suraj General Sponsor
Joined: 17 Apr 2008 Posts: 5744 Location: NCR Faridabad, E mail suraj_engineer@yahoo.co.uk
Posted: Wed Dec 22, 2004 5:32 am Post subject: Some questions about concrete |
Structural concrete pour
Some simple practical questions about concrete for the budding engineers
Concrete of grade 35 or 40N is to be poured
Acceptable slump is 125+/- 25mm
Temperature of concrete 26 deg C
At delivery time slump is observed 200mm
What should be done? Reject or accept the truck?
Cubes fail on 7th day test. What should be done ?
What should be preferred for curing of concrete
Curing compound or water
Eng Suraj Singh PE
kagarwal SEFI Member
Posted: Wed Dec 22, 2004 9:04 am Post subject: Some questions about concrete |
Dear members. I am designing a 9 story building near noida. The site is rocky having bearing capacity around 21t/m^2. I am trying to proceed with isolated and combined footing as recommended by soil consultant. Is there any codal provision, restricting the use of isolated/combined footing in such cases. Thanks Kapish
-----Original Message----- Message From rccbuildings2@yahoo.co.uk [mailto:rccbuildings2@yahoo.co.uk] Sent: Wednesday, December 22, 2004 4:32 PM To: Kapish Agarwal Subject: Some questions about concrete
Eng Suraj Singh PE
--------------------------------- ALL-NEW Yahoo! Messenger - all new features - even more fun!
Posted: Wed Dec 22, 2004 10:17 am Post subject: Some questions about concrete |
It is suggested to design beams frame foundation for such case
kagarwal@desein.com wrote: Dear members. I am designing a 9 story building near noida. The site is rocky having bearing capacity around 21t/m^2. I am trying to proceed with isolated and combined footing as recommended by soil consultant. Is there any codal provision, restricting the use of isolated/combined footing in such cases. Thanks Kapish
Eng Suraj Singh PE
chordia1 SEFI Member
Posted: Wed Dec 22, 2004 11:14 am Post subject: Some questions about concrete |
There is no codal provision one can easily go in for combination of Isolated and Combined footing and to be more causious connect it with stiching slab.
sanjeevJain ----- Original Message ----- Message From <rccbuildings2@yahoo.co.uk> To: <chordia@del6.vsnl.net.in> Sent: Wednesday, December 22, 2004 3:50 PM Subject: Some questions about concrete
Quote: | It is suggested to design beams frame foundation for such case
Eng Suraj Singh PE
sidhudaljeet ...
Posted: Wed Dec 22, 2004 2:19 pm Post subject: Some questions about concrete |
Slump 200 is too much, 125 is also on heigher side, if you pump conc. it is all right. Take sample of the mix, just check how much water it has. simply dry the conc, this way you would be able to know the water cement ratio. since slump is very rough idea of water cement ratio. 7 days sample gennerally fails due to curing at low temp, if the ambient temp is above 30, 7 days strength should be allright. if water cement ratio comes much more than the specified, it might be poor conc. it should be rejected. Daljeet
Eng Suraj Singh PE
raju_goa SEFI Regulars
Posted: Wed Dec 22, 2004 3:56 pm Post subject: Some questions about concrete |
Hi Kapish, There is no codal provision restricting use of isolated / combined footings. You can opt for isolated footings and possibly combined footings if the footings overlap. It would be ideal to tie the columns at plinth level with plinth beams.
Shekhar Panandiker Goa.
James_Cohen SEFI Regulars
Posted: Wed Dec 22, 2004 4:10 pm Post subject: Some questions about concrete |
Dear Mr. Singh,
If the high slump and low strength results are for the same pour, the concrete should be rejected before additional construction takes place. If the specification called for a specific 7-day strength, this is usually done to provide the contractor with "advance notice" that there may be a problem. So, if the low-strength results are local, I would advise halting construction in that area until additional strength tests are completed. It is best to stop further construction until either 14-day test results can establish the adequacy of the concrete or to remove and replace the affected area. The contractor is unlikely to want to wait for 28-day results and you and the owner are unlikely to want additional construction to occur which may need to be removed or substantially altered. If the problem is endemic to the entire structure, the available choices are not good, but still need to be resolved.
An alternative approach is to re-analyze the structure with the lower results. Design is typically predicated on a rather high factor of safety, part of which is based on unknown material strengths and unknown construction tolerances. If these are known, as should be the case in your situation, these factors of safety are no longer required. It may be that the actual strength is still adequate to provide the required residual factor of safety. In situ testing may also help to establish that the concrete does have the necessary strength to remain with little or no strengthening.
James Cohen, PE James Cohen Consulting, PC http://expertpages.com/jccpc
rajmane ...
Posted: Thu Dec 23, 2004 2:07 pm Post subject: Some questions about concrete |
23rd Dec 2004 Dear all (1)" Concrete of grade 35 or 40N is to be poured, Acceptable slump is 125+/- 25mm, Temperature of concrete 26 deg C,
At delivery time slump is observed 200mm" I think the concrete need not be rejected provided the increased slump does not cause any construction problems. It is almost to produce concrete every time with the same slump. This is a fact. I think more emphasis should be on parameters such as : (a) cohesiveness, (b) non-seggregability, (c)no excessive bleeding, (c) Correct setting property, etc. (2) "Cubes fail on 7th day test". The reasons for this should be studied in any particular case. Some parameters to be looked into are: Change in cement and admixture type and content (b) Change in materials, (c) Actual curing regime followed, (d) Method of testing, loading rate etc, (d) Status of test specimen, defects if ant in specimen, (e) Calibration of testing machine. etc. If all these can be satisfactorily looked into, then, NDT on structures including core sampling should be considered. 7 day strength is only an indicator and not the final criterion for acceptance or rejection of concrete as per IS:456-2000. (3) "What should be preferred for curing of concrete, Curing compound or water" Water curing must be always preferred. However, with expert supervision (not usual normal supervision), curing compound can be used. Any project engineer/site supervisor should develop a proper quality check and application methodology.
(4) The suggestion of "simply dry the conc, this way you would be able to know the water cement ratio" is not rational. This way w/c can not be determined. I do not know in which reference/standard published works, this suggestion is available. Drying (in hot air oven) causes further hydration of cement and this does not get reflected in weight loss. we can send endlessly on the problems/difficulties in accepting this suggestion. I draw the attention of Neville's one paper in Concrete International where he hoped that some day some body will find acceptable/correct way to find w/c of fresh concrete after it is mixed.
Thank you all
N P Rajamane Deputy Director and Head, CCL, SERC, CSIR, Chennai 600113 Ph: 22549152 (O), 24417882 (R), 9840076821 Fax: 22541508
Posted: Thu Dec 23, 2004 3:52 pm Post subject: Some questions about concrete |
Dear Sir, Impressed by the your explanation Eng Suraj Singh PE
rajmane@sercm.csir.res.in wrote: 23rd Dec 2004 Dear all (1)" Concrete of grade 35 or 40N is to be poured, Acceptable slump is 125+/- 25mm, Temperature of concrete 26 deg C,
Thank you all
vikramjeet SEFI Member
Posted: Wed Dec 29, 2004 6:46 am Post subject: Some questions about concrete |
Dear kapish
Isolated Footings are economical vis -a - other type of footings / Raft.However, since the structure is located in Zone - 4 It is advisable to tie the isolated footigs at foundatioin Level itself in both directions .Tie beams will also take care of Moments at footing LvL due to gravity loads & Seismic.
Jeet