Mean of the Group of 4 Non-Overlapping Consecutive Test Results In N/mm^2
Er. Surya
PostPosted: Mon Apr 29, 2019 7:10 am    Post subject: Mean of the Group of 4 Non-Overlapping Consecutive Test Results In N/mm^2 Reply with quote
Dear SEFI Forum Members.
Request your kind advice on how to group the average results obtained from mean of 3 cube specimens
say.
CUBE 1
CUBE 2
AVG SAMPLE 1
CUBE 3
CUBE 4
CUBE 5 AVG SAMPLE 2
CUBE 6
CUBE 7
CUBE 8 AVG SAMPLE 3
CUBE 9
CUBE 10
CUBE 11 AVG SAMPLE 4
CUBE 12
CUBE 13
CUBE 14 AVG SAMPLE 5
CUBE 15
CUBE 16
CUBE 17 AVG SAMPLE 6
CUBE 18
CUBE 19
CUBE 20 AVG SAMPLE 7
CUBE 21
CUBE 22
CUBE 23 AVG SAMPLE 8
CUBE 24
Now the grouping of AVG SAMPLE will be...HOW?
1st non overlapping AVG SAMPLE (1+2+3+4)
2nd non overlapping AVG SAMPLE (2+3+4+5)
               OR
2nd non overlapping AVG SAMPLE (5+6+7+8)
Thanks in advance.
badamsundararao
PostPosted: Tue Apr 30, 2019 2:38 am    Post subject: AVERAGE Reply with quote
To my opinion average is required for set of three only and no need to go for further average.Elders have to confirm this.
es_jayakumar
PostPosted: Tue Apr 30, 2019 2:54 pm    Post subject: Reply with quote
IS Code 456 : 2000 stipulates :
16 ACCEPTANCE CRITERIA
16.1 Compressive Strength
The concrete shall be deemed to comply with the strength requirements when both the following condition are met:
a) The mean strength determined from any group of four consecutive test results compiles with the appropriate limits in col. 2 of Table 11.
b) Any individual test result complies with the appropriate limits in co1 3 of Table 11.
Going by "any group of four consecutive test results " in the above, the groups (1,2,3,4), (2,3,4,5), (3,4,5,6),....etc. shall hold good.
However, the heading of Col.2 of Table 11 stipulates "Mean of the Group of
4 Non-Overlapping Consecutive Test Results". Here, "Non-overlapping" creates confusion.
Ashok K. Jain, in his book "Reinforced Concrete - Limit State Design", in Example No.2.7.(c), has adopted moving mean of 4 results, ie., (1,2,3,4), (2,3,4,5), (3,4,5,6),....etc.
es_jayakumar
PostPosted: Tue May 14, 2019 1:31 am    Post subject: Reply with quote
No further comments / clarifications were seen posted here, on this topic. A spread sheet prepared for checking the acceptance criteria as per the Codal provisions (moving mean concept) is attached.
Mix Design (Acceptance Criteria) .xls
 Filename:  Mix Design (Acceptance Criteria) .xls
 Filesize:  35 KB
 Downloaded:  772 Time(s)
TPS61
PostPosted: Wed May 15, 2019 10:29 am    Post subject: acceptance criteria for cube strengths Reply with quote
The codal clause is quite clear. As stated by Jayakumar, the consecutive groups to be examined are (1,2,3,4), (2,3,4,5),(3,4,5,6) etc.
The average of each of these groups must meet the stated criteria.
es_jayakumar
PostPosted: Fri May 17, 2019 2:21 am    Post subject: Reply with quote
Sir,
What does the term "non-overlapping" in "Mean of the Group of 4 Non-Overlapping Consecutive Test Results" [Col.2 of Table 11] indicate ? This creates confusion.
TPS61
PostPosted: Fri May 17, 2019 3:29 am    Post subject: acceptance criteria for cube strengths Reply with quote
I agree, the language is confusing.
I go by Logic which is : "average of any 4 consecutive strength results should...."
Er. Surya
PostPosted: Fri May 24, 2019 12:25 pm    Post subject: Reply with quote
Dear Members of SEFI
Request your kind views on Explanation of acceptance criteria on page- ( Page - 34,35,36,37,38 ) of SP-24
on page 37 of SP -24 towards the end (a) it states.
if  every  sample  is  to  the  right  of  C,
accept  each  of  the  sample.  (see  Fig.  E-3)
Where when referred C = Fck Characteristic Strength which for M25 would be 25 N/mm^2 after 28 days curing.
es_jayakumar
PostPosted: Tue Jul 30, 2019 2:59 am    Post subject: Re: acceptance criteria for cube strengths Reply with quote
But, Dr.N.Subramanian, in his book on Reinforced Concrete Design (PP-132) says "test result of one group should not be taken in another group too". This stresses on "non-overlapping" requirement.
 Filesize:  142 KB
 Viewed:  50 Time(s)
es_jayakumar
PostPosted: Thu Oct 31, 2019 3:08 am    Post subject: Reply with quote
Yesterday, I clarified as per "Correction slip No.1 to IS 456 : 2000" that "non-overlapping" has been added in Cl.16.1 (a) too.
Now it is clear that we have to take the sequence (1,2,3,4), (5,6,7,8 ), (9,10,11,12),....etc. BS EN 206: 2013 permits the use of either, but cautions that in case of adopting  overlapping test results, the risk of rejection is more. A work sheet prepared accordingly is enclosed. The previous one posted by me may be discarded.
Acceptance Criteria for Design Mix 30.10.2019.xls
 Filename:  Acceptance Criteria for Design Mix 30.10.2019.xls
 Filesize:  44.5 KB
 Downloaded:  27 Time(s)
