Hi friends,
i have 6.50m (s.s.beam 200x600mm) carrying 42.74 kn/m udl. My deflection check from formula 5WL4/384EI gives me value 1.38mm which is less than SPAN/350 that is 18.57mm.is ok. But my software RAPT which gives me warning that total deflection is greater than user define limit which is 20mm bydefault.It shows me 4 value of deflection.
1.Transfer deflection = 1.15 mm 2.Short term deflection = 17.4 mm 3.Incremental deflection = 14.2 mm 4.Total long term deflection = 28 mm
My question is deflection check from 5WL4/384EI is valid that is 1.38mm, shall i have to still increse section size by 200x750mm which gives me 18.5 mm total deflection value less than 20mm given by software. Shall we check according to total long term deflection not by 5WL4/384EI VALUE???
Best regards Dipesh dipeshtanuja[AT]red...
satyam SEFI Member
Posted: Tue Dec 26, 2006 4:05 am Post subject: Deflection check |
Mr. Dipesh,
we shall check the deflection limit w.r.to Total Deflection value only. The deflection calculated through the formaula (5WL4/384EI)is Elastic deflection. Span/350 is the limit for the longterm deflection due to Permanent loads. Span/250 is the limit for the long term deflection due to Dead+Live loads.
Regards Satyanarayana.J
-----Original Message----- Message From dipeshtanuja[AT]red... [mailto:dipeshtanuja[AT]red...] Sent: Sunday, December 24, 2006 11:56 PM To: Satyanarayana J Subject: Deflection check
Hi friends,
DISCLAIMER: This Message and its contents is intended solely for the addressee and is proprietary.Information in this mail is for L&T Business Usage only. Any Use to other than the addressee is misuse and infringement to Proprietorship of L&T ECC.If you are not the addressee please return the mail to the sender.L&T ECC DIVISION