SEISMIC JOINTS

 
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion
View previous topic :: View next topic  
Author Message
kishorpss
General Sponsor
General Sponsor


Joined: 22 Aug 2010
Posts: 153
Location: GUJARAT

PostPosted: Wed Mar 06, 2019 5:12 am    Post subject: SEISMIC JOINTS Reply with quote

Dear Senior Sefians,

I am requesting all to through light on the above subject.

Design of a large size building of G+2 storied is under progress. Due to its large plan area, it is divided into 10 parts with separation joints.

As per clause 7.11.3 separation between Adjacent units of IS 1893 (Part1): 2016, the calculated separation gap joints are coming 450 mm.

Sefians are requested to provide solutions to overcome the problem.

Thanks in advance.

Kishore
Back to top
View user's profile Send private message
sukanta.adhikari
General Sponsor
General Sponsor


Joined: 26 Jan 2003
Posts: 726

PostPosted: Thu Mar 07, 2019 5:32 am    Post subject: Re: SEISMIC JOINTS Reply with quote

del

Last edited by sukanta.adhikari on Mon Mar 11, 2019 4:10 am; edited 1 time in total
Back to top
View user's profile Send private message
mjnasar
...
...


Joined: 26 Jan 2003
Posts: 72

PostPosted: Thu Mar 07, 2019 10:54 am    Post subject: Reply with quote

Dear Engs,

Please correct the following case ( IS 1893 (Part1): 2016)

Supposing:

G+1 Assume as 8mtsmax height

Response ReductionFactor = 3 ( OMRF)

Deflection ofbuilding as per Ch 6.4.3 ( elastic deformation from analysis program  for Service combinations )

Say Max allowableDeflection  or Storey  drift = 0.004* 8000 = 32mm

The Separation Gap Should beas per 7.11.3

( R1 delta1 + R2 delta 2) = (3 * 32 + 3 * 32 )  = 192mm max

Regards


Back to top
View user's profile Send private message
structuralprashant
SEFI Member
SEFI Member


Joined: 11 May 2011
Posts: 11

PostPosted: Mon Mar 11, 2019 6:45 pm    Post subject: Re: SEISMIC JOINTS Reply with quote

sukanta.adhikari wrote:
del

Dear fellow members,
In my opinion it will be suitable to provide the gap as per requirement and bridge it with flexible or easily yielding material, so that impact of one part is not carried to the adjoining structures. Er. Patwe
Back to top
View user's profile Send private message
kishorpss
General Sponsor
General Sponsor


Joined: 22 Aug 2010
Posts: 153
Location: GUJARAT

PostPosted: Tue Mar 12, 2019 10:01 am    Post subject: Reply with quote

Dear Er. mjnasar,

Allowable drift is 0.004%. For the 1mtr height of the building, allowable drift is 4mm of each side. Hence for 1mtr height, allowable thickness of separation joint is ((4mm+4mm)*5) 40mm considering Response reduction factor as "5". For the total height of the building of 10.00mtr separation gap thickness required is 400mm.


Dear Er. prashant,
I need to know the flexible or easily yielding material used in the present scenario.


Thanking you.


KISHORE
Back to top
View user's profile Send private message
structuralprashant
SEFI Member
SEFI Member


Joined: 11 May 2011
Posts: 11

PostPosted: Wed Mar 13, 2019 6:25 pm    Post subject: Reply with quote

Dear fellow member, Just send the cad file showing positions of structural members, so that it will be possible to suggest a solution. patweconsultant@gmail.com
Back to top
View user's profile Send private message
kishorpss
General Sponsor
General Sponsor


Joined: 22 Aug 2010
Posts: 153
Location: GUJARAT

PostPosted: Sat Mar 16, 2019 11:51 am    Post subject: Reply with quote

Dear Er. Prasanta,

Please check mail.

Brgds,

KISHORE
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion All times are GMT
Page 1 of 1

 

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


© 2003, 2008 SEFINDIA, Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service. advertisement policy