Welcome to the Econference on Design and Construction of Tal
Goto page 1, 2, 3  Next
alpa_sheth
PostPosted: Mon Nov 19, 2012 3:22 am    Post subject: Welcome to the Econference on Design and Construction of Tal Reply with quote
Dear All:
Greetings and welcome to the E-conference on Design and Construction of Tall Buildings in India. As has been mentioned earlier the conference will run Nov. 19 through Nov 28.
A few pointers on Econference protocol.
* All topics pertaining to Tall Buildings may be discussed and we will  urge all of you to participate in adding value to a topic with informed and well-thought out comments so as to maintain the  standard of the Econference to international quality. We request that you please keep your subject note or comment on an issue crisp and  topical.
* Any issues which are not core to the technical part of the Econference may please be discussed on the SpeakOut forum, not in the Econference, please.
* Kindly limit  discussions to   max of two issues pertaining to tall buildings  in a single mail. The issues should be in different paragraphs. Also, when differing with another commentator, pl exercise utmost civility while expressing  your disagreement.
We had suggested some topics for discussion and we had received valuable input from all of you. We have incorporated your suggestions and produced a revised list as under. This is not an exhaustive list and other pertinent technical issues can be added as required.
We have a list of subject experts for the Econference. We will introduce them along the way. We look forward to some exciting days ahead.....
warm regards,
Alpa Sheth
Prof CVR Murry
Prof Swaminathan Krishnan
Econference Moderators
Topics for Tall Buildings Conference
What do we define as a tall building?
a)      Siting of tall buildings:
      i Where are tall buildings allowed/not allowed to be sited?
b)      Geotechnical  Issues
  •   Soil Testing for Tall Buildings.
  •   Testing for establishing soil and pile modulus
c)      General Parameters of Tall Buildings
  •  Geometric Proportioning
  •  Height and Aspect Ratio
  •  General Distribution and area of  Vertical  and Lateral load carrying elements as % of plan area for concrete and steel structures.
  • Min required stiffness of building
  • Perimeter offset to avoid pounding
d)       Structural Configuration, Structural Systems and their Behaviour
  •   Selection of Structural system- Preliminary behavior analysis   of alternative systems
  • Discussion of Strucutral Sustems- Frames, Shear Walls, Frame-Shear Walls, Slab-Column Shear Wall structure, Tube Stucture, Hybrid Structure.....
  •   Performance of different structural systems;
  •   What levels of ductility are achievable in the lateral force resisting systems being constructed in India?  What should the value of R be?
  • Hybrid Structural Systems and their behaviour
  •  Achieving  redundancy and alternative load path
d)      Load Combinations
e)       Use of Masonry partition walls in tall buildings
  •  Should they be included in  analysis?
  •  Should they be isolated from structure or not?
  •  Any special specifications for partition walls of  tall buildings?  (Light weight etc.)
f)      Modeling and Analysis
  • Appropriate Modelling tools and soft ware for elastic, inelastic design for different systems and elements
g)      Structural Irregularities
  • Should structural system transfer be allowed in tall buildings? If yes what are the limitations to be observed?
  • Soft storey, Weak Storey
  • How to deal with torsional irregularity? How much max  modal mass may be excited in torsional modes of vibration?
h)        Wind Design
  •  When should Wind Tunnel Testing be carried out?
  • What are the wind tunnel  tests that should be carried out and to what effect?  How to account for future buildings in the neighborhood in the layout and configurtion of adjacent buildings in the wind tunnel?
  • What are the results to be asked from the WT testing agency?
  • Appropriate Damping Values
  • Discussion on Wind Dampers- When to use them, What type to use for what building application?
  • Should there be instrumentation on tall buildings for measurement of vibrations/accelerations?
i)        Earthquake Analysis and Design
  • Does the current IS 1893 assure acceptable performance of tall buildings?
  • Seismic hazard characterization (base shear, response spectrum, ground motion histories, near-source effects, fault maps, fault classification w.r.t. earthquake potential characterization).
  • Site soil characterization.
  • Closely spaced modes-How critical is this issue?
  •   Linear static analysis procedure.
  •  Dynamic response spectrum procedure.  What should the spectrum look like?  When should a site-specific spectrum be required?  How to account for near-source effects (applies to linear static procedure as well)?
  • When should one do non-linear analysis? What are the earthquake ground motions to be considered in Indian scenario?
  •  How to properly account for P-Delta effects (modeling gravity columns)?  Do we have software for nonlinear analysis readily available?  Are test data  characterizing component nonlinear (cyclic) behavior using prevailing Indian standards of practice available?  What should the material models look like for various structural components?
  •  When is a pushover analysis required?
j)        Frame Structure -Ductile detailing criteria:
  • ·   What criteria and when applicable?
  • ·   Strong-column weak beam in moment frames
  • ·    boundary elements in shear walls
  • ·    tie-spacing
  • ·    135 degree hooks
  • ·    lap-splices and development length
  • ·    location of splices
  • ·    beam-column joint detailing in concrete frames
  • ·    continuity of column vertical rebar and beam longitudinal rebar through the joint
  • ·    link beam detailing (diagonal rebar)
  • ·    required level of diaphragm attachment on either side of a given length of wall, etc.
  • ·   When and where is Capacity Design required?
  •   Column (gravity/lateral) design (include long-term axial shortening of columns due to creep and its effects on beams/floor slabs, etc.);
  •  Use of composite sections for creep control.
k) Shear Wall
  • Wall design (include long-term axial shortening due to creep)
  •   Link beam design
  •  Diaphragm design
l) Energy dissipation devices
  • viscous fluid dampers
  • added stiffness and damping devices
m)       Use of Precast in Tall Building Construction
  • Should it be permitted?
  • To be used for which  elements of structure?
  • Design and detailing of joints?
  • Behaviour in past earthquakes
n)        Foundations
a.       Discussion on Piled raft foundations
·   Allowable deformations
·   Pile-raft interaction
·   Analysis of piled rafts
.   Shoring for Deep Basements
·   Pile testing for deep piles
·   Max allowable deformation of piles of piled raft- codal provisions?
·   Deformations in piled raft?
·   Differential settlement between core and perimeter.  Provide a pour strip to minimize such settlement (when to provide).  Additional moments in beams and slab due to such differential settlement.
·   Design methodology and detailing of piles and rafts; lateral shear capacity of piles, vertical load carrying capacity of piles (skin friction vs bearing).
b.      Raft  foundations for tall buildings
c.       Pile foundations for Tall buildings
o)    Facades
  • Stiffness
  • Isolation;  Designing the façade system to permit movement corresponding to wind and seismic drift limits.
p)      Tall Building with Podium issues
  • Should tower be connected to Podium?  When?
  • Should Basement walls be considered in Analysis?
  •  Any special considerations to cater for large shear transfer in the podium diaphragm from tower? (refer ATC)
q)      Performance Criteria
  • Serviceability Requirements
  • What should be the limiting acceleration values for human comfort level in wind design?
  • What is max drift to be allowed in wind and earthquake?  What can be the sudden spike in interstorey drift due to a soft/weak storey?
r)      Performance Based (Seismic) Design of Structures
  • When to do this?
  • How to do it?
  • Review Procedures ....
s)      Other Detailing Aspects of Tall Buildings
  •  Detailing of cold joints (Core and floor slab done separately)
  • Dealing with congestion of steel
  • Splices/Anchorages
  • Expansion Joint issues
  • Seismic joints:  When to use and how to design.
  • Design of Inclines Columns, Bracings etc.
t)       Construction Issues of Tall Buildings
  • Modular/Lightweight shuttering
  • Slipform Shuttering
  • High strength concretes – Issues of microcracking, delayed strength, additives, flyash, silica fumes etc.
  • High Grade Steel- Inconsistency in yield stress.
  • Dealing with congestion of steel  in beam-column joints
  • Vertical Transportation of concrete
  • Durability of Tall Buildings- How to repair/retrofit?
  • Concrete grade of columns vs. concrete grade of slabs – How to deal with difference?
u)       Construction Specifications
  • Materials (including welds, rebar, concrete, structural steel, etc.)
  • Structural, Mechanical, Electrical, Plumbing, Vertical Transportation systems
  • Site preparation and managementa
v)        Green Building Issues
Econf_Moderator
E-Conference Moderator
PostPosted: Mon Nov 19, 2012 3:26 am    Post subject: Welcome to the Econference on Design and Construction of Tal Reply with quote
Dear All:
warm regards,
Alpa Sheth
Prof CVR Murry
h)        Wind Design
  • ·    tie-spacing
k) Shear Wall
  •   Link beam design
  •  Diaphragm design
n)        Foundations
o)    Facades
  • Stiffness
  • When to do this?
  • How to do it?
napeera
PostPosted: Mon Nov 19, 2012 4:15 am    Post subject: Welcome to the Econference on Design and Construction of Tal Reply with quote
Dear all,It is my privilege to be a member of this very highly professional and knowledgeable forum from which I have benefited a lot. 5 stars from me for starting this very informative E-Conference, which will help immensely, the structural engineers who must have just started designing tall structures.My first question will be.  What is the definition of Tall Building in detail?Regards & best of luck. NAPeera - from Vodafone
Date: Mon, 19 Nov 2012 09:00:03 +0530
To: <econf34289@sefindia.org>
ReplyTo: econf34289@sefindia.org
Subject: [E-CONF] Welcome to the Econference on Design and Construction of Tall bUildings
     Dear All:    Greetings and welcome to the E-conference on Design and Construction of Tall Buildings in India. As has been mentioned earlier the conference will run Nov. 19 through Nov 28.    A few pointers on Econference protocol.    * All topics pertaining to Tall Buildings may be discussed and we will  urge all of you to participate in adding value to a topic with informed and well-thought out comments so as to maintain the  standard of the Econference to international quality. We request that you please keep your subject note or comment on an issue crisp and  topical.    * Any issues which are not core to the technical part of the Econference may please be discussed on the SpeakOut forum, not in the Econference, please.    * Kindly limit  discussions to   max of two issues pertaining to tall buildings  in a single mail. The issues should be in different paragraphs. Also, when differing with another commentator, pl exercise utmost civility while expressing  your disagreement.    We had suggested some topics for discussion and we had received valuable input from all of you. We have incorporated your suggestions and produced a revised list as under. This is not an exhaustive list and other pertinent technical issues can be added as required.    We have a list of subject experts for the Econference. We will introduce them along the way. We look forward to some exciting days ahead.....    warm regards,   Alpa Sheth  Prof CVR Murry Prof Swaminathan Krishnan    Econference Moderators    *********************                Topics for Tall Buildings Conference     What do we define as a tall building?  a)      Siting of tall buildings:         i Where are tall buildings allowed/not allowed to be sited?  b)      Geotechnical  Issues
d)      Load Combinations   e)       Use of Masonry partition walls in tall buildings
h)        Wind Design
  • ·    tie-spacing
  k) Shear Wall
  •   Link beam design
  •  Diaphragm design
n)        Foundations  a.       Discussion on Piled raft foundations  ·   Allowable deformations  ·   Pile-raft interaction  ·   Analysis of piled rafts  .   Shoring for Deep Basements    ·   Pile testing for deep piles   ·   Max allowable deformation of piles of piled raft- codal provisions?  ·   Deformations in piled raft?  ·   Differential settlement between core and perimeter.  Provide a pour strip to minimize such settlement (when to provide).  Additional moments in beams and slab due to such differential settlement.  ·   Design methodology and detailing of piles and rafts; lateral shear capacity of piles, vertical load carrying capacity of piles (skin friction vs bearing).  b.      Raft  foundations for tall buildings  c.       Pile foundations for Tall buildings       o)    Facades
  • Stiffness
  • When to do this?
  • How to do it?
       v)        Green Building Issues          --
dssri
PostPosted: Mon Nov 19, 2012 5:50 am    Post subject: Welcome to the Econference on Design and Construction of Tal Reply with quote
1. How do we define a tall building - absolute height, aspect ratio, method of construction or the sesimic zone it is situated
2. Permission to go ahead with a tall building - Any regulation needed to restrict the construction of tall buildings only to builder/developer/contractor having prior experience
god bless
D S SRIDHAR
ME, FIE, FIV, AMP (IIM)
G 908 Mantri Tranquil
Sy. No. 7/9/13 Gubalala
Kanakapura Road
BANGALORE 560061
KARNATAKA INDIA
CELL +91-9845094486
dssri64@gmail.com (dssri64@gmail.com)
sridhar.ds@alumni.iimb.ernet.in (sridhar.ds@alumni.iimb.ernet.in)
-- Original Message --
To: econf34289@sefindia.org (econf34289@sefindia.org)
Sent: Monday, November 19, 2012 11:00 AM
Subject: [E-CONF] Re: Welcome to the Econference on Design and Construction of Tal
Dear All:
warm regards,
Alpa Sheth
Prof CVR Murry
h) Wind Design
  • · tie-spacing
k) Shear Wall
  • Link beam design
  • Diaphragm design
n) Foundations
o) Facades
  • Stiffness
  • When to do this?
  • How to do it?
Engineer
PostPosted: Mon Nov 19, 2012 6:06 am    Post subject: Econference on Design and Construction of Tall Blgds - Seism Reply with quote
I have attached herewith draft document prepared by CTBHU Committee on Seismic Design of Tall Buildingswww.ctbhu.org
Hemant Gor
CTBHU_Guide_Sesimic_Design_of_Tall_bldgs.pdf
 Filename:  CTBHU_Guide_Sesimic_Design_of_Tall_bldgs.pdf
 Filesize:  1.99 MB
 Downloaded:  741 Time(s)
prasadam_iitm
PostPosted: Mon Nov 19, 2012 6:33 am    Post subject: Welcome to the Econference on Design and Construction of Tal Reply with quote
On 19-Nov-2012, at 11:00 AM, Econf_Moderator wrote:
Dear All:
warm regards,
Alpa Sheth
Prof CVR Murry
h) Wind Design
  • · tie-spacing
k) Shear Wall
  • Link beam design
  • Diaphragm design
n) Foundations
o) Facades
  • Stiffness
  • When to do this?
  • How to do it?
Meher Prasad Anumolu
Professor, Department of Civil Engineering
IIT Madras
prasadam@iitm.ac.in (prasadam@iitm.ac.in)
drferozkottamal
PostPosted: Mon Nov 19, 2012 8:52 am    Post subject: Welcome to the Econference on Design and Construction of Tal Reply with quote
How to check safety against overturning, what should be the height aspect ratio, geometric proportioning...
On 19 November 2012 06:30, alpa_sheth <forum@sefindia.org (forum@sefindia.org)> wrote:
           Dear All:
warm regards,
Alpa Sheth
Prof CVR Murry
h)        Wind Design
  • ·    tie-spacing
k) Shear Wall
  •   Link beam design
  •  Diaphragm design
n)        Foundations
o)    Facades
  • Stiffness
  • When to do this?
  • How to do it?
ishacon
Silver Sponsor
Silver Sponsor
PostPosted: Mon Nov 19, 2012 10:15 am    Post subject: Welcome to the Econference on Design and Construction of Tal Reply with quote
It is indeed very heartening to see that this Econf has kicked off with
Welcome Notes from eminent engineers and Professors.
Permit me to voice some of my concerns in general.
Having been involved in Design audits of several tall buildings ( 75 meter height and above),
in NCR region during last more than a decade, I have seen at close quarters the dire
need of improvement in preparation of the drawings and careful checking thereof.
Shortage of trained manpower for checking and the copy, paste routines of CAD by the draftsmen
leave many errors untraced.
This practice needs to be stopped at the consultant's end.
Due to the urgencies imposed by the Builder / developer, often the Structural Consultant
is compelled to perform the analysis based on half baked inputs from the Architect and he
has to issue foundation drawings with column schedules without having gone through detailed
investigations on analysis front since the excavation is already done. Often the soil investigation reports
do not do full justice to the testing and making appropriate recommnedations.
It is about time, that everyone in the industry recognise the perils of doing so.
V.P. Agarwal
B.Tech (IITMadras), M.Engg (USA)
ISHA CONSULTANTS (P) LTD
NEW DELHI 110074
PH : 011-2630 1158 ;
08010071749 ; 093 1345 2180
Sent: Monday, November 19, 2012 3:00 PM
:  Dear All:
warm regards,
Alpa Sheth
Prof CVR Murry
h) Wind Design
  • · tie-spacing
k) Shear Wall
  • Link beam design
  • Diaphragm design
n) Foundations
o) Facades
  • Stiffness
  • When to do this?
  • How to do it?
IIT Madras
prasadam@iitm.ac.in (prasadam@iitm.ac.in) (prasadam@iitm.ac.in (prasadam@iitm.ac.in))
BJREDDY
PostPosted: Mon Nov 19, 2012 11:20 am    Post subject: Reply with quote
Dear All
My best wishes to SEFI organizers for creating this excellent platform for sharing knowledge about tall buildings. I am much excited and enthusiastic to participate in this E-conference.
I would like to share this document prepared by CTBUH, which will basically explain
"Criteria for the Defining and Measuring of Tall Buildings".
Thanks & Regards,
BJReddy
CTBUH_Height Criteria.pdf
 Filename:  CTBUH_Height Criteria.pdf
 Filesize:  843.43 KB
 Downloaded:  968 Time(s)
partha at adaptsoft.com
Guest
PostPosted: Mon Nov 19, 2012 11:21 am    Post subject: Welcome to the Econference on Design and Construction of Tal Reply with quote
Thank you for starting such an informative session. While I go through the topic I have following comments:
1. What should be ideal classification of Tall Building?
2. About Material, let us talk more Steel and Post Tension Concrete. As use of Reinforced Concrete will reduce the head room (for the presence of beam and thicker slab) and increase the building weight thus experience higher magnitude of Seismic Force.
3. Can we have a single document (according to the topics) containing details at the end of the conference?
Partha Pratim Roy
Vice President (Technical)
ADAPT Concrete Software
www.adaptsoft.com
Dear All:
warm regards,
Alpa Sheth
Prof CVR Murry
h) Wind Design
  • · tie-spacing
k) Shear Wall
  • Link beam design
  • Diaphragm design
n) Foundations
o) Facades
  • Stiffness
  • When to do this?
  • How to do it?
Page 1 of 3