Load bearing Masonry building Design
Goto page Previous  1, 2, 3
 
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion
View previous topic :: View next topic  
Author Message
vikram.jeet
General Sponsor
General Sponsor


Joined: 26 Jan 2003
Posts: 3835

PostPosted: Sun Jul 18, 2021 3:52 am    Post subject: Reply with quote

LOAD BEARING MASONRY BUILDINGS

Since stepped footings of masonry  are continuous strip foundation
,it has better resistance to unequal settlements as compared to isolated column foundations.

However , it is always wise to introduce  rcc columns , even of small dimensions to take care of point loads at following locations:

Front Balcony - The cantilever beams carrying Balcony load exert additional reaction at cantilever ends in form of M/L effect. Also the cantilever beam must continue at back to at least twice the cantilever span to have adequate FOS against overturning. Rcc column at cantilever face of beam shall be introduced to protect masonry excessive masonry stresses at root of cantilever.

Corridors , if more than  single storey , needs to be supported on rcc columns . For single storey corridors brick piers can easily support.

Large openings , or a no of openings like windows and doors in succession in a wall with small brick pillars available between doors and window. The front walls having such openings with much less brickwork area , needs to be supported on rcc columns with rcc beam over wall .

Hall having  longer walls without any cross walls. It is better to introduce rcc columns at about 3 to 3.5m. Though wall in which these columns are sandwiched are gravity load bearing, for EQ in its orthogonal dir , rcc column to be designed to take entire EQ.
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion All times are GMT
Goto page Previous  1, 2, 3
Page 3 of 3

 

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


© 2003, 2008 SEFINDIA, Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service. advertisement policy