PostPosted: Fri Jul 23, 2021 10:27 am    Post subject: Field Engineering Building+General+Soil+Quality+Testing Fresh Concrete on Site Reply with quote
External Works & Utilities-Chapter 7+Quality+Testing Fresh Concrete on Site
MS27
Index
Scope/Reference documents/Definitions/Responsibilities/Safety/Method/Equipment/Attachments
Scope
1     Purpose of this method statement, is to define procedure that shall be adopted for onsite testing of fresh concrete, delivered from Batching plant.
Reference documents
1     Project Specification concrete related
Safety & Responsibilities
1     Refer to safety general description on page 1
Method
Material delivery
1     Site Laboratory shall be informed of concreting program, by providing one copy of project specifications.
2     Each delivery of concrete to site, shall report to concrete Foreman/QC.
3     Concrete Foreman shall assist laboratory technician in testing fresh concrete delivery.
4     Delivery ticket shall first be checked for correct grade and type of concrete.
5     Specific point to be examined on delivery docket to ensure that time of discharge from batching plant & time of reaching/arriving truck to site does not exceed than whatever maximum prescribed
6     Testing on site shall be conducted for following properties
a     Concrete slump- should be within prescribed limits, respecting crane or pump pouring, because for both cases, slumps are different. More value of slump is permissible, when concrete is poured using pump
b     Concrete temperature- should be within specified limits, generally 5 deg C to 32 deg C
c     Air voids- should not exceed than defined
Pumping
1     Truck mixer shall discharge its delivery into concrete pump only after, all such site tests are completed.
2     Or Upon commencement of a pour, concrete pump operator shall flush pump line with fresh concrete.
3     Initial small discharge quantity from concrete pump line shall be discarded.
4     A sample of concrete circulated through concrete pump, shall be taken from end of concrete pump line. Pumping operation shall then cease, until laboratory technician has completed required testing.
5     Temperature of concrete sample shall be determined, according to ASTM C1064.
6     A slump of concrete sample shall be conducted, according to ASTM C143.
7     These details shall be recorded upon test record format QC.
8     Once, these test results have been established conforming to specification requirements, concrete pumping operation can proceed
9     Subsequent deliveries of fresh concrete shall follow a similar procedure.
10     Exemption being that initial discharge of subsequent truck mixers shall not be discarded.
11     Laboratory technician shall take concrete samples from random truck mixers, for purpose of filling concrete test cubes.
12     Frequency of these concrete test cubes shall be three cubes per 100 cubic meters of delivered concrete.
13     Additional concrete cubes shall be taken, as directed by laboratory manager for conducting further tests upon hardened cubes, as defined within specifications.
Equipment
1     Truck Mixer/Concrete Pump/Slump Cone/Thermometer/Cube moulds
1     ITP #
suraj
PostPosted: Fri Jul 23, 2021 10:39 am    Post subject: Field Engineering Building+General+Soil+FIDICSilver-Quality+Replacement of Misaligned Anchor Bolts in Foundation Refer Reply with quote
External Works & Utilities-Chapter 7+Quality+Replacement  of Misaligned Anchor Bolts  in Foundation Reference Indicatively 55-vv-906, Using Renderoc Lax Tra - Delicate Repair
Index
Scope
1     Objective of this statement is to propose procedures to be adopted to carry out replacement to foundation damaged anchor bolts. Foundation comprises of RCC material
Reference Documents
1     Method Statement # approved for concrete repairs Item F (Renderoc Lax Tra FOSROC) or equivalent, per approvals
Method
1     2# Anchor bolts installed for this RCC foundation were damaged post concrete pouring & therefore, damaged anchor bolts are required to be removed & replaced by new anchor bolts
Following operations are involved to reinstate anchor bolts into foundation
1     Effected concrete portion shall be removed in a triangular form from foundation corners in an approximate prismatic shape of base 250mmx200mm and height of prism 600mm approximately.
2     During breaking concrete, care shall be taken not to damage reinforcing bars. Suitable breaker shall be used for purpose of breaking concrete
3     Exposed reinforcing bars shall be properly cleaned, using hard brush, so that no loose particles remain intact to rebar surface
4     Surface of broken concrete shall be cleared  of  all debris and  new bolts installed in correct locations
5     Forms shall be erected to correct profile, aligned, properly leveled and plumbed.
6     Chamfer at edges shall be aligned properly.
7     Form and concrete surface shall be properly sealed, using silicon sealant material to avoid leakage from poured renderroc laxtra material
8     Civil Contractor QC inspection shall be conducted to ascertain correct alignment of anchor bolts and forms
9     Then prepared surface shall be soaked in water for 24 hours, prior to grouting by chemical mortar
10     Material shall be mixed with specified quantity of clean water, according to meeting manufacturer’s instruction and poured in layers not exceeding 200 mm thick each
11     Civil Contractor QC inspection shall be conducted, throughout pouring operation
12     After approval of repair works and giving allowance of specified number of days, further operations shall be carried out
Major Equipment
1     Peddle Mixer
2     Concrete breaking tool
1     None
suraj
PostPosted: Fri Jul 23, 2021 11:23 pm    Post subject: Field Engineering Building+General+Soil+FIDICSilver-Quality Reply with quote
24.07.2021-Civil Field Engineering + Quality AnnexSL + COVID-19 + HSE Engineers Role + Designs + Construction + Methods + Contracts + Organisations + Communication + Coordination + Why be behind Quality of Concrete Standard Material? Talk 431
https://www.facebook.com/pesuraj/videos/1015234352613704
suraj
PostPosted: Sat Jul 24, 2021 9:44 am    Post subject: Field Engineering Building+General+Quality++Fixing Sheeting Panels Wall & Roof Cladding Reply with quote
External Works & Utilities-Chapter 7+Quality+Fixing Sheeting Panels Wall & Roof Cladding
MS29
Index
Scope
1     Objective of this Statement is to propose procedures to be adopted to Fix Roof And Wall Metal Panels for various structures to be Cladded
1     Refer to safety general description on page 1 & in addition
2     In this case, excavation has to be carried out on Operating Authority area
3     Therefore all regulated precautions shall be strictly adhered to effect ‘Full Safety Standard’.
Reference
1     Specification (Metals) for fasteners,
Material
2     MAR Formawall for wall panels,
3     Trisomet for Roof Panels, Profile EP3-Corrugated steel sheet (Single Skin)- by European Profiles (BS/ HHR)
4     Three types of panels shall be used as follows
1     Maintenance Building-Roof Panels- Trisomet, Wall Panels- Formawall Flat
2     Car Parks- Corrugated Cladding
3     Work shall be carried out by M/S ………
Method
Preparation
1     Prior to commencement of sheeting operations, structural items, including door posts and parapet etc. shall be lined and leveled properly to requirements within acceptable tolerances
2     Wind brace clips shall be removed and building cleaned
3     All necessary documentations i.e.  Check List, RFI etc. shall be completed and submitted, prior to work commencement
4     Civil Contractor QC inspection shall be conducted to ensure that structural elements are aligned, leveled and fixed to specified requirement
5     Installation shall be carried out in accordance with provisions included within specifications
Fixing Roof Panels
1     Valley gutters shall be fixed and aligned
2     Internal ridge flashing shall be fixed in position
3     Insulated Trisomet panels shall be fixed starting from valley, rising to ridge and all fixings/accessories fastened on crown, meeting to specification requirement
4     All end laps shall be cleaned of all dust, dirt etc. & sealed, complying to manufacturer’s instructions with mastic to prevent capillary humidity rise
5     Procedure shall be repeated for parapet wall by fixing and aligning gutter
6     External ridge flashing shall be fixed
7     Entire roof shall be brush cleaned and colour caps fixed
8     Civil Contractor QC inspection shall be conducted throughout above operations to ITP requirements
Fixing Formawall Flat Panels
First Tier
1     Drip flashing shall be fixed at base of wall to be used, as a straight datum line
2     First formawall vertical panel shall be fixed to true plumb and fastened by steel screws throughout joints
3     Next panel fixed along side of first panel, by providing a tight vertical joint & process repeated, until end is reached
4     Special flashing shall be fixed to entire length of first tier of vertical panels
Second Tier
1     Second tier of blue panels shall be fixed in same manner, as lower panel
2     Procedure shall continue, until all sides are completed
3     Special corner flashing shall be used/included/provided internally and externally to give an aesthetic finish at corner joints
4     Civil Contractor QC inspection shall be conducted throughout above operations to ITP requirements
Car Park
Corrugated cladding
1     Single long panel shall be fixed & fastened to straight end of structure through crown, with one and a half profile overlapped on sides and mastic inserted between sheets
2     Procedure shall be continued to curve, where sheets are to be racked and cut to provide roof curvature
3     Entire roof shall be brush cleaned and colour caps inserted
5     Walls
Field Check for water leakage
1     Upon completion of installation, walls shall be checked for Water Penetration in accordance with AAMA standard 501.2-83
2     ‘Field check of Metal Curtain Walls for water leakage’ on designated area
Site Clearance
1     All debris & excess material shall be removed, making sure that no weep holes and drainage channels are unobstructed and free of dust and sealants
Equipment
1     Man Lift
2     Electric Drills
1     M/S subcontractor’s method statement ref….
2     MAR approval reference…..
3     Note-QA Documentation Formats…../shall be submitted separately
suraj
PostPosted: Sat Jul 24, 2021 9:50 am    Post subject: Field Engineering Building+General+Quality++HDPE Pipes Butt Fusion Reply with quote
External Works & Utilities-Chapter 7+Quality+HDPE Pipes Butt  Fusion
MS30
Index
Scope
1     Objective of this Statement is to propose procedures to be adopted to carry out welding by fusion at joints, between HDPE pipes using COSMOPLAST/equivalent/advanced PE jointing technology
1     All safety means recommended by manufacturer COSMOPLAST/or equivalent (refer to page 14 & 35 on catalogue) as well as, required to be adopted by regulations shall be adhered to
Material
1     Pipes & fittings (COSMOPLAST or equivalent)
Method
Electrofusion-Precautions
1     A check shall be made about pipes to be joined are of same size to Standard Dimension Ratio (SDR) and consistent/competent material.
2     Only, compatible material shall be used
3     Butt fusion machine shall be located/sited on a suitable clean, dry baseboard or ground inside a shelter to minimize contamination and wind effect
4     It shall be ensured that Control Box Voltage is compatible with fitting
5     Alignment/restraining clamps shall be used
6     Pipe ends shall be cut square for electrofusion sockets
7     Pipe or spigot surfaces shall be scraped fully, while surfaces & fittings kept clean
8     It shall be ensured that correct fusion & cooling times/hours are adhered to
9     Joint shall be assembled & fused immediately, after scraping pipe
10     Joint shall be completed in one go
11     Fitting shall not be allowed to be taken out of protective bags
12     Dirty fittings shall not be used
13     Prepared pipe surfaces shall not be touched
14     Assemblies shall not be allowed to get dampen, before joining
15     During welding/fusion cycle, weld shall not be touched
16     Joint shall not be removed from clamp, unless full cooling time has elapsed
17     Integral cutter shall not be removed from saddle, once main has been drilled
Pre jointing checks
1     Only, regularly serviced equipment in good condition shall be used
2     It shall be ensured that correct joining parameters for machine and pipe being welded are known and clearly, understood
3     It shall be ensured that generator has sufficient/adequate quantity of fuel for duration of programmed work.
4     Heater plate should be cleaned or washed, using only clean and cold water, and dried out with a clean lint free cloth or paper towel
5     A check shall be made to ascertain that trimmer is clean with undamaged blades in good condition
6     It shall be ensured that clamp liners and securing screws of correct size are available for size of pipe to be joined.
7     Lines must be clean and should sit fully in pipe clamps to ensure correct alignment.
8     A check shall be made to ensure that heater plate is at correct temperature
9     Correct parameters shall be selected for pipes to be joined
Making Joint
1     In an emergency, ‘Red Stop Reset Button’ when put off, shall stop all automatic cycles and set machine safe and return to start of cycle
2     Dummy weld shall be made to remove all fine particles from heater plate, before every welding session, after changing from one pipe size to another  pipe size & also, if heater has been allowed to cool
Connection & Pipe selection
1     Heater, chassis and trimmer cables shall be connected to computer
2     After ensuring that hydraulic connections are clean, connection shall be made to controller
3     Generator shall be started & computer connected to generator
4     Pipe to be connected shall be selected
5     Data shall be confirmed
Pipe Preparation
1     Pipe Preparation shall be carried out, according to description given on page on manufacturer’s catalogue
Making weld
1     Making weld shall be carried out, according to description on page on manufacturer’s catalogue
2     Quality checks shall be conducted, according to description on page
3     All Do’s described on page 13 shall be followed and don’ts on page 14 avoided
4     Joint assembly preparation shall be carried out to indicative description on page
5     Pressure testing of joint shall be conducted, complying to indicative description on page
Quality Check
Quality shall be checked to indicative description on relevant page of datasheet/catalogue Check (Butt Fusion)
1     That fusion indicators have risen, while fitted
2     That no melted material or wire has exuded from fitting
3     That pipe has not moved from fitting
4     That area around joint is clean
5     Evidence of scraping shall be checked
6     That saddles are square on pipe
7     That print out is taken from control box and result checked
In case, weld fails, following checks shall be required,
1     For sockets, joint shall be cutout and use another fitting
2     For saddles, main shall not be taped, but a repeat weld carried out, using a new fitting at least 200mm from failed joint
3     Civil Contractor QC inspection shall be conducted throughout above operations, as required according to ITP and procedures
Major Equipment
1     Generator, Electrofusion Control Box, Restraining & alignment equipment, Welding tent/shelter & ground sheet, Scraping equipment, Pipe cutter, Indelible Marker pen
1     Cosmoplast Method Statement
suraj
PostPosted: Sat Jul 24, 2021 9:54 am    Post subject: Field Engineering Building+General+Quality+Roof & Side Cladding Plant Area Reply with quote
External Works & Utilities-Chapter 7+Quality+Roof & Side Cladding Plant Area
MS31
Index
Scope
1     Purpose of this Method Statement is to define sequence and methodology that shall be implemented for installation of Roof and Side cladding on mentioned structures.
Reference Documents
1     CENTRIA Drawings – CR-56 Roofing/Single Skin
Definitions
1     EF                 Erection Foreman.
2     EF shall control workforce, ensuring full implementation of this Method Statement including all safety measures.
Method
Materials receivables
1     All cladding material to be used for permanent works shall be received on site on to appropriate lay down area.
2     Items shall be inspected against necessary shipping documents.
3     All cladding shall be checked for quantity and identification.
4     Materials shall be properly stored and protected.
Fasteners (bolts, nuts & washers)
1     Upon receipt on site required fasteners, a minimum of one sample shall be selected and tested by an independent laboratory to confirm that it meets specification conformance.
Installation of cladding: Roof and Side cladding
Cladding sheets shall be installed as follows
1     One by one from scaffolds and working platforms.
2     Install in accordance with approved erection drawings and instructions.
3     All panels shall be erected left to right, unless otherwise noted.
4     Panel cutoffs shall be made, after all material is erected.
5     All cutting and notching of panels around windows, doors, louvers etc. shall be done on site, using right/suitable compatible tools as listed.
6     All edge cuts shall be coated with clear spar varnish.
7     All bevel and notch cutting of panels shall be made on site.
8     All panels notched around beams and channel shall be flashed properly.
(for further details see enclosed Method Statement from Centria manufacturer)
Construction sequence of side & roof sheeting
1     Monitor on roof shall be sheeted first.
2     East and West sides shall follow, then North and South sides, including flashing in fills.
3     Roof and Flashings (corner) shall be last items to be installed.
Erection of sheeting (side)
1     Erection of side sheeting shall be lifted from ground between floor beams and side girts, since sheets are too long to lower from roof, because of being in one piece.
2     North side scaffolding shall be installed from ground floor and regarding laydown area, EPC Contractor Construction team shall provide.
Equipment
1     Drilling Machines          2 #s
2     Screw Guns               2 #s
3     Screw Gun Sockets          2 #s
4     Rivet Gun               1 #s
5     Nibbler               1 #s
6     Double Cut Shear          1 #s
7     Jigsaw                          1 #s
8     Vice Grips               2 #s
9     Sheet metal Snips          1 #s
10     Extension Cords 2 x 50m     3 #s
11     Drill bits               10 #s
1     Scaffolding erection of side sheet
suraj
PostPosted: Sun Jul 25, 2021 1:27 am    Post subject: Field Engineering Building+General+Soil+FIDICSilver+SHE+Electrics+Welding Reply with quote
25.07.2021-Civil Field Engineering + Quality AnnexSL + COVID-19 + HSE Engineers Role + Designs + Construction + Methods + Contracts + Organisations + Communication + Coordination + Why be behind Quality of Concrete Standard Material? Talk 433
https://www.facebook.com/100000185425294/videos/184661720352540
suraj
PostPosted: Sun Jul 25, 2021 7:13 am    Post subject: Engineering-Sales, Products & Quality Reply with quote
I have been concerned with Quality Issues, not because I treat myself an expert of that discipline, but I consider that Quality is a Must, because seller charges for quality also, within price
It is a fundamental right of a customer to be provided with required quality
Manufacturer or industrialist do not do any obligation on their part in favour of customer. Simple equation is that Customer pays & manufacturer sells
Why should then bad quality products be accepted or be manufactured
This is a top burning question & also, this relates to all field of engineering
I have very bad experience of purchases simple products from internationally reputed organisers.
Recent examples, when I bought online on Microtech UPS for my computer, I paid demanded sale price & got delivery
Having installed it, it failed in just 7 days of installation
I complained & one part was replaced, blaming on voltage fluctuations
Till, order is delivered, many SMS are received, which is a good informative issue, but my requirement is not SMS, but Quality product
That UPS again broke during warranty period of 2 years.
I placed an order of 2 # HP wired mouses online & got delivery
When started using, one mouse did not work at all.
I sent a mail to agent of HP, but no reliable response, which made ma angry & to write scolding language to them
Then, after being helpless, I wrote to HP & they could not understand.
Then one mail was received that you have to write to someone else.
I got a call after that directed writing & disputed with them, because they again asked my what problem was
Means there exists no one in that section, even to read mails clearly
Again, I with high pitch language, explained to them & they asked me to contact agent, which raised my temperature & I shouted on them that it is your responsibility & solve it
After, received a mail, through, which they tried to teach me to talk politely & again I responded that you deserve such treatment
I wrote back & forced them that you have to do it
They asked me to go to their service centre, which further irritated me
Then I did it, but my visit failed to get me any result
Then I wrote to them a bombarding mail & asked them to get their Quality Certification copy
Really, I was too upset with functioning of quality system on products sales
I told then that you are not functioning, per quality certification, because you failed to check functioning of product, prior to packing
I told them that I shall impact your certificate & I was serious
Later, I got a mail that management is thinking to replace it & it would take 2 weeks
Then they tried to refer to another wireless mouse & not wired mouse
I replied to them that I required wired mouse
No solution reached till now
I am informing this to your guys, because I do not find any degree of seriousness of quality anywhere, whether it be construction of manufacturing or industry
Current generation is mobile born, air conditioned born, & they do not know impact of Sun & Thunderstorm
If there is no meaning of checking products, before delivery, where does quality exist?
It exists only in papers & customer is least bothered about papers
Quality Product is demanded & not SMS or packing
Swift service is demanded to replace bad products
It is not fault of customer, but seller or manufacturer
There are so many other instances that we face every day & you too may be facing, but seriousness nowhere exists
Construction in Civil engineering is number 1 dominating world, where no quality exists & people just talk a lot & do very little
Engineering Institutions failed everywhere to organise quality on products
Engineers have failed drastically, as far as, quality organisation is concerned
Whole team depends only on engineers!
It is only engineers that an change scenario or else!!!!!
suraj
PostPosted: Sun Jul 25, 2021 7:39 am    Post subject: List of My Videos effective 15.07.2019 to 25.07.2021on FB+Others Reply with quote
These videos have been classified as Engineering, COVID-19 & others
These vary in duration/s from few minutes to few hours
SurajVideoRecordsFB-IEIApplicationStatusJuly25,2021.docx
List of My Videos effective 15.07.2019 to 25.07.2021 on FB+Others
 Filename:  SurajVideoRecordsFB-IEIApplicationStatusJuly25,2021.docx
 Filesize:  336.09 KB
 Downloaded:  29 Time(s)
suraj
PostPosted: Sun Jul 25, 2021 11:16 am    Post subject: Field Engineering Building+General+Soil+Quality+Ethylene Export Foundations along Fence, Below ‘Fertil Overh Reply with quote
External Works & Utilities-Chapter 7+Quality+Ethylene Export Foundations along Fence, Below
‘Fertil Overhead Conveyor for Pipe Rack Leading to Sea
MS32
Index
Scope
1     Objective of this statement is to outline procedures to be adopted to carry out construction of proposed pipe rack foundations located along fence, from near PS 2061 below ‘Fertil overhead conveyor’ & up to sea for Ethylene export facility
Reference
1     Pipe Supports GA & RC Details Foundations
2     In this case, excavation has to be carried out on Operating Authority area. Therefore all regulated precautions shall be strictly adhered to effect ‘full safety standard’.
Method (sketch # 20 indicatively)
1     Required permit to work shall be obtained from Plant Refinery Division.
2     Record drawings, regarding existing services shall be obtained.
Procedures
1     These foundations shall be located 3m off existing Sulphur Plant fence towards conveyor. Location is just for indicative information only
2     Layout for proposed foundations shall be set out by surveyor to design requirement
3     Civil Contractor QC shall inspect layout & approve
4     Hand excavation shall be carried out to expose all live cables & other services, by employing seaming procedure, using detectors in involved area, to discover existence of live cables
5     Remaining portion of trench shall also, be excavated manually to defined levels
6     All post excavation operations shall be carried out, according to approved procedures, such as preparation of Formation Levels, Blinding Concrete, Formwork, Placing Steel Reinforcement, Anchor Bolts Fixing, Noncritical Cathodic Protection, Concrete Pouring, Concrete Curing, Application of Concrete Protection, Backfilling etc.
7     Civil Contractor QC inspections shall be conducted to Checklists & ITP requirement from time to time
Major Equipment
1     Compactors, Concrete pump, Compressor, Shovel etc
1     Drawing Copies
Page 87 of 155