Dear All,
Can somebody please share a design example for Flag post.
A 12m high flag post is to be erected with a flag of 1m (H) x 3m (W).
i have tried using ANSI/NAAMM FP 1001-07, and i get section size of 168.3mm Dia and 5mm thick.
Is the above section going to be adequate or is it too big.
Advise on the above will be helpful.
rgds
|
|
Back to top |
|
|
es_jayakumar General Sponsor
Joined: 24 Nov 2011 Posts: 1408 Location: Cochin
|
Posted: Thu Dec 26, 2019 4:22 pm Post subject: |
|
|
I hope, the flag will not impart any torsion / BM / shear to the post, as the same will orient itself in the direction of the wind (parallel to wind). Thus, the flag post can be designed as a cantilever steel beam acted upon by wind load. The wind load can be computed using Table 25 of IS 875 (Part 3) : 2015 [Design Loads (Other than Earthquake) for Buildings and Structures — Code of Practice Part 3 Wind Loads].
1. Assume a trial diameter for the steel post (tube).
2. Calculate the wind load per metre run using Table 25 of the Wind Code, for a circular section, by finding the appropriate value of Cf.
3. Calculate the maximum BM for the post as a cantilever and design the section as a beam.
4. If the self weight of the pole is significant, design as a beam-column, for the combined BM and axial load.
E S Jayakumar
|
|
Back to top |
|
|
prakash chitale SEFI Member
Joined: 08 Jan 2011 Posts: 1
|
Posted: Fri Dec 27, 2019 8:30 am Post subject: FLAG POST |
|
|
It is correct size
On Fri, 27 Dec 2019, 12:22 pm husseins20, <forum@sefindia.org (forum@sefindia.org)> wrote:
Quote: | Dear All,
Can somebody please share a design example for Flag post.
A 12m high flag post is to be erected with a flag of 1m (H) x 3m (W).
i have tried using ANSI/NAAMM FP 1001-07, and i get section size of 168.3mm Dia and 5mm thick.
Is the above section going to be adequate or is it too big.
Advise on the above will be helpful.
rgds
|
Posted via Email
|
|
Back to top |
|
|
es_jayakumar General Sponsor
Joined: 24 Nov 2011 Posts: 1408 Location: Cochin
|
Posted: Sun Dec 29, 2019 6:59 am Post subject: |
|
|
A rough design of the flag-post in question, without considering the self weight of the mast & dynamic wind effects is attempted. Experts please check it guide.
E S Jayakumar
Description: |
|
Filesize: |
223.05 KB |
Viewed: |
487 Time(s) |
|
|
|
Back to top |
|
|
es_jayakumar General Sponsor
Joined: 24 Nov 2011 Posts: 1408 Location: Cochin
|
Posted: Wed Jan 01, 2020 2:25 am Post subject: |
|
|
Dear Er.Hussein,
Please see the attached Article by Dr.N.Subramanian on the design of flag poles. As per this, the wind load on the flag is also to be considered in the design. An empirical formula for calculating the wind load on flag is also given. You can design your flag pole by taking into consideration the wind force on the flag also, using the mentioned formula. [ The quantum of this is found to be meagre, though]
Best wishes,
E S Jayakumar
Warning: Make sure you scan the downloaded attachment with updated antivirus tools before opening them. They may contain viruses. Use online scanners here and here to upload downloaded attachment to check for safety.
|
Description: |
|
Download |
Filename: |
Design & Construction of Flag Posts.pdf |
Filesize: |
182.41 KB |
Downloaded: |
884 Time(s) |
|
|
Back to top |
|
|
husseins20 ...
Joined: 25 Apr 2013 Posts: 62
|
Posted: Fri Jan 03, 2020 8:54 am Post subject: Flag Post |
|
|
Thank you for your valued input.
Do we also need to satisfy l/r for this. since the pole will be as a cantilever, minimum r to satisfy le/r = 133mm thus 406.4 Dia 6mm thick would be required. Is this check also required to be satisfied?
|
|
Back to top |
|
|
Dr. N. Subramanian General Sponsor
Joined: 21 Feb 2008 Posts: 5538 Location: Gaithersburg, MD, U.S.A.
|
Posted: Fri Jan 03, 2020 7:06 pm Post subject: Re: Flag Post |
|
|
Dear Er Hussein
Yes. you need to check the pole considering it as a cantilevered column.
see Clause 6.7 of ANSI/NSSMM FP 1001-07 Guide Specification for the Design of Metal Flagpoles, which can be downloaded from https://law.resource.org/pub/us/code/bsc.ca.gov/sibr/org.naamm.FP_1001-07.pdf
It also has sample calculations
Hope you also read my article, posted by my friend Er E.S. Jayakumar.
Best wishes
NS
husseins20 wrote: | Thank you for your valued input.
Do we also need to satisfy l/r for this. since the pole will be as a cantilever, minimum r to satisfy le/r = 133mm thus 406.4 Dia 6mm thick would be required. Is this check also required to be satisfied? |
|
|
Back to top |
|
|
es_jayakumar General Sponsor
Joined: 24 Nov 2011 Posts: 1408 Location: Cochin
|
Posted: Sat Jan 04, 2020 1:26 am Post subject: |
|
|
Dear NS Sir,
Thanks for your guidance. The major vertical load on the pole is its own self weight and the eccentricity due to this will be practically nil. However, when it deflects laterally under wind force, then the resulting deflection will laterally translate the CG of the self weight ( at mid height) and this will cause some eccentricity with respect to its base. This has to be taken care of, I think.
Regards,
E S Jayakumar
|
|
Back to top |
|
|
Dr. N. Subramanian General Sponsor
Joined: 21 Feb 2008 Posts: 5538 Location: Gaithersburg, MD, U.S.A.
|
Posted: Sat Jan 04, 2020 3:05 am Post subject: |
|
|
Dear Er Jayakumar
Yes. You are right. The document quoted by me also has sample calculations at the end.
Warm regards
Subramanian
es_jayakumar wrote: | Dear NS Sir,
Thanks for your guidance. The major vertical load on the pole is its own self weight and the eccentricity due to this will be practically nil. However, when it deflects laterally under wind force, then the resulting deflection will laterally translate the CG of the self weight ( at mid height) and this will cause some eccentricity with respect to its base. This has to be taken care of, I think.
Regards,
E S Jayakumar |
|
|
Back to top |
|
|
renold jose kurian SEFI Member
Joined: 14 Jun 2022 Posts: 1
|
Posted: Thu Jul 06, 2023 6:11 am Post subject: |
|
|
es_jayakumar wrote: | A rough design of the flag-post in question, without considering the self weight of the mast & dynamic wind effects is attempted. Experts please check it guide.
E S Jayakumar |
do we have to consider the flag load? kindly advice any reference
|
|