
hemal
--- On Wed, 28/7/10, drnsmani <forum@sefindia.org> wrote:
| Quote: |
From: drnsmani <forum@sefindia.org>
Subject: [SEFI] Re: MODERATE EXPOSURE CONDITIONS AS PER IS:456-2000
To: general@sefindia.org
Date: Wednesday, 28 July, 2010, 1:46 PM
Dear Er Mallick,
As per ACI the min concrete strength is 27.5 MPa and as per BS it is M30(for moderate exposure). It may be difficult to adopt different grades of concrete for different elements of the building such as internal columns, beams, external beams, columns,etc. But it is common to have high strength column and normal strength beams and slabs.
Regards,
Subramanian
P.K.Mallick wrote: Table-3 of IS:456 2000 describes Environmental Exposure Condition. in the same table the MODERATE exposure condition is explained as follows:
Concrete surfaces sheltered from severe rain or freezing whilst wet
Concrete exposed to condensation and rain
Concrete continuously under water
Concrete in contact or buried under non-aggressive soil/ground water
Concrete surfaces sheltered from saturated salt area in coastal area.
As per Table -5 of IS:456-2000
Minimum Grade of Reinforced Concrete for Moderate exposure is M25.
I have observed that some Engineers suggest
M25 concrete for Foundation,External columns,Peripheral beams and Roof slab and M2O concrete for Internal columns,internal beams and slabs other than roof slab in case of Moderate Exposure.[/color:94cba95561]
Do you agree or disagree ?
|
Posted via Email |
|
|
| Back to top |
|
 |
arunkashikar Wise Person

Joined: 14 Oct 2008 Posts: 59
|
Posted: Sat Jul 31, 2010 2:36 pm Post subject: MODERATE EXPOSURE CONDITIONS AS PER IS:456-2000 |
|
|
Different mix for column and beam/slab also creates one problem at our sites. Beam-column junction is often cast with lower grade concrete used for beam/slab which is not correct. Regards,Arun kashikar
- from VodafoneFrom: "vikram.jeet" <forum@sefindia.org>
Date: Sat, 31 Jul 2010 10:07:52 +0530
To: <general@sefindia.org>
ReplyTo: general@sefindia.org
Subject: [SEFI] Re: MODERATE EXPOSURE CONDITIONS AS PER IS:456-2000
Respected PK Mallick sir, Since at site ,it is the Foremen and labour which work under tiring conditions and specifying different grades of concrete for internal and external columns may increase the chances of error on part of human and may not be encouraged. However for beams and slabs on floor ,one mix, different than column mix may not trouble . Even as regards reinforcements for slabs, some design engineers , prefer to use only one type dia of bars in RCC slabs on a floor to avoid chances of mixing of bars by labour. (If 10mm dia is used for slabs ,its spacing is varied ). These cares are being taken by designers due to fact that supervision is never upto the desired standards and it is considered as QA measure at design stage itself. with kind regards vikramjeet -- ญญ --------------
Posted via Email |
|
| Back to top |
|
 |
Jalil A. Sheikh SEFI Member

Joined: 06 Dec 2008 Posts: 18
|
Posted: Sat Jul 31, 2010 3:31 pm Post subject: MODERATE EXPOSURE CONDITIONS AS PER IS:456-2000 |
|
|
Respected subramanian sir,
By selecting different mixes for column and beam/slab, say m-35 for column and m-25 for beam/slab, which concrete mix is ok for junction between column & beam.
Some seniors says that lower grade is ok for such junctions( i.e. m-25). According your views what is advisable?
J.A.Sheikh
From: drnsmani <forum@sefindia.org>
To: general@sefindia.org
Sent: Thu, 29 July, 2010 12:16:54 AM
Subject: [SEFI] Re: MODERATE EXPOSURE CONDITIONS AS PER IS:456-2000
Dear Er Mallick,
As per ACI the min concrete strength is 27.5 MPa and as per BS it is M30(for moderate exposure). It may be difficult to adopt different grades of concrete for different elements of the building such as internal columns, beams, external beams, columns,etc. But it is common to have high strength column and normal strength beams and slabs.
Regards,
Subramanian
P.K.Mallick wrote: Table-3 of IS:456 2000 describes Environmental Exposure Condition. in the same table the MODERATE exposure condition is explained as follows:
Concrete surfaces sheltered from severe rain or freezing whilst wet
Concrete exposed to condensation and rain
Concrete continuously under water
Concrete in contact or buried under non-aggressive soil/ground water
Concrete surfaces sheltered from saturated salt area in coastal area.
As per Table -5 of IS:456-2000
Minimum Grade of Reinforced Concrete for Moderate exposure is M25.
I have observed that some Engineers suggest
M25 concrete for Foundation,External columns,Peripheral beams and Roof slab and M2O concrete for Internal columns,internal beams and slabs other than roof slab in case of Moderate Exposure.[/color:94cba95561]
Do you agree or disagree ?
Posted via Email |
|
| Back to top |
|
 |
|
|
You cannot post new topics in this forum You cannot reply to topics in this forum You cannot edit your posts in this forum You cannot delete your posts in this forum You cannot vote in polls in this forum You can attach files in this forum You can download files in this forum
|
|
|