Posted: Mon Apr 25, 2022 12:45 pm Post subject: |
vikram.jeet wrote: | Modelling in staad
Since illiterate I.e. not proficient in CAD designs ,just a layman's view :
Pl model piles as pinned supports for raft.
Model raft as tank base slab along with modelling of walls
Apply inside loadings
Also see tank empty case with outside loadings
Hope other members may guide u more explicitly , vividly and more candidly.. |
dear sir how earthquake analysis will be done for this tank ? will earthquake will effect majorly or not? as no procedure is there for such tank resting underground.... |
Posted: Tue Apr 26, 2022 8:18 am Post subject: |
Dear Er
EQ effects need to be taken in design , both under tank full conditions as well as tank empty conditions.
Fluids exert hydrodynamic pressure in tank full case .
The earth pressures from surrounding soil also higher under EQ .
Pl apply such loadings , either as additional loads during EQ , or in staad facility is there to apply directly such loadings.
Some other members proficient in software can guide u , better. |
pvgraju ...
Posted: Tue Apr 26, 2022 10:02 am Post subject: tube settler clarifier |
Piles can be modelled as springs with stiffness of allowable load/allowable deflection.
Seismic provisions to be as per IS-1893-PART-1,IS-1893-PART-2,IS-1893-PART-2-AMD-1.
Provisions for ground supported are applicable for this also.
Design as per IS-3370-2021-PART 1 TO 4.
P.V.Gavarraju. |
Posted: Tue Apr 26, 2022 12:55 pm Post subject: Re: tube settler clarifier |
pvgraju wrote: | Dear Sir,
P.V.Gavarraju. |
dear sir can some one provide sample stad file with pile raft design? |
Posted: Thu May 12, 2022 10:40 am Post subject: Re: tube settler clarifier |
P.V.Gavarraju. |
Posted: Thu May 12, 2022 10:50 am Post subject: tube settler clarifier |
dear sir i have modeled and analyzed
further my doubts are would these spring final reaction and moments wcan i use to calculate no. of piles and reinforcement. Take a look in this model |
Posted: Wed May 18, 2022 12:37 pm Post subject: tube settler clarifier |
STAAD SPACE
START JOB INFORMATION
ENGINEER DATE 29-Apr-22
END JOB INFORMATION
INPUT WIDTH 79
INPUT WIDTH 79
UNIT METER KN
JOINT COORDINATES
1 0 0 0; 2 0.5 0 0; 3 1 0 0; 4 1.5 0 0; 5 2 0 0; 6 2.5 0 0; 7 3 0 0; 8 3.5 0 0;
9 4 0 0; 10 4.5 0 0; 11 5 0 0; 12 0 0 -0.900001; 13 0.5 0 -0.900001;
14 1 0 -0.900001; 15 1.5 0 -0.9; 16 2 0 -0.9; 17 2.5 0 -0.9; 18 3 0 -0.9;
19 3.5 0 -0.9; 20 4 0 -0.9; 21 4.5 0 -0.9; 22 5 0 -0.9; 23 0 0 -1.8;
24 0.5 0 -1.8; 25 1 0 -1.8; 26 1.5 0 -1.8; 27 2 0 -1.8; 28 2.5 0 -1.8;
29 3 0 -1.8; 30 3.5 0 -1.8; 31 4 0 -1.8; 32 4.5 0 -1.8; 33 5 0 -1.8;
34 0 0 -2.7; 35 0.5 0 -2.7; 36 1 0 -2.7; 37 1.5 0 -2.7; 38 2 0 -2.7;
39 2.5 0 -2.7; 40 3 0 -2.7; 41 3.5 0 -2.7; 42 4 0 -2.7; 43 4.5 0 -2.7;
44 5 0 -2.7; 45 0 0 -3.6; 46 0.5 0 -3.6; 47 1 0 -3.6; 48 1.5 0 -3.6;
49 2 -1.5 -3.6; 50 2.5 -1.5 -3.6; 51 3 -1.5 -3.6; 52 3.5 0 -3.6; 53 4 0 -3.6;
54 4.5 0 -3.6; 55 5 0 -3.6; 56 0 0 -4.5; 57 0.5 0 -4.5; 58 1 0 -4.5;
59 1.5 0 -4.5; 60 2 -1.5 -4.5; 61 2.5 -1.5 -4.5; 62 3 -1.5 -4.5; 63 3.5 0 -4.5;
64 4 0 -4.5; 65 4.5 0 -4.5; 66 5 0 -4.5; 67 0 0 -5.4; 68 0.5 0 -5.4;
69 1 0 -5.4; 70 1.5 0 -5.4; 71 2 -1.5 -5.4; 72 2.5 -1.5 -5.4; 73 3 -1.5 -5.4;
74 3.5 0 -5.4; 75 4 0 -5.4; 76 4.5 0 -5.4; 77 5 0 -5.4; 78 0 0 -6.3;
79 0.5 0 -6.3; 80 1 0 -6.3; 81 1.5 0 -6.3; 82 2 0 -6.3; 83 2.5 0 -6.3;
84 3 0 -6.3; 85 3.5 0 -6.3; 86 4 0 -6.3; 87 4.5 0 -6.3; 88 5 0 -6.3;
89 0 0 -7.2; 90 0.5 0 -7.2; 91 1 0 -7.2; 92 1.5 0 -7.2; 93 2 0 -7.2;
94 2.5 0 -7.2; 95 3 0 -7.2; 96 3.5 0 -7.2; 97 4 0 -7.2; 98 4.5 0 -7.2;
99 5 0 -7.2; 100 0 0 -8.1; 101 0.5 0 -8.1; 102 1 0 -8.1; 103 1.5 0 -8.1;
104 2 0 -8.1; 105 2.5 0 -8.1; 106 3 0 -8.1; 107 3.5 0 -8.1; 108 4 0 -8.1;
109 4.5 0 -8.1; 110 5 0 -8.1; 111 0 0 -9; 112 0.5 0 -9; 113 1 0 -9;
114 1.5 0 -9; 115 2 0 -9; 116 2.5 0 -9; 117 3 0 -9; 118 3.5 0 -9; 119 4 0 -9;
120 4.5 0 -9; 121 5 0 -9; 427 0.5 0 -9.9; 428 0 0 -9.9; 429 1 0 -9.9;
430 1.5 0 -9.9; 431 2 0 -9.9; 432 2.5 0 -9.9; 433 3 0 -9.9; 434 3.5 0 -9.9;
435 4 0 -9.9; 436 4.5 0 -9.9; 437 5 0 -9.9; 438 -1 0 0; 439 -0.5 0 0;
440 -0.5 0 -0.900001; 441 -1 0 -0.900001; 442 -0.5 0 -1.8; 443 -1 0 -1.8;
444 -0.5 0 -2.7; 445 -1 0 -2.7; 446 -0.5 0 -3.6; 447 -1 0 -3.6;
448 -0.5 0 -4.5; 449 -1 0 -4.5; 450 -0.5 0 -5.4; 451 -1 0 -5.4;
452 -0.5 0 -6.3; 453 -1 0 -6.3; 454 -0.5 0 -7.2; 455 -1 0 -7.2;
456 -0.5 0 -8.1; 457 -1 0 -8.1; 458 -0.5 0 -9; 459 -1 0 -9; 460 -0.5 0 -9.9;
461 -1 0 -9.9; 462 5.5 0 0; 463 5.5 0 -0.9; 464 6 0 0; 465 6 0 -0.9;
466 5.5 0 -1.8; 467 6 0 -1.8; 468 5.5 0 -2.7; 469 6 0 -2.7; 470 5.5 0 -3.6;
471 6 0 -3.6; 472 5.5 0 -4.5; 473 6 0 -4.5; 474 5.5 0 -5.4; 475 6 0 -5.4;
476 5.5 0 -6.3; 477 6 0 -6.3; 478 5.5 0 -7.2; 479 6 0 -7.2; 480 5.5 0 -8.1;
481 6 0 -8.1; 482 5.5 0 -9; 483 6 0 -9; 484 5.5 0 -9.9; 485 6 0 -9.9;
486 0 0 0.9; 487 0.5 0 0.9; 488 1 0 0.9; 489 1.5 0 0.9; 490 2 0 0.9;
491 2.5 0 0.9; 492 3 0 0.9; 493 3.5 0 0.9; 494 4 0 0.9; 495 4.5 0 0.9;
496 5 0 0.9; 497 -1 0 0.9; 498 -0.5 0 0.9; 499 5.5 0 0.9; 500 6 0 0.9;
501 1.5 0 -5.85; 502 1.5 0 -3.15; 503 3.5 0 -5.85; 504 3.5 0 -3.15;
505 2 0 -5.85; 506 2.5 0 -5.85; 507 3 0 -5.85; 508 2 0 -3.15; 509 2.5 0 -3.15;
510 3 0 -3.15; 511 3.5 -1.5 -3.6; 512 1.5 -1.5 -3.6; 513 1.5 -1.5 -5.4;
514 3.5 -1.5 -5.4; 515 3.5 -1.5 -4.5; 516 1.5 -1.5 -4.5; 517 3.5 -1.5 -5.85;
518 2.5 -1.5 -5.85; 519 2.5 -1.5 -3.15; 520 2 -1.5 -3.15; 521 3 -1.5 -3.15;
522 2 -1.5 -5.85; 523 3.5 -1.5 -3.15; 524 1.5 -1.5 -3.15; 525 1.5 -1.5 -5.85;
526 3 -1.5 -5.85; 527 1.5 -0.5 -5.85; 528 3.5 -0.5 -5.85; 529 2 -0.5 -5.85;
530 2.5 -0.5 -5.85; 531 3 -0.5 -5.85; 532 3.5 -0.5 -3.6; 533 3.5 -0.5 -4.5;
534 3.5 -0.5 -5.4; 535 3.5 -0.5 -3.15; 536 1.5 -0.5 -3.15; 537 2 -0.5 -3.15;
538 2.5 -0.5 -3.15; 539 3 -0.5 -3.15; 540 1.5 -0.5 -3.6; 541 1.5 -0.5 -4.5;
542 1.5 -0.5 -5.4; 543 0 0.5 -9; 544 0 1 -9; 545 0 1.5 -9; 546 0 2 -9;
547 0 2.5 -9; 548 0 3 -9; 549 0 3.5 -9; 550 0 4 -9; 551 0 4.5 -9; 552 0 5 -9;
553 0.5 0.5 -9; 554 0.5 1 -9; 555 0.5 1.5 -9; 556 0.5 2 -9; 557 0.5 2.5 -9;
558 0.5 3 -9; 559 0.5 3.5 -9; 560 0.5 4 -9; 561 0.5 4.5 -9; 562 0.5 5 -9;
563 1 0.5 -9; 564 1 1 -9; 565 1 1.5 -9; 566 1 2 -9; 567 1 2.5 -9; 568 1 3 -9;
569 1 3.5 -9; 570 1 4 -9; 571 1 4.5 -9; 572 1 5 -9; 573 1.5 0.5 -9;
574 1.5 1 -9; 575 1.5 1.5 -9; 576 1.5 2 -9; 577 1.5 2.5 -9; 578 1.5 3 -9;
579 1.5 3.5 -9; 580 1.5 4 -9; 581 1.5 4.5 -9; 582 1.5 5 -9; 583 2 0.5 -9;
584 2 1 -9; 585 2 1.5 -9; 586 2 2 -9; 587 2 2.5 -9; 588 2 3 -9; 589 2 3.5 -9;
590 2 4 -9; 591 2 4.5 -9; 592 2 5 -9; 593 2.5 0.5 -9; 594 2.5 1 -9;
595 2.5 1.5 -9; 596 2.5 2 -9; 597 2.5 2.5 -9; 598 2.5 3 -9; 599 2.5 3.5 -9;
600 2.5 4 -9; 601 2.5 4.5 -9; 602 2.5 5 -9; 603 3 0.5 -9; 604 3 1 -9;
605 3 1.5 -9; 606 3 2 -9; 607 3 2.5 -9; 608 3 3 -9; 609 3 3.5 -9; 610 3 4 -9;
611 3 4.5 -9; 612 3 5 -9; 613 3.5 0.5 -9; 614 3.5 1 -9; 615 3.5 1.5 -9;
616 3.5 2 -9; 617 3.5 2.5 -9; 618 3.5 3 -9; 619 3.5 3.5 -9; 620 3.5 4 -9;
621 3.5 4.5 -9; 622 3.5 5 -9; 623 4 0.5 -9; 624 4 1 -9; 625 4 1.5 -9;
626 4 2 -9; 627 4 2.5 -9; 628 4 3 -9; 629 4 3.5 -9; 630 4 4 -9; 631 4 4.5 -9;
632 4 5 -9; 633 4.5 0.5 -9; 634 4.5 1 -9; 635 4.5 1.5 -9; 636 4.5 2 -9;
637 4.5 2.5 -9; 638 4.5 3 -9; 639 4.5 3.5 -9; 640 4.5 4 -9; 641 4.5 4.5 -9;
642 4.5 5 -9; 643 5 0.5 -9; 644 5 1 -9; 645 5 1.5 -9; 646 5 2 -9; 647 5 2.5 -9;
648 5 3 -9; 649 5 3.5 -9; 650 5 4 -9; 651 5 4.5 -9; 652 5 5 -9; 659 1 4 -8.5;
660 0 4 -8.5; 661 2 4 -8.5; 662 3 4 -8.5; 663 4 4 -8.5; 664 5 4 -8.5;
665 0 4.5 -9.5; 666 1 4.5 -9.5; 667 2 4.5 -9.5; 668 3 4.5 -9.5; 669 4 4.5 -9.5;
670 5 4.5 -9.5; 671 0 5 -9.5; 672 0.5 5 -9.5; 673 0.5 4.5 -9.5; 674 1 5 -9.5;
675 1.5 5 -9.5; 676 1.5 4.5 -9.5; 677 2 5 -9.5; 678 2.5 5 -9.5;
679 2.5 4.5 -9.5; 680 3 5 -9.5; 681 3.5 5 -9.5; 682 3.5 4.5 -9.5; 683 4 5 -9.5;
684 4.5 5 -9.5; 685 4.5 4.5 -9.5; 686 5 5 -9.5; 687 0 4.5 -8.5;
688 0.5 4.5 -8.5; 689 0.5 4 -8.5; 690 1 4.5 -8.5; 691 1.5 4.5 -8.5;
692 1.5 4 -8.5; 693 2 4.5 -8.5; 694 2.5 4.5 -8.5; 695 2.5 4 -8.5;
696 3 4.5 -8.5; 697 3.5 4.5 -8.5; 698 3.5 4 -8.5; 699 4 4.5 -8.5;
700 4.5 4.5 -8.5; 701 4.5 4 -8.5; 702 5 4.5 -8.5; 704 0 0.5 0; 705 0 1 0;
706 0 1.5 0; 707 0 2 0; 708 0 2.5 0; 709 0 3 0; 710 0 3.5 0; 711 0 4 0;
712 0 4.5 0; 713 0 5 0; 714 0.5 0.5 0; 715 0.5 1 0; 716 0.5 1.5 0; 717 0.5 2 0;
718 0.5 2.5 0; 719 0.5 3 0; 720 0.5 3.5 0; 721 0.5 4 0; 722 0.5 4.5 0;
723 0.5 5 0; 724 1 0.5 0; 725 1 1 0; 726 1 1.5 0; 727 1 2 0; 728 1 2.5 0;
729 1 3 0; 730 1 3.5 0; 731 1 4 0; 732 1 4.5 0; 733 1 5 0; 734 1.5 0.5 0;
735 1.5 1 0; 736 1.5 1.5 0; 737 1.5 2 0; 738 1.5 2.5 0; 739 1.5 3 0;
740 1.5 3.5 0; 741 1.5 4 0; 742 1.5 4.5 0; 743 1.5 5 0; 744 2 0.5 0; 745 2 1 0;
746 2 1.5 0; 747 2 2 0; 748 2 2.5 0; 749 2 3 0; 750 2 3.5 0; 751 2 4 0;
752 2 4.5 0; 753 2 5 0; 754 2.5 0.5 0; 755 2.5 1 0; 756 2.5 1.5 0; 757 2.5 2 0;
758 2.5 2.5 0; 759 2.5 3 0; 760 2.5 3.5 0; 761 2.5 4 0; 762 2.5 4.5 0;
763 2.5 5 0; 764 3 0.5 0; 765 3 1 0; 766 3 1.5 0; 767 3 2 0; 768 3 2.5 0;
769 3 3 0; 770 3 3.5 0; 771 3 4 0; 772 3 4.5 0; 773 3 5 0; 774 3.5 0.5 0;
775 3.5 1 0; 776 3.5 1.5 0; 777 3.5 2 0; 778 3.5 2.5 0; 779 3.5 3 0;
780 3.5 3.5 0; 781 3.5 4 0; 782 3.5 4.5 0; 783 3.5 5 0; 784 4 0.5 0; 785 4 1 0;
786 4 1.5 0; 787 4 2 0; 788 4 2.5 0; 789 4 3 0; 790 4 3.5 0; 791 4 4 0;
792 4 4.5 0; 793 4 5 0; 794 4.5 0.5 0; 795 4.5 1 0; 796 4.5 1.5 0; 797 4.5 2 0;
798 4.5 2.5 0; 799 4.5 3 0; 800 4.5 3.5 0; 801 4.5 4 0; 802 4.5 4.5 0;
803 4.5 5 0; 804 5 0.5 0; 805 5 1 0; 806 5 1.5 0; 807 5 2 0; 808 5 2.5 0;
809 5 3 0; 810 5 3.5 0; 811 5 4 0; 812 5 4.5 0; 813 5 5 0; 814 1 4 -0.5;
815 0 4 -0.5; 816 2 4 -0.5; 817 3 4 -0.5; 818 4 4 -0.5; 819 5 4 -0.5;
820 0 4.5 0.5; 821 1 4.5 0.5; 822 2 4.5 0.5; 823 3 4.5 0.5; 824 4 4.5 0.5;
825 5 4.5 0.5; 826 0 5 0.5; 827 0.5 5 0.5; 828 0.5 4.5 0.5; 829 1 5 0.5;
830 1.5 5 0.5; 831 1.5 4.5 0.5; 832 2 5 0.5; 833 2.5 5 0.5; 834 2.5 4.5 0.5;
835 3 5 0.5; 836 3.5 5 0.5; 837 3.5 4.5 0.5; 838 4 5 0.5; 839 4.5 5 0.5;
840 4.5 4.5 0.5; 841 5 5 0.5; 842 0 4.5 -0.5; 843 0.5 4.5 -0.5; 844 0.5 4 -0.5;
845 1 4.5 -0.5; 846 1.5 4.5 -0.5; 847 1.5 4 -0.5; 848 2 4.5 -0.5;
849 2.5 4.5 -0.5; 850 2.5 4 -0.5; 851 3 4.5 -0.5; 852 3.5 4.5 -0.5;
853 3.5 4 -0.5; 854 4 4.5 -0.5; 855 4.5 4.5 -0.5; 856 4.5 4 -0.5;
857 5 4.5 -0.5; 858 5 0.5 -8.1; 859 5 1 -8.1; 860 5 1.5 -8.1; 861 5 2 -8.1;
862 5 2.5 -8.1; 863 5 3 -8.1; 864 5 3.5 -8.1; 865 5 4 -8.1; 866 5 4.5 -8.1;
867 5 5 -8.1; 868 5 0.5 -7.2; 869 5 1 -7.2; 870 5 1.5 -7.2; 871 5 2 -7.2;
872 5 2.5 -7.2; 873 5 3 -7.2; 874 5 3.5 -7.2; 875 5 4 -7.2; 876 5 4.5 -7.2;
877 5 5 -7.2; 878 5 0.5 -6.3; 879 5 1 -6.3; 880 5 1.5 -6.3; 881 5 2 -6.3;
882 5 2.5 -6.3; 883 5 3 -6.3; 884 5 3.5 -6.3; 885 5 4 -6.3; 886 5 4.5 -6.3;
887 5 5 -6.3; 888 5 0.5 -5.4; 889 5 1 -5.4; 890 5 1.5 -5.4; 891 5 2 -5.4;
892 5 2.5 -5.4; 893 5 3 -5.4; 894 5 3.5 -5.4; 895 5 4 -5.4; 896 5 4.5 -5.4;
897 5 5 -5.4; 898 5 0.5 -4.5; 899 5 1 -4.5; 900 5 1.5 -4.5; 901 5 2 -4.5;
902 5 2.5 -4.5; 903 5 3 -4.5; 904 5 3.5 -4.5; 905 5 4 -4.5; 906 5 4.5 -4.5;
907 5 5 -4.5; 908 5 0.5 -3.6; 909 5 1 -3.6; 910 5 1.5 -3.6; 911 5 2 -3.6;
912 5 2.5 -3.6; 913 5 3 -3.6; 914 5 3.5 -3.6; 915 5 4 -3.6; 916 5 4.5 -3.6;
917 5 5 -3.6; 918 5 0.5 -2.7; 919 5 1 -2.7; 920 5 1.5 -2.7; 921 5 2 -2.7;
922 5 2.5 -2.7; 923 5 3 -2.7; 924 5 3.5 -2.7; 925 5 4 -2.7; 926 5 4.5 -2.7;
927 5 5 -2.7; 928 5 0.5 -1.8; 929 5 1 -1.8; 930 5 1.5 -1.8; 931 5 2 -1.8;
932 5 2.5 -1.8; 933 5 3 -1.8; 934 5 3.5 -1.8; 935 5 4 -1.8; 936 5 4.5 -1.8;
937 5 5 -1.8; 938 5 0.5 -0.9; 939 5 1 -0.9; 940 5 1.5 -0.9; 941 5 2 -0.9;
942 5 2.5 -0.9; 943 5 3 -0.9; 944 5 3.5 -0.9; 945 5 4 -0.9; 946 5 4.5 -0.9;
947 5 5 -0.9; 948 4.5 4 -8.1; 949 4.5 4 -7.2; 950 4.5 4 -6.3; 951 4.5 4 -5.4;
952 4.5 4 -4.5; 953 4.5 4 -3.6; 954 4.5 4 -2.7; 955 4.5 4 -1.8;
956 4.5 4 -0.900001; 957 5.5 4.5 -9; 958 5.5 4.5 -8.1; 959 5.5 4.5 -7.2;
960 5.5 4.5 -6.3; 961 5.5 4.5 -5.4; 962 5.5 4.5 -4.5; 963 5.5 4.5 -3.6;
964 5.5 4.5 -2.7; 965 5.5 4.5 -1.8; 966 5.5 4.5 -0.9; 967 5.5 4.5 0;
968 5.5 5 -9; 969 5.5 5 -8.1; 970 5.5 5 -7.2; 971 5.5 5 -6.3; 972 5.5 5 -5.4;
973 5.5 5 -4.5; 974 5.5 5 -3.6; 975 5.5 5 -2.7; 976 5.5 5 -1.8; 977 5.5 5 -0.9;
978 5.5 5 0; 979 4.5 4.5 -8.1; 980 4.5 4.5 -7.2; 981 4.5 4.5 -6.3;
982 4.5 4.5 -5.4; 983 4.5 4.5 -4.5; 984 4.5 4.5 -3.6; 985 4.5 4.5 -2.7;
986 4.5 4.5 -1.8; 987 4.5 4.5 -0.9; 988 0 0.5 -8.1; 989 0 1 -8.1;
990 0 1.5 -8.1; 991 0 2 -8.1; 992 0 2.5 -8.1; 993 0 3 -8.1; 994 0 3.5 -8.1;
995 0 4 -8.1; 996 0 4.5 -8.1; 997 0 5 -8.1; 998 0 0.5 -7.2; 999 0 1 -7.2;
1000 0 1.5 -7.2; 1001 0 2 -7.2; 1002 0 2.5 -7.2; 1003 0 3 -7.2;
1004 0 3.5 -7.2; 1005 0 4 -7.2; 1006 0 4.5 -7.2; 1007 0 5 -7.2;
1008 0 0.5 -6.3; 1009 0 1 -6.3; 1010 0 1.5 -6.3; 1011 0 2 -6.3;
1012 0 2.5 -6.3; 1013 0 3 -6.3; 1014 0 3.5 -6.3; 1015 0 4 -6.3;
1016 0 4.5 -6.3; 1017 0 5 -6.3; 1018 0 0.5 -5.4; 1019 0 1 -5.4;
1020 0 1.5 -5.4; 1021 0 2 -5.4; 1022 0 2.5 -5.4; 1023 0 3 -5.4;
1024 0 3.5 -5.4; 1025 0 4 -5.4; 1026 0 4.5 -5.4; 1027 0 5 -5.4;
1028 0 0.5 -4.5; 1029 0 1 -4.5; 1030 0 1.5 -4.5; 1031 0 2 -4.5;
1032 0 2.5 -4.5; 1033 0 3 -4.5; 1034 0 3.5 -4.5; 1035 0 4 -4.5;
1036 0 4.5 -4.5; 1037 0 5 -4.5; 1038 0 0.5 -3.6; 1039 0 1 -3.6;
1040 0 1.5 -3.6; 1041 0 2 -3.6; 1042 0 2.5 -3.6; 1043 0 3 -3.6;
1044 0 3.5 -3.6; 1045 0 4 -3.6; 1046 0 4.5 -3.6; 1047 0 5 -3.6;
1048 0 0.5 -2.7; 1049 0 1 -2.7; 1050 0 1.5 -2.7; 1051 0 2 -2.7;
1052 0 2.5 -2.7; 1053 0 3 -2.7; 1054 0 3.5 -2.7; 1055 0 4 -2.7;
1056 0 4.5 -2.7; 1057 0 5 -2.7; 1058 0 0.5 -1.8; 1059 0 1 -1.8;
1060 0 1.5 -1.8; 1061 0 2 -1.8; 1062 0 2.5 -1.8; 1063 0 3 -1.8;
1064 0 3.5 -1.8; 1065 0 4 -1.8; 1066 0 4.5 -1.8; 1067 0 5 -1.8;
1068 0 0.5 -0.9; 1069 0 1 -0.9; 1070 0 1.5 -0.9; 1071 0 2 -0.9;
1072 0 2.5 -0.9; 1073 0 3 -0.9; 1074 0 3.5 -0.9; 1075 0 4 -0.9;
1076 0 4.5 -0.9; 1077 0 5 -0.9; 1078 0.5 4 -8.1; 1079 0.5 4 -7.2;
1080 0.5 4 -6.3; 1081 0.5 4 -5.4; 1082 0.5 4 -4.5; 1083 0.5 4 -3.6;
1084 0.5 4 -2.7; 1085 0.5 4 -1.8; 1086 0.5 4 -0.900001; 1087 -0.5 4.5 -9;
1088 -0.499999 4.5 -8.1; 1089 -0.499999 4.5 -7.2; 1090 -0.499999 4.5 -6.3;
1091 -0.499999 4.5 -5.4; 1092 -0.499999 4.5 -4.5; 1093 -0.499999 4.5 -3.6;
1094 -0.499999 4.5 -2.7; 1095 -0.499999 4.5 -1.8; 1096 -0.499999 4.5 -0.9;
1097 -0.5 4.5 0; 1098 -0.5 5 -9; 1099 -0.5 5 -8.1; 1100 -0.5 5 -7.2;
1101 -0.5 5 -6.3; 1102 -0.5 5 -5.4; 1103 -0.5 5 -4.5; 1104 -0.5 5 -3.6;
1105 -0.5 5 -2.7; 1106 -0.5 5 -1.8; 1107 -0.5 5 -0.9; 1108 -0.5 5 0;
1109 0.499999 4.5 -8.1; 1110 0.499999 4.5 -7.2; 1111 0.499999 4.5 -6.3;
1112 0.499999 4.5 -5.4; 1113 0.499999 4.5 -4.5; 1114 0.499999 4.5 -3.6;
1115 0.499999 4.5 -2.7; 1116 0.499999 4.5 -1.8; 1117 0.499999 4.5 -0.9;
1118 -0.5 4.5 -9.5; 1119 -0.5 5 -9.5; 1120 5.5 5 -9.5; 1121 5.5 4.5 -9.5;
1122 5.5 5 0.5; 1123 5.5 4.5 0.5; 1124 -0.5 4.5 0.5; 1125 -0.5 5 0.5;
1126 -1.5 0 0; 1127 -1.5 0 -0.900001; 1128 -1.5 0 -1.8; 1129 -1.5 0 -2.7;
1130 -1.5 0 -3.6; 1131 -1.5 0 -4.5; 1132 -1.5 0 -5.4; 1133 -1.5 0 -6.3;
1134 -1.5 0 -7.2; 1135 -1.5 0 -8.1; 1136 -1.5 0 -9; 1137 -1.5 0 -9.9;
1138 -1.5 0 0.9; 1139 6.5 0 0; 1140 6.5 0 -0.9; 1141 6.5 0 -1.8;
1142 6.5 0 -2.7; 1143 6.5 0 -3.6; 1144 6.5 0 -4.5; 1145 6.5 0 -5.4;
1146 6.5 0 -6.3; 1147 6.5 0 -7.2; 1148 6.5 0 -8.1; 1149 6.5 0 -9;
1150 6.5 0 -9.9; 1151 6.5 0 0.9; 1152 0.5 0 -10.5; 1153 0 0 -10.5;
1154 1 0 -10.5; 1155 1.5 0 -10.5; 1156 2 0 -10.5; 1157 2.5 0 -10.5;
1158 3 0 -10.5; 1159 3.5 0 -10.5; 1160 4 0 -10.5; 1161 4.5 0 -10.5;
1162 5 0 -10.5; 1163 -0.5 0 -10.5; 1164 -1 0 -10.5; 1165 5.5 0 -10.5;
1166 6 0 -10.5; 1167 -1.5 0 -10.5; 1168 6.5 0 -10.5; 1169 0 0 1.5;
1170 0.5 0 1.5; 1171 1 0 1.5; 1172 1.5 0 1.5; 1173 2 0 1.5; 1174 2.5 0 1.5;
1175 3 0 1.5; 1176 3.5 0 1.5; 1177 4 0 1.5; 1178 4.5 0 1.5; 1179 5 0 1.5;
1180 -1 0 1.5; 1181 -0.5 0 1.5; 1182 5.5 0 1.5; 1183 6 0 1.5; 1184 -1.5 0 1.5;
1185 6.5 0 1.5;
MEMBER INCIDENCES
1075 111 100; 1076 1 2; 1077 11 22; 1078 121 120; 1079 503 507; 1080 501 70;
1081 502 508; 1082 504 52; 1083 525 522; 1084 517 514; 1085 523 521;
1086 524 512; 1087 2 3; 1088 3 4; 1089 4 5; 1090 5 6; 1091 6 7; 1092 7 8;
1093 8 9; 1094 9 10; 1095 10 11; 1096 12 1; 1097 22 33; 1098 23 12; 1099 33 44;
1100 34 23; 1101 44 55; 1102 45 34; 1103 48 502; 1104 52 63; 1105 55 66;
1106 56 45; 1107 59 48; 1108 63 74; 1109 66 77; 1110 67 56; 1111 70 59;
1112 74 503; 1113 77 88; 1114 78 67; 1115 88 99; 1116 89 78; 1117 99 110;
1118 100 89; 1119 110 121; 1120 112 111; 1121 113 112; 1122 114 113;
1123 115 114; 1124 116 115; 1125 117 116; 1126 118 117; 1127 119 118;
1128 120 119; 1129 505 501; 1130 506 505; 1131 507 506; 1132 508 509;
1133 509 510; 1134 510 504; 1135 511 523; 1136 512 516; 1137 513 525;
1138 514 515; 1139 515 511; 1140 516 513; 1141 518 526; 1142 519 520;
1143 520 524; 1144 521 519; 1145 522 518; 1146 526 517;
ELEMENT INCIDENCES SHELL
1 1 2 13 12; 2 2 3 14 13; 3 3 4 15 14; 4 4 5 16 15; 5 5 6 17 16; 6 6 7 18 17;
7 7 8 19 18; 8 8 9 20 19; 9 9 10 21 20; 10 10 11 22 21; 11 12 13 24 23;
12 13 14 25 24; 13 14 15 26 25; 14 15 16 27 26; 15 16 17 28 27; 16 17 18 29 28;
17 18 19 30 29; 18 19 20 31 30; 19 20 21 32 31; 20 21 22 33 32; 21 23 24 35 34;
22 24 25 36 35; 23 25 26 37 36; 24 26 27 38 37; 25 27 28 39 38; 26 28 29 40 39;
27 29 30 41 40; 28 30 31 42 41; 29 31 32 43 42; 30 32 33 44 43; 31 34 35 46 45;
32 35 36 47 46; 33 36 37 48 47; 38 41 42 53 52; 39 42 43 54 53; 40 43 44 55 54;
41 45 46 57 56; 42 46 47 58 57; 43 47 48 59 58; 44 512 49 60 516;
45 49 50 61 60; 46 50 51 62 61; 47 51 511 515 62; 48 52 53 64 63;
49 53 54 65 64; 50 54 55 66 65; 51 56 57 68 67; 52 57 58 69 68; 53 58 59 70 69;
54 516 60 71 513; 55 60 61 72 71; 56 61 62 73 72; 57 62 515 514 73;
58 63 64 75 74; 59 64 65 76 75; 60 65 66 77 76; 61 67 68 79 78; 62 68 69 80 79;
63 69 70 81 80; 68 74 75 86 85; 69 75 76 87 86; 70 76 77 88 87; 71 78 79 90 89;
72 79 80 91 90; 73 80 81 92 91; 74 81 82 93 92; 75 82 83 94 93; 76 83 84 95 94;
77 84 85 96 95; 78 85 86 97 96; 79 86 87 98 97; 80 87 88 99 98;
81 89 90 101 100; 82 90 91 102 101; 83 91 92 103 102; 84 92 93 104 103;
85 93 94 105 104; 86 94 95 106 105; 87 95 96 107 106; 88 96 97 108 107;
89 97 98 109 108; 90 98 99 110 109; 91 100 101 112 111; 92 101 102 113 112;
93 102 103 114 113; 94 103 104 115 114; 95 104 105 116 115; 96 105 106 117 116;
97 106 107 118 117; 98 107 108 119 118; 99 108 109 120 119;
100 109 110 121 120; 401 111 112 427 428; 402 112 113 429 427;
403 113 114 430 429; 404 114 115 431 430; 405 115 116 432 431;
406 116 117 433 432; 407 117 118 434 433; 408 118 119 435 434;
409 119 120 436 435; 410 120 121 437 436; 411 438 439 440 441;
412 439 1 12 440; 413 441 440 442 443; 414 440 12 23 442; 415 443 442 444 445;
416 442 23 34 444; 417 445 444 446 447; 418 444 34 45 446; 419 447 446 448 449;
420 446 45 56 448; 421 449 448 450 451; 422 448 56 67 450; 423 451 450 452 453;
424 450 67 78 452; 425 453 452 454 455; 426 452 78 89 454; 427 455 454 456 457;
428 454 89 100 456; 429 457 456 458 459; 430 456 100 111 458;
431 459 458 460 461; 432 458 111 428 460; 433 11 462 463 22;
434 462 464 465 463; 435 22 463 466 33; 436 463 465 467 466; 437 33 466 468 44;
438 466 467 469 468; 439 44 468 470 55; 440 468 469 471 470; 441 55 470 472 66;
442 470 471 473 472; 443 66 472 474 77; 444 472 473 475 474; 445 77 474 476 88;
446 474 475 477 476; 447 88 476 478 99; 448 476 477 479 478;
449 99 478 480 110; 450 478 479 481 480; 451 110 480 482 121;
452 480 481 483 482; 453 121 482 484 437; 454 482 483 485 484; 455 486 487 2 1;
456 487 488 3 2; 457 488 489 4 3; 458 489 490 5 4; 459 490 491 6 5;
460 491 492 7 6; 461 492 493 8 7; 462 493 494 9 8; 463 494 495 10 9;
464 495 496 11 10; 465 497 498 439 438; 466 498 486 1 439; 467 496 499 462 11;
468 499 500 464 462; 469 81 501 505 82; 470 82 505 506 83; 471 83 506 507 84;
472 84 507 503 85; 473 512 524 520 49; 474 49 520 519 50; 475 50 519 521 51;
476 51 521 523 511; 477 502 37 38 508; 478 508 38 39 509; 479 509 39 40 510;
480 510 40 41 504; 481 525 513 71 522; 482 522 71 72 518; 483 518 72 73 526;
484 526 73 514 517; 485 501 527 529 505; 486 505 529 530 506;
487 506 530 531 507; 488 507 531 528 503; 489 527 525 522 529;
490 529 522 518 530; 491 530 518 526 531; 492 531 526 517 528;
493 502 536 537 508; 494 508 537 538 509; 495 509 538 539 510;
496 510 539 535 504; 497 536 524 520 537; 498 537 520 519 538;
499 538 519 521 539; 500 539 521 523 535; 501 503 528 534 74;
502 528 517 514 534; 503 74 534 533 63; 504 534 514 515 533; 505 63 533 532 52;
507 533 515 511 532; 508 532 511 523 535; 509 52 532 535 504;
510 501 527 542 70; 511 527 525 513 542; 512 70 542 541 59;
513 542 513 516 541; 514 59 541 540 48; 515 541 516 512 540;
516 540 512 524 536; 517 48 540 536 502; 518 111 543 553 112;
519 543 544 554 553; 520 544 545 555 554; 521 545 546 556 555;
522 546 547 557 556; 523 547 548 558 557; 524 548 549 559 558;
525 549 550 560 559; 526 550 551 561 560; 527 551 552 562 561;
528 112 553 563 113; 529 553 554 564 563; 530 554 555 565 564;
531 555 556 566 565; 532 556 557 567 566; 533 557 558 568 567;
534 558 559 569 568; 535 559 560 570 569; 536 560 561 571 570;
537 561 562 572 571; 538 113 563 573 114; 539 563 564 574 573;
540 564 565 575 574; 541 565 566 576 575; 542 566 567 577 576;
543 567 568 578 577; 544 568 569 579 578; 545 569 570 580 579;
546 570 571 581 580; 547 571 572 582 581; 548 114 573 583 115;
549 573 574 584 583; 550 574 575 585 584; 551 575 576 586 585;
552 576 577 587 586; 553 577 578 588 587; 554 578 579 589 588;
555 579 580 590 589; 556 580 581 591 590; 557 581 582 592 591;
558 115 583 593 116; 559 583 584 594 593; 560 584 585 595 594;
561 585 586 596 595; 562 586 587 597 596; 563 587 588 598 597;
564 588 589 599 598; 565 589 590 600 599; 566 590 591 601 600;
567 591 592 602 601; 568 116 593 603 117; 569 593 594 604 603;
570 594 595 605 604; 571 595 596 606 605; 572 596 597 607 606;
573 597 598 608 607; 574 598 599 609 608; 575 599 600 610 609;
576 600 601 611 610; 577 601 602 612 611; 578 117 603 613 118;
579 603 604 614 613; 580 604 605 615 614; 581 605 606 616 615;
582 606 607 617 616; 583 607 608 618 617; 584 608 609 619 618;
585 609 610 620 619; 586 610 611 621 620; 587 611 612 622 621;
588 118 613 623 119; 589 613 614 624 623; 590 614 615 625 624;
591 615 616 626 625; 592 616 617 627 626; 593 617 618 628 627;
594 618 619 629 628; 595 619 620 630 629; 596 620 621 631 630;
597 621 622 632 631; 598 119 623 633 120; 599 623 624 634 633;
600 624 625 635 634; 601 625 626 636 635; 602 626 627 637 636;
603 627 628 638 637; 604 628 629 639 638; 605 629 630 640 639;
606 630 631 641 640; 607 631 632 642 641; 608 120 633 643 121;
609 633 634 644 643; 610 634 635 645 644; 611 635 636 646 645;
612 636 637 647 646; 613 637 638 648 647; 614 638 639 649 648;
615 639 640 650 649; 616 640 641 651 650; 617 641 642 652 651;
623 660 659 570 550; 624 659 661 590 570; 625 661 662 610 590;
626 662 663 630 610; 627 663 664 650 630; 628 551 571 666 665;
629 571 591 667 666; 630 591 611 668 667; 631 611 631 669 668;
632 631 651 670 669; 633 665 671 672 673; 634 673 672 674 666;
635 666 674 675 676; 636 676 675 677 667; 637 667 677 678 679;
638 679 678 680 668; 639 668 680 681 682; 640 682 681 683 669;
641 669 683 684 685; 642 685 684 686 670; 643 660 687 688 689;
644 689 688 690 659; 645 659 690 691 692; 646 692 691 693 661;
647 661 693 694 695; 648 695 694 696 662; 649 662 696 697 698;
650 698 697 699 663; 651 663 699 700 701; 652 701 700 702 664; 653 1 704 714 2;
654 704 705 715 714; 655 705 706 716 715; 656 706 707 717 716;
657 707 708 718 717; 658 708 709 719 718; 659 709 710 720 719;
660 710 711 721 720; 661 711 712 722 721; 662 712 713 723 722; 663 2 714 724 3;
664 714 715 725 724; 665 715 716 726 725; 666 716 717 727 726;
667 717 718 728 727; 668 718 719 729 728; 669 719 720 730 729;
670 720 721 731 730; 671 721 722 732 731; 672 722 723 733 732; 673 3 724 734 4;
674 724 725 735 734; 675 725 726 736 735; 676 726 727 737 736;
677 727 728 738 737; 678 728 729 739 738; 679 729 730 740 739;
680 730 731 741 740; 681 731 732 742 741; 682 732 733 743 742; 683 4 734 744 5;
684 734 735 745 744; 685 735 736 746 745; 686 736 737 747 746;
687 737 738 748 747; 688 738 739 749 748; 689 739 740 750 749;
690 740 741 751 750; 691 741 742 752 751; 692 742 743 753 752; 693 5 744 754 6;
694 744 745 755 754; 695 745 746 756 755; 696 746 747 757 756;
697 747 748 758 757; 698 748 749 759 758; 699 749 750 760 759;
700 750 751 761 760; 701 751 752 762 761; 702 752 753 763 762; 703 6 754 764 7;
704 754 755 765 764; 705 755 756 766 765; 706 756 757 767 766;
707 757 758 768 767; 708 758 759 769 768; 709 759 760 770 769;
710 760 761 771 770; 711 761 762 772 771; 712 762 763 773 772; 713 7 764 774 8;
714 764 765 775 774; 715 765 766 776 775; 716 766 767 777 776;
717 767 768 778 777; 718 768 769 779 778; 719 769 770 780 779;
720 770 771 781 780; 721 771 772 782 781; 722 772 773 783 782; 723 8 774 784 9;
724 774 775 785 784; 725 775 776 786 785; 726 776 777 787 786;
727 777 778 788 787; 728 778 779 789 788; 729 779 780 790 789;
730 780 781 791 790; 731 781 782 792 791; 732 782 783 793 792;
733 9 784 794 10; 734 784 785 795 794; 735 785 786 796 795;
736 786 787 797 796; 737 787 788 798 797; 738 788 789 799 798;
739 789 790 800 799; 740 790 791 801 800; 741 791 792 802 801;
742 792 793 803 802; 743 10 794 804 11; 744 794 795 805 804;
745 795 796 806 805; 746 796 797 807 806; 747 797 798 808 807;
748 798 799 809 808; 749 799 800 810 809; 750 800 801 811 810;
751 801 802 812 811; 752 802 803 813 812; 753 711 731 814 815;
754 731 751 816 814; 755 751 771 817 816; 756 771 791 818 817;
757 791 811 819 818; 758 820 821 732 712; 759 821 822 752 732;
760 822 823 772 752; 761 823 824 792 772; 762 824 825 812 792;
763 820 826 827 828; 764 828 827 829 821; 765 821 829 830 831;
766 831 830 832 822; 767 822 832 833 834; 768 834 833 835 823;
769 823 835 836 837; 770 837 836 838 824; 771 824 838 839 840;
772 840 839 841 825; 773 815 842 843 844; 774 844 843 845 814;
775 814 845 846 847; 776 847 846 848 816; 777 816 848 849 850;
778 850 849 851 817; 779 817 851 852 853; 780 853 852 854 818;
781 818 854 855 856; 782 856 855 857 819; 783 121 643 858 110;
784 643 644 859 858; 785 644 645 860 859; 786 645 646 861 860;
787 646 647 862 861; 788 647 648 863 862; 789 648 649 864 863;
790 649 650 865 864; 791 650 651 866 865; 792 651 652 867 866;
793 110 858 868 99; 794 858 859 869 868; 795 859 860 870 869;
796 860 861 871 870; 797 861 862 872 871; 798 862 863 873 872;
799 863 864 874 873; 800 864 865 875 874; 801 865 866 876 875;
802 866 867 877 876; 803 99 868 878 88; 804 868 869 879 878;
805 869 870 880 879; 806 870 871 881 880; 807 871 872 882 881;
808 872 873 883 882; 809 873 874 884 883; 810 874 875 885 884;
811 875 876 886 885; 812 876 877 887 886; 813 88 878 888 77;
814 878 879 889 888; 815 879 880 890 889; 816 880 881 891 890;
817 881 882 892 891; 818 882 883 893 892; 819 883 884 894 893;
820 884 885 895 894; 821 885 886 896 895; 822 886 887 897 896;
823 77 888 898 66; 824 888 889 899 898; 825 889 890 900 899;
826 890 891 901 900; 827 891 892 902 901; 828 892 893 903 902;
829 893 894 904 903; 830 894 895 905 904; 831 895 896 906 905;
832 896 897 907 906; 833 66 898 908 55; 834 898 899 909 908;
835 899 900 910 909; 836 900 901 911 910; 837 901 902 912 911;
838 902 903 913 912; 839 903 904 914 913; 840 904 905 915 914;
841 905 906 916 915; 842 906 907 917 916; 843 55 908 918 44;
844 908 909 919 918; 845 909 910 920 919; 846 910 911 921 920;
847 911 912 922 921; 848 912 913 923 922; 849 913 914 924 923;
850 914 915 925 924; 851 915 916 926 925; 852 916 917 927 926;
853 44 918 928 33; 854 918 919 929 928; 855 919 920 930 929;
856 920 921 931 930; 857 921 922 932 931; 858 922 923 933 932;
859 923 924 934 933; 860 924 925 935 934; 861 925 926 936 935;
862 926 927 937 936; 863 33 928 938 22; 864 928 929 939 938;
865 929 930 940 939; 866 930 931 941 940; 867 931 932 942 941;
868 932 933 943 942; 869 933 934 944 943; 870 934 935 945 944;
871 935 936 946 945; 872 936 937 947 946; 873 22 938 804 11;
874 938 939 805 804; 875 939 940 806 805; 876 940 941 807 806;
877 941 942 808 807; 878 942 943 809 808; 879 943 944 810 809;
880 944 945 811 810; 881 945 946 812 811; 882 946 947 813 812;
883 650 640 948 865; 884 865 948 949 875; 885 875 949 950 885;
886 885 950 951 895; 887 895 951 952 905; 888 905 952 953 915;
889 915 953 954 925; 890 925 954 955 935; 891 935 955 956 945;
892 945 956 801 811; 893 957 651 866 958; 894 958 866 876 959;
895 959 876 886 960; 896 960 886 896 961; 897 961 896 906 962;
898 962 906 916 963; 899 963 916 926 964; 900 964 926 936 965;
901 965 936 946 966; 902 966 946 812 967; 903 957 968 969 958;
904 958 969 970 959; 905 959 970 971 960; 906 960 971 972 961;
907 961 972 973 962; 908 962 973 974 963; 909 963 974 975 964;
910 964 975 976 965; 911 965 976 977 966; 912 966 977 978 967;
913 640 641 979 948; 914 948 979 980 949; 915 949 980 981 950;
916 950 981 982 951; 917 951 982 983 952; 918 952 983 984 953;
919 953 984 985 954; 920 954 985 986 955; 921 955 986 987 956;
922 956 987 802 801; 923 111 543 988 100; 924 543 544 989 988;
925 544 545 990 989; 926 545 546 991 990; 927 546 547 992 991;
928 547 548 993 992; 929 548 549 994 993; 930 549 550 995 994;
931 550 551 996 995; 932 551 552 997 996; 933 100 988 998 89;
934 988 989 999 998; 935 989 990 1000 999; 936 990 991 1001 1000;
937 991 992 1002 1001; 938 992 993 1003 1002; 939 993 994 1004 1003;
940 994 995 1005 1004; 941 995 996 1006 1005; 942 996 997 1007 1006;
943 89 998 1008 78; 944 998 999 1009 1008; 945 999 1000 1010 1009;
946 1000 1001 1011 1010; 947 1001 1002 1012 1011; 948 1002 1003 1013 1012;
949 1003 1004 1014 1013; 950 1004 1005 1015 1014; 951 1005 1006 1016 1015;
952 1006 1007 1017 1016; 953 78 1008 1018 67; 954 1008 1009 1019 1018;
955 1009 1010 1020 1019; 956 1010 1011 1021 1020; 957 1011 1012 1022 1021;
958 1012 1013 1023 1022; 959 1013 1014 1024 1023; 960 1014 1015 1025 1024;
961 1015 1016 1026 1025; 962 1016 1017 1027 1026; 963 67 1018 1028 56;
964 1018 1019 1029 1028; 965 1019 1020 1030 1029; 966 1020 1021 1031 1030;
967 1021 1022 1032 1031; 968 1022 1023 1033 1032; 969 1023 1024 1034 1033;
970 1024 1025 1035 1034; 971 1025 1026 1036 1035; 972 1026 1027 1037 1036;
973 56 1028 1038 45; 974 1028 1029 1039 1038; 975 1029 1030 1040 1039;
976 1030 1031 1041 1040; 977 1031 1032 1042 1041; 978 1032 1033 1043 1042;
979 1033 1034 1044 1043; 980 1034 1035 1045 1044; 981 1035 1036 1046 1045;
982 1036 1037 1047 1046; 983 45 1038 1048 34; 984 1038 1039 1049 1048;
985 1039 1040 1050 1049; 986 1040 1041 1051 1050; 987 1041 1042 1052 1051;
988 1042 1043 1053 1052; 989 1043 1044 1054 1053; 990 1044 1045 1055 1054;
991 1045 1046 1056 1055; 992 1046 1047 1057 1056; 993 34 1048 1058 23;
994 1048 1049 1059 1058; 995 1049 1050 1060 1059; 996 1050 1051 1061 1060;
997 1051 1052 1062 1061; 998 1052 1053 1063 1062; 999 1053 1054 1064 1063;
1000 1054 1055 1065 1064; 1001 1055 1056 1066 1065; 1002 1056 1057 1067 1066;
1003 23 1058 1068 12; 1004 1058 1059 1069 1068; 1005 1059 1060 1070 1069;
1006 1060 1061 1071 1070; 1007 1061 1062 1072 1071; 1008 1062 1063 1073 1072;
1009 1063 1064 1074 1073; 1010 1064 1065 1075 1074; 1011 1065 1066 1076 1075;
1012 1066 1067 1077 1076; 1013 12 1068 704 1; 1014 1068 1069 705 704;
1015 1069 1070 706 705; 1016 1070 1071 707 706; 1017 1071 1072 708 707;
1018 1072 1073 709 708; 1019 1073 1074 710 709; 1020 1074 1075 711 710;
1021 1075 1076 712 711; 1022 1076 1077 713 712; 1023 995 1078 560 550;
1024 1005 1079 1078 995; 1025 1015 1080 1079 1005; 1026 1025 1081 1080 1015;
1027 1035 1082 1081 1025; 1028 1045 1083 1082 1035; 1029 1055 1084 1083 1045;
1030 1065 1085 1084 1055; 1031 1075 1086 1085 1065; 1032 711 721 1086 1075;
1033 1088 996 551 1087; 1034 1089 1006 996 1088; 1035 1090 1016 1006 1089;
1036 1091 1026 1016 1090; 1037 1092 1036 1026 1091; 1038 1093 1046 1036 1092;
1039 1094 1056 1046 1093; 1040 1095 1066 1056 1094; 1041 1096 1076 1066 1095;
1042 1097 712 1076 1096; 1043 1087 1098 1099 1088; 1044 1088 1099 1100 1089;
1045 1089 1100 1101 1090; 1046 1090 1101 1102 1091; 1047 1091 1102 1103 1092;
1048 1092 1103 1104 1093; 1049 1093 1104 1105 1094; 1050 1094 1105 1106 1095;
1051 1095 1106 1107 1096; 1052 1096 1107 1108 1097; 1053 560 561 1109 1078;
1054 1078 1109 1110 1079; 1055 1079 1110 1111 1080; 1056 1080 1111 1112 1081;
1057 1081 1112 1113 1082; 1058 1082 1113 1114 1083; 1059 1083 1114 1115 1084;
1060 1084 1115 1116 1085; 1061 1085 1116 1117 1086; 1062 1086 1117 722 721;
1063 1118 1119 671 665; 1064 670 686 1120 1121; 1065 1118 1087 551 665;
1066 670 651 957 1121; 1067 1098 1087 1118 1119; 1068 968 957 1121 1120;
1069 825 841 1122 1123; 1070 978 1122 1123 967; 1071 967 812 825 1123;
1072 1124 1125 826 820; 1073 1125 1124 1097 1108; 1074 1124 820 712 1097;
1147 1126 438 441 1127; 1148 1127 441 443 1128; 1149 1128 443 445 1129;
1150 1129 445 447 1130; 1151 1130 447 449 1131; 1152 1131 449 451 1132;
1153 1132 451 453 1133; 1154 1133 453 455 1134; 1155 1134 455 457 1135;
1156 1135 457 459 1136; 1157 1136 459 461 1137; 1158 1138 497 438 1126;
1159 464 1139 1140 465; 1160 465 1140 1141 467; 1161 467 1141 1142 469;
1162 469 1142 1143 471; 1163 471 1143 1144 473; 1164 473 1144 1145 475;
1165 475 1145 1146 477; 1166 477 1146 1147 479; 1167 479 1147 1148 481;
1168 481 1148 1149 483; 1169 483 1149 1150 485; 1170 500 1151 1139 464;
1171 1167 1137 461 1164; 1172 1164 461 460 1163; 1173 1163 460 428 1153;
1174 1153 428 427 1152; 1175 1152 427 429 1154; 1176 1154 429 430 1155;
1177 1155 430 431 1156; 1178 1156 431 432 1157; 1179 1157 432 433 1158;
1180 1158 433 434 1159; 1181 1159 434 435 1160; 1182 1160 435 436 1161;
1183 1161 436 437 1162; 1184 1162 437 484 1165; 1185 1165 484 485 1166;
1186 1166 485 1150 1168; 1187 1138 1184 1180 497; 1188 497 1180 1181 498;
1189 498 1181 1169 486; 1190 486 1169 1170 487; 1191 487 1170 1171 488;
1192 488 1171 1172 489; 1193 489 1172 1173 490; 1194 490 1173 1174 491;
1195 491 1174 1175 492; 1196 492 1175 1176 493; 1197 493 1176 1177 494;
1198 494 1177 1178 495; 1199 495 1178 1179 496; 1200 496 1179 1182 499;
1201 499 1182 1183 500; 1202 500 1183 1185 1151; 1203 501 70 74 503;
1204 70 59 63 74; 1205 59 48 52 63; 1206 48 502 504 52;
START GROUP DEFINITION
ELEMENT
_TCHANNEL 628 TO 632 758 TO 762 893 TO 902 1033 TO 1042 1065 1066 1071 1074
_BCHANNEL 623 TO 627 753 TO 757 883 TO 892 1023 TO 1032
_PIT 44 TO 47 54 TO 57 473 TO 476 481 TO 484
_RAFT 1 TO 33 38 TO 43 48 TO 53 58 TO 63 68 TO 100 469 TO 472 477 TO 480
JOINT
_PILE 2 10 17 57 65 105 112 120 432 438 449 459 464 473 483 491
END GROUP DEFINITION
ELEMENT PROPERTY
485 TO 505 507 TO 617 653 TO 752 783 TO 882 923 TO 1022 THICKNESS 0.3
623 TO 652 753 TO 782 883 TO 922 1023 TO 1074 THICKNESS 0.15
1 TO 33 38 TO 63 68 TO 100 401 TO 484 1147 TO 1206 THICKNESS 0.3
DEFINE MATERIAL START
ISOTROPIC CONCRETE
E 2.17185e+07
POISSON 0.17
DENSITY 23.5616
ALPHA 1e-05
DAMP 0.05
TYPE CONCRETE
STRENGTH FCU 27579
END DEFINE MATERIAL
MEMBER PROPERTY INDIAN
1075 TO 1146 PRIS YD 0.6 ZD 0.3
CONSTANTS
MATERIAL CONCRETE ALL
SUPPORTS
1 3 TO 9 11 TO 16 18 TO 47 49 TO 51 53 TO 56 58 60 TO 62 64 66 TO 69 -
71 TO 73 75 TO 104 106 TO 111 113 TO 119 121 427 TO 431 433 TO 437 -
439 TO 448 450 TO 458 460 TO 463 465 TO 472 474 TO 482 484 TO 490 -
492 TO 500 511 TO 516 518 TO 522 526 1126 TO 1184 -
1185 ELASTIC MAT DIRECT Y SUBGRADE 400 PRINT
2 10 17 57 65 105 112 120 432 438 449 459 464 473 483 491 517 523 TO 524 -
525 FIXED BUT KFX 52000 KFY 300000 KFZ 52000
DEFINE IS1893 2016 LOAD
ZONE 0.36 RF 4 I 1.5 SS 3 ST 4 DM 0.05 PX 0.09 PZ 0.123 DT 1.5
WALL AREA X
0.3 5;
WALL AREA Z
0.3 9;
SELFWEIGHT 1
LOAD 1 LOADTYPE Seismic-H TITLE EQX+
1893 LOAD X 1
PERFORM ANALYSIS
CHANGE
LOAD 2 LOADTYPE Seismic-H TITLE EQX-
1893 LOAD X -1
PERFORM ANALYSIS
CHANGE
LOAD 3 LOADTYPE Seismic-H TITLE EQZ+
1893 LOAD Z 1
PERFORM ANALYSIS
CHANGE
LOAD 4 LOADTYPE Seismic-H TITLE EQZ-
1893 LOAD Z -1
PERFORM ANALYSIS
CHANGE
LOAD 5 LOADTYPE Dead TITLE SELFWEIGHT
SELFWEIGHT Y -1
LOAD 6 LOADTYPE Dead TITLE SOILSUMP
ELEMENT LOAD
511 TRAP JT -10.8 -32.4 -32.4 -10.8
512 TRAP JT 0 -10.8 -10.8 0
513 TRAP JT -10.8 -32.4 -32.4 -10.8
514 TRAP JT 0 -10.8 -10.8 0
515 TRAP JT -10.8 -32.4 -32.4 -10.8
516 TRAP JT -10.8 -32.4 -32.4 -10.8
517 TRAP JT 0 -10.8 -10.8 0
510 TRAP JT 0 -10.8 -10.8 0
501 TRAP JT 0 10.8 10.8 0
502 TRAP JT 10.8 32.4 32.4 10.8
503 TRAP JT 0 10.8 10.8 0
504 TRAP JT 10.8 32.4 32.4 10.8
505 TRAP JT 0 10.8 10.8 0
507 TRAP JT 10.8 32.4 32.4 10.8
508 TRAP JT 10.8 32.4 32.4 10.8
509 TRAP JT 0 10.8 10.8 0
485 TRAP JT 0 10.8 10.8 0
486 TRAP JT 0 10.8 10.8 0
487 TRAP JT 0 10.8 10.8 0
488 TRAP JT 0 10.8 10.8 0
489 TRAP JT 10.8 32.4 32.4 10.8
490 TRAP JT 10.8 32.4 32.4 10.8
491 TRAP JT 10.8 32.4 32.4 10.8
492 TRAP JT 10.8 32.4 32.4 10.8
493 TRAP JT 0 -10.8 -10.8 0
494 TRAP JT 0 -10.8 -10.8 0
495 TRAP JT 0 -10.8 -10.8 0
496 TRAP JT 0 -10.8 -10.8 0
497 TRAP JT -10.8 -32.4 -32.4 -10.8
498 TRAP JT -10.8 -32.4 -32.4 -10.8
499 TRAP JT -10.8 -32.4 -32.4 -10.8
500 TRAP JT -10.8 -32.4 -32.4 -10.8
LOAD 7 LOADTYPE Dead TITLE SOILTANK
ELEMENT LOAD
924 TRAP JT 21.6 10.8 10.8 21.6
925 TRAP JT 10.8 0 0 10.8
933 TRAP JT 32.4 21.6 21.6 32.4
934 TRAP JT 21.6 10.8 10.8 21.6
935 TRAP JT 10.8 0 0 10.8
943 TRAP JT 32.4 21.6 21.6 32.4
944 TRAP JT 21.6 10.8 10.8 21.6
945 TRAP JT 10.8 0 0 10.8
953 TRAP JT 32.4 21.6 21.6 32.4
954 TRAP JT 21.6 10.8 10.8 21.6
955 TRAP JT 10.8 0 0 10.8
963 TRAP JT 32.4 21.6 21.6 32.4
964 TRAP JT 21.6 10.8 10.8 21.6
965 TRAP JT 10.8 0 0 10.8
973 TRAP JT 32.4 21.6 21.6 32.4
974 TRAP JT 21.6 10.8 10.8 21.6
975 TRAP JT 10.8 0 0 10.8
983 TRAP JT 32.4 21.6 21.6 32.4
984 TRAP JT 21.6 10.8 10.8 21.6
985 TRAP JT 10.8 0 0 10.8
993 TRAP JT 32.4 21.6 21.6 32.4
994 TRAP JT 21.6 10.8 10.8 21.6
995 TRAP JT 10.8 0 0 10.8
1003 TRAP JT 32.4 21.6 21.6 32.4
1004 TRAP JT 21.6 10.8 10.8 21.6
1005 TRAP JT 10.8 0 0 10.8
1013 TRAP JT 32.4 21.6 21.6 32.4
1014 TRAP JT 21.6 10.8 10.8 21.6
1015 TRAP JT 10.8 0 0 10.8
923 TRAP JT 32.4 21.6 21.6 32.4
783 TRAP JT -32.4 -21.6 -21.6 -32.4
784 TRAP JT -21.6 -10.8 -10.8 -21.6
785 TRAP JT -10.8 0 0 -10.8
793 TRAP JT -32.4 -21.6 -21.6 -32.4
794 TRAP JT -21.6 -10.8 -10.8 -21.6
795 TRAP JT -10.8 0 0 -10.8
803 TRAP JT -32.4 -21.6 -21.6 -32.4
804 TRAP JT -21.6 -10.8 -10.8 -21.6
805 TRAP JT -10.8 0 0 -10.8
813 TRAP JT -32.4 -21.6 -21.6 -32.4
814 TRAP JT -21.6 -10.8 -10.8 -21.6
815 TRAP JT -10.8 0 0 -10.8
823 TRAP JT -32.4 -21.6 -21.6 -32.4
824 TRAP JT -21.6 -10.8 -10.8 -21.6
825 TRAP JT -10.8 0 0 -10.8
833 TRAP JT -32.4 -21.6 -21.6 -32.4
834 TRAP JT -21.6 -10.8 -10.8 -21.6
835 TRAP JT -10.8 0 0 -10.8
843 TRAP JT -32.4 -21.6 -21.6 -32.4
844 TRAP JT -21.6 -10.8 -10.8 -21.6
845 TRAP JT -10.8 0 0 -10.8
853 TRAP JT -32.4 -21.6 -21.6 -32.4
854 TRAP JT -21.6 -10.8 -10.8 -21.6
855 TRAP JT -10.8 0 0 -10.8
863 TRAP JT -32.4 -21.6 -21.6 -32.4
864 TRAP JT -21.6 -10.8 -10.8 -21.6
865 TRAP JT -10.8 0 0 -10.8
873 TRAP JT -32.4 -21.6 -21.6 -32.4
874 TRAP JT -21.6 -10.8 -10.8 -21.6
875 TRAP JT -10.8 0 0 -10.8
653 TRAP JT 32.4 21.6 21.6 32.4
654 TRAP JT 21.6 10.8 10.8 21.6
655 TRAP JT 10.8 0 0 10.8
663 TRAP JT 32.4 21.6 21.6 32.4
664 TRAP JT 21.6 10.8 10.8 21.6
665 TRAP JT 10.8 0 0 10.8
673 TRAP JT 32.4 21.6 21.6 32.4
674 TRAP JT 21.6 10.8 10.8 21.6
675 TRAP JT 10.8 0 0 10.8
683 TRAP JT 32.4 21.6 21.6 32.4
684 TRAP JT 21.6 10.8 10.8 21.6
685 TRAP JT 10.8 0 0 10.8
693 TRAP JT 32.4 21.6 21.6 32.4
694 TRAP JT 21.6 10.8 10.8 21.6
695 TRAP JT 10.8 0 0 10.8
703 TRAP JT 32.4 21.6 21.6 32.4
704 TRAP JT 21.6 10.8 10.8 21.6
705 TRAP JT 10.8 0 0 10.8
713 TRAP JT 32.4 21.6 21.6 32.4
714 TRAP JT 21.6 10.8 10.8 21.6
715 TRAP JT 10.8 0 0 10.8
723 TRAP JT 32.4 21.6 21.6 32.4
724 TRAP JT 21.6 10.8 10.8 21.6
725 TRAP JT 10.8 0 0 10.8
733 TRAP JT 32.4 21.6 21.6 32.4
734 TRAP JT 21.6 10.8 10.8 21.6
735 TRAP JT 10.8 0 0 10.8
743 TRAP JT 32.4 21.6 21.6 32.4
744 TRAP JT 21.6 10.8 10.8 21.6
745 TRAP JT 10.8 0 0 10.8
518 TRAP JT -32.4 -21.6 -21.6 -32.4
519 TRAP JT -21.6 -10.8 -10.8 -21.6
520 TRAP JT -10.8 0 0 -10.8
528 TRAP JT -32.4 -21.6 -21.6 -32.4
529 TRAP JT -21.6 -10.8 -10.8 -21.6
530 TRAP JT -10.8 0 0 -10.8
538 TRAP JT -32.4 -21.6 -21.6 -32.4
539 TRAP JT -21.6 -10.8 -10.8 -21.6
540 TRAP JT -10.8 0 0 -10.8
548 TRAP JT -32.4 -21.6 -21.6 -32.4
549 TRAP JT -21.6 -10.8 -10.8 -21.6
550 TRAP JT -10.8 0 0 -10.8
558 TRAP JT -32.4 -21.6 -21.6 -32.4
559 TRAP JT -21.6 -10.8 -10.8 -21.6
560 TRAP JT -10.8 0 0 -10.8
568 TRAP JT -32.4 -21.6 -21.6 -32.4
569 TRAP JT -21.6 -10.8 -10.8 -21.6
570 TRAP JT -10.8 0 0 -10.8
578 TRAP JT -32.4 -21.6 -21.6 -32.4
579 TRAP JT -21.6 -10.8 -10.8 -21.6
580 TRAP JT -10.8 0 0 -10.8
588 TRAP JT -32.4 -21.6 -21.6 -32.4
589 TRAP JT -21.6 -10.8 -10.8 -21.6
590 TRAP JT -10.8 0 0 -10.8
598 TRAP JT -32.4 -21.6 -21.6 -32.4
599 TRAP JT -21.6 -10.8 -10.8 -21.6
600 TRAP JT -10.8 0 0 -10.8
608 TRAP JT -32.4 -21.6 -21.6 -32.4
609 TRAP JT -21.6 -10.8 -10.8 -21.6
610 TRAP JT -10.8 0 0 -10.8
LOAD 8 LOADTYPE Roof Live TITLE WATERPRESTANK
ELEMENT LOAD
654 TRAP JT -34.335 -29.43 -29.43 -34.335
655 TRAP JT -29.43 -24.525 -24.525 -29.43
656 TRAP JT -24.525 -19.62 -19.62 -24.525
657 TRAP JT -19.62 -14.715 -14.715 -19.62
658 TRAP JT -14.715 -9.81 -9.81 -14.715
659 TRAP JT -9.81 -4.905 -4.905 -9.81
660 TRAP JT -4.905 0 0 -4.905
663 TRAP JT -39.24 -34.335 -34.335 -39.24
664 TRAP JT -34.335 -29.43 -29.43 -34.335
665 TRAP JT -29.43 -24.525 -24.525 -29.43
666 TRAP JT -24.525 -19.62 -19.62 -24.525
667 TRAP JT -19.62 -14.715 -14.715 -19.62
668 TRAP JT -14.715 -9.81 -9.81 -14.715
669 TRAP JT -9.81 -4.905 -4.905 -9.81
670 TRAP JT -4.905 0 0 -4.905
673 TRAP JT -39.24 -34.335 -34.335 -39.24
674 TRAP JT -34.335 -29.43 -29.43 -34.335
675 TRAP JT -29.43 -24.525 -24.525 -29.43
676 TRAP JT -24.525 -19.62 -19.62 -24.525
677 TRAP JT -19.62 -14.715 -14.715 -19.62
678 TRAP JT -14.715 -9.81 -9.81 -14.715
679 TRAP JT -9.81 -4.905 -4.905 -9.81
680 TRAP JT -4.905 0 0 -4.905
683 TRAP JT -39.24 -34.335 -34.335 -39.24
684 TRAP JT -34.335 -29.43 -29.43 -34.335
685 TRAP JT -29.43 -24.525 -24.525 -29.43
686 TRAP JT -24.525 -19.62 -19.62 -24.525
687 TRAP JT -19.62 -14.715 -14.715 -19.62
688 TRAP JT -14.715 -9.81 -9.81 -14.715
689 TRAP JT -9.81 -4.905 -4.905 -9.81
690 TRAP JT -4.905 0 0 -4.905
693 TRAP JT -39.24 -34.335 -34.335 -39.24
694 TRAP JT -34.335 -29.43 -29.43 -34.335
695 TRAP JT -29.43 -24.525 -24.525 -29.43
696 TRAP JT -24.525 -19.62 -19.62 -24.525
697 TRAP JT -19.62 -14.715 -14.715 -19.62
698 TRAP JT -14.715 -9.81 -9.81 -14.715
699 TRAP JT -9.81 -4.905 -4.905 -9.81
700 TRAP JT -4.905 0 0 -4.905
703 TRAP JT -39.24 -34.335 -34.335 -39.24
704 TRAP JT -34.335 -29.43 -29.43 -34.335
705 TRAP JT -29.43 -24.525 -24.525 -29.43
706 TRAP JT -24.525 -19.62 -19.62 -24.525
707 TRAP JT -19.62 -14.715 -14.715 -19.62
708 TRAP JT -14.715 -9.81 -9.81 -14.715
709 TRAP JT -9.81 -4.905 -4.905 -9.81
710 TRAP JT -4.905 0 0 -4.905
713 TRAP JT -39.24 -34.335 -34.335 -39.24
714 TRAP JT -34.335 -29.43 -29.43 -34.335
715 TRAP JT -29.43 -24.525 -24.525 -29.43
716 TRAP JT -24.525 -19.62 -19.62 -24.525
717 TRAP JT -19.62 -14.715 -14.715 -19.62
718 TRAP JT -14.715 -9.81 -9.81 -14.715
719 TRAP JT -9.81 -4.905 -4.905 -9.81
720 TRAP JT -4.905 0 0 -4.905
723 TRAP JT -39.24 -34.335 -34.335 -39.24
724 TRAP JT -34.335 -29.43 -29.43 -34.335
725 TRAP JT -29.43 -24.525 -24.525 -29.43
726 TRAP JT -24.525 -19.62 -19.62 -24.525
727 TRAP JT -19.62 -14.715 -14.715 -19.62
728 TRAP JT -14.715 -9.81 -9.81 -14.715
729 TRAP JT -9.81 -4.905 -4.905 -9.81
730 TRAP JT -4.905 0 0 -4.905
733 TRAP JT -39.24 -34.335 -34.335 -39.24
734 TRAP JT -34.335 -29.43 -29.43 -34.335
735 TRAP JT -29.43 -24.525 -24.525 -29.43
736 TRAP JT -24.525 -19.62 -19.62 -24.525
737 TRAP JT -19.62 -14.715 -14.715 -19.62
738 TRAP JT -14.715 -9.81 -9.81 -14.715
739 TRAP JT -9.81 -4.905 -4.905 -9.81
740 TRAP JT -4.905 0 0 -4.905
743 TRAP JT -39.24 -34.335 -34.335 -39.24
744 TRAP JT -34.335 -29.43 -29.43 -34.335
745 TRAP JT -29.43 -24.525 -24.525 -29.43
746 TRAP JT -24.525 -19.62 -19.62 -24.525
747 TRAP JT -19.62 -14.715 -14.715 -19.62
748 TRAP JT -14.715 -9.81 -9.81 -14.715
749 TRAP JT -9.81 -4.905 -4.905 -9.81
750 TRAP JT -4.905 0 0 -4.905
653 TRAP JT -39.24 -34.335 -34.335 -39.24
518 TRAP JT 39.24 34.335 34.335 39.24
519 TRAP JT 34.335 29.43 29.43 34.335
520 TRAP JT 29.43 24.525 24.525 29.43
521 TRAP JT 24.525 19.62 19.62 24.525
522 TRAP JT 19.62 14.715 14.715 19.62
523 TRAP JT 14.715 9.81 9.81 14.715
524 TRAP JT 9.81 4.905 4.905 9.81
525 TRAP JT 4.905 0 0 4.905
528 TRAP JT 39.24 34.335 34.335 39.24
529 TRAP JT 34.335 29.43 29.43 34.335
530 TRAP JT 29.43 24.525 24.525 29.43
531 TRAP JT 24.525 19.62 19.62 24.525
532 TRAP JT 19.62 14.715 14.715 19.62
533 TRAP JT 14.715 9.81 9.81 14.715
534 TRAP JT 9.81 4.905 4.905 9.81
535 TRAP JT 4.905 0 0 4.905
538 TRAP JT 39.24 34.335 34.335 39.24
539 TRAP JT 34.335 29.43 29.43 34.335
540 TRAP JT 29.43 24.525 24.525 29.43
541 TRAP JT 24.525 19.62 19.62 24.525
542 TRAP JT 19.62 14.715 14.715 19.62
543 TRAP JT 14.715 9.81 9.81 14.715
544 TRAP JT 9.81 4.905 4.905 9.81
545 TRAP JT 4.905 0 0 4.905
548 TRAP JT 39.24 34.335 34.335 39.24
549 TRAP JT 34.335 29.43 29.43 34.335
550 TRAP JT 29.43 24.525 24.525 29.43
551 TRAP JT 24.525 19.62 19.62 24.525
552 TRAP JT 19.62 14.715 14.715 19.62
553 TRAP JT 14.715 9.81 9.81 14.715
554 TRAP JT 9.81 4.905 4.905 9.81
555 TRAP JT 4.905 0 0 4.905
558 TRAP JT 39.24 34.335 34.335 39.24
559 TRAP JT 34.335 29.43 29.43 34.335
560 TRAP JT 29.43 24.525 24.525 29.43
561 TRAP JT 24.525 19.62 19.62 24.525
562 TRAP JT 19.62 14.715 14.715 19.62
563 TRAP JT 14.715 9.81 9.81 14.715
564 TRAP JT 9.81 4.905 4.905 9.81
565 TRAP JT 4.905 0 0 4.905
568 TRAP JT 39.24 34.335 34.335 39.24
569 TRAP JT 34.335 29.43 29.43 34.335
570 TRAP JT 29.43 24.525 24.525 29.43
571 TRAP JT 24.525 19.62 19.62 24.525
572 TRAP JT 19.62 14.715 14.715 19.62
573 TRAP JT 14.715 9.81 9.81 14.715
574 TRAP JT 9.81 4.905 4.905 9.81
575 TRAP JT 4.905 0 0 4.905
578 TRAP JT 39.24 34.335 34.335 39.24
579 TRAP JT 34.335 29.43 29.43 34.335
580 TRAP JT 29.43 24.525 24.525 29.43
581 TRAP JT 24.525 19.62 19.62 24.525
582 TRAP JT 19.62 14.715 14.715 19.62
583 TRAP JT 14.715 9.81 9.81 14.715
584 TRAP JT 9.81 4.905 4.905 9.81
585 TRAP JT 4.905 0 0 4.905
588 TRAP JT 39.24 34.335 34.335 39.24
589 TRAP JT 34.335 29.43 29.43 34.335
590 TRAP JT 29.43 24.525 24.525 29.43
591 TRAP JT 24.525 19.62 19.62 24.525
592 TRAP JT 19.62 14.715 14.715 19.62
593 TRAP JT 14.715 9.81 9.81 14.715
594 TRAP JT 9.81 4.905 4.905 9.81
595 TRAP JT 4.905 0 0 4.905
598 TRAP JT 39.24 34.335 34.335 39.24
599 TRAP JT 34.335 29.43 29.43 34.335
600 TRAP JT 29.43 24.525 24.525 29.43
601 TRAP JT 24.525 19.62 19.62 24.525
602 TRAP JT 19.62 14.715 14.715 19.62
603 TRAP JT 14.715 9.81 9.81 14.715
604 TRAP JT 9.81 4.905 4.905 9.81
605 TRAP JT 4.905 0 0 4.905
608 TRAP JT 39.24 34.335 34.335 39.24
609 TRAP JT 34.335 29.43 29.43 34.335
610 TRAP JT 29.43 24.525 24.525 29.43
611 TRAP JT 24.525 19.62 19.62 24.525
612 TRAP JT 19.62 14.715 14.715 19.62
613 TRAP JT 14.715 9.81 9.81 14.715
614 TRAP JT 9.81 4.905 4.905 9.81
615 TRAP JT 4.905 0 0 4.905
923 TRAP JT -39.24 -34.335 -34.335 -39.24
924 TRAP JT -34.335 -29.43 -29.43 -34.335
925 TRAP JT -29.43 -24.525 -24.525 -29.43
926 TRAP JT -24.525 -19.62 -19.62 -24.525
927 TRAP JT -19.62 -14.715 -14.715 -19.62
928 TRAP JT -14.715 -9.81 -9.81 -14.715
929 TRAP JT -9.81 -4.905 -4.905 -9.81
930 TRAP JT -4.905 0 0 -4.905
933 TRAP JT -39.24 -34.335 -34.335 -39.24
934 TRAP JT -34.335 -29.43 -29.43 -34.335
935 TRAP JT -29.43 -24.525 -24.525 -29.43
936 TRAP JT -24.525 -19.62 -19.62 -24.525
937 TRAP JT -19.62 -14.715 -14.715 -19.62
938 TRAP JT -14.715 -9.81 -9.81 -14.715
939 TRAP JT -9.81 -4.905 -4.905 -9.81
940 TRAP JT -4.905 0 0 -4.905
943 TRAP JT -39.24 -34.335 -34.335 -39.24
944 TRAP JT -34.335 -29.43 -29.43 -34.335
945 TRAP JT -29.43 -24.525 -24.525 -29.43
946 TRAP JT -24.525 -19.62 -19.62 -24.525
947 TRAP JT -19.62 -14.715 -14.715 -19.62
948 TRAP JT -14.715 -9.81 -9.81 -14.715
949 TRAP JT -9.81 -4.905 -4.905 -9.81
950 TRAP JT -4.905 0 0 -4.905
953 TRAP JT -39.24 -34.335 -34.335 -39.24
954 TRAP JT -34.335 -29.43 -29.43 -34.335
955 TRAP JT -29.43 -24.525 -24.525 -29.43
956 TRAP JT -24.525 -19.62 -19.62 -24.525
957 TRAP JT -19.62 -14.715 -14.715 -19.62
958 TRAP JT -14.715 -9.81 -9.81 -14.715
959 TRAP JT -9.81 -4.905 -4.905 -9.81
960 TRAP JT -4.905 0 0 -4.905
963 TRAP JT -39.24 -34.335 -34.335 -39.24
964 TRAP JT -34.335 -29.43 -29.43 -34.335
965 TRAP JT -29.43 -24.525 -24.525 -29.43
966 TRAP JT -24.525 -19.62 -19.62 -24.525
967 TRAP JT -19.62 -14.715 -14.715 -19.62
968 TRAP JT -14.715 -9.81 -9.81 -14.715
969 TRAP JT -9.81 -4.905 -4.905 -9.81
970 TRAP JT -4.905 0 0 -4.905
973 TRAP JT -39.24 -34.335 -34.335 -39.24
974 TRAP JT -34.335 -29.43 -29.43 -34.335
975 TRAP JT -29.43 -24.525 -24.525 -29.43
976 TRAP JT -24.525 -19.62 -19.62 -24.525
977 TRAP JT -19.62 -14.715 -14.715 -19.62
978 TRAP JT -14.715 -9.81 -9.81 -14.715
979 TRAP JT -9.81 -4.905 -4.905 -9.81
980 TRAP JT -4.905 0 0 -4.905
983 TRAP JT -39.24 -34.335 -34.335 -39.24
984 TRAP JT -34.335 -29.43 -29.43 -34.335
985 TRAP JT -29.43 -24.525 -24.525 -29.43
986 TRAP JT -24.525 -19.62 -19.62 -24.525
987 TRAP JT -19.62 -14.715 -14.715 -19.62
988 TRAP JT -14.715 -9.81 -9.81 -14.715
989 TRAP JT -9.81 -4.905 -4.905 -9.81
990 TRAP JT -4.905 0 0 -4.905
993 TRAP JT -39.24 -34.335 -34.335 -39.24
994 TRAP JT -34.335 -29.43 -29.43 -34.335
995 TRAP JT -29.43 -24.525 -24.525 -29.43
996 TRAP JT -24.525 -19.62 -19.62 -24.525
997 TRAP JT -19.62 -14.715 -14.715 -19.62
998 TRAP JT -14.715 -9.81 -9.81 -14.715
999 TRAP JT -9.81 -4.905 -4.905 -9.81
1000 TRAP JT -4.905 0 0 -4.905
1003 TRAP JT -39.24 -34.335 -34.335 -39.24
1004 TRAP JT -34.335 -29.43 -29.43 -34.335
1005 TRAP JT -29.43 -24.525 -24.525 -29.43
1006 TRAP JT -24.525 -19.62 -19.62 -24.525
1007 TRAP JT -19.62 -14.715 -14.715 -19.62
1008 TRAP JT -14.715 -9.81 -9.81 -14.715
1009 TRAP JT -9.81 -4.905 -4.905 -9.81
1010 TRAP JT -4.905 0 0 -4.905
1013 TRAP JT -39.24 -34.335 -34.335 -39.24
1014 TRAP JT -34.335 -29.43 -29.43 -34.335
1015 TRAP JT -29.43 -24.525 -24.525 -29.43
1016 TRAP JT -24.525 -19.62 -19.62 -24.525
1017 TRAP JT -19.62 -14.715 -14.715 -19.62
1018 TRAP JT -14.715 -9.81 -9.81 -14.715
1019 TRAP JT -9.81 -4.905 -4.905 -9.81
1020 TRAP JT -4.905 0 0 -4.905
783 TRAP JT 39.24 34.335 34.335 39.24
784 TRAP JT 34.335 29.43 29.43 34.335
785 TRAP JT 29.43 24.525 24.525 29.43
786 TRAP JT 24.525 19.62 19.62 24.525
787 TRAP JT 19.62 14.715 14.715 19.62
788 TRAP JT 14.715 9.81 9.81 14.715
789 TRAP JT 9.81 4.905 4.905 9.81
790 TRAP JT 4.905 0 0 4.905
793 TRAP JT 39.24 34.335 34.335 39.24
794 TRAP JT 34.335 29.43 29.43 34.335
795 TRAP JT 29.43 24.525 24.525 29.43
796 TRAP JT 24.525 19.62 19.62 24.525
797 TRAP JT 19.62 14.715 14.715 19.62
798 TRAP JT 14.715 9.81 9.81 14.715
799 TRAP JT 9.81 4.905 4.905 9.81
800 TRAP JT 4.905 0 0 4.905
803 TRAP JT 39.24 34.335 34.335 39.24
804 TRAP JT 34.335 29.43 29.43 34.335
805 TRAP JT 29.43 24.525 24.525 29.43
806 TRAP JT 24.525 19.62 19.62 24.525
807 TRAP JT 19.62 14.715 14.715 19.62
808 TRAP JT 14.715 9.81 9.81 14.715
809 TRAP JT 9.81 4.905 4.905 9.81
810 TRAP JT 4.905 0 0 4.905
813 TRAP JT 39.24 34.335 34.335 39.24
814 TRAP JT 34.335 29.43 29.43 34.335
815 TRAP JT 29.43 24.525 24.525 29.43
816 TRAP JT 24.525 19.62 19.62 24.525
817 TRAP JT 19.62 14.715 14.715 19.62
818 TRAP JT 14.715 9.81 9.81 14.715
819 TRAP JT 9.81 4.905 4.905 9.81
820 TRAP JT 4.905 0 0 4.905
823 TRAP JT 39.24 34.335 34.335 39.24
824 TRAP JT 34.335 29.43 29.43 34.335
825 TRAP JT 29.43 24.525 24.525 29.43
826 TRAP JT 24.525 19.62 19.62 24.525
827 TRAP JT 19.62 14.715 14.715 19.62
828 TRAP JT 14.715 9.81 9.81 14.715
829 TRAP JT 9.81 4.905 4.905 9.81
830 TRAP JT 4.905 0 0 4.905
833 TRAP JT 39.24 34.335 34.335 39.24
834 TRAP JT 34.335 29.43 29.43 34.335
835 TRAP JT 29.43 24.525 24.525 29.43
836 TRAP JT 24.525 19.62 19.62 24.525
837 TRAP JT 19.62 14.715 14.715 19.62
838 TRAP JT 14.715 9.81 9.81 14.715
839 TRAP JT 9.81 4.905 4.905 9.81
840 TRAP JT 4.905 0 0 4.905
843 TRAP JT 39.24 34.335 34.335 39.24
844 TRAP JT 34.335 29.43 29.43 34.335
845 TRAP JT 29.43 24.525 24.525 29.43
846 TRAP JT 24.525 19.62 19.62 24.525
847 TRAP JT 19.62 14.715 14.715 19.62
848 TRAP JT 14.715 9.81 9.81 14.715
849 TRAP JT 9.81 4.905 4.905 9.81
850 TRAP JT 4.905 0 0 4.905
853 TRAP JT 39.24 34.335 34.335 39.24
854 TRAP JT 34.335 29.43 29.43 34.335
855 TRAP JT 29.43 24.525 24.525 29.43
856 TRAP JT 24.525 19.62 19.62 24.525
857 TRAP JT 19.62 14.715 14.715 19.62
858 TRAP JT 14.715 9.81 9.81 14.715
859 TRAP JT 9.81 4.905 4.905 9.81
860 TRAP JT 4.905 0 0 4.905
863 TRAP JT 39.24 34.335 34.335 39.24
864 TRAP JT 34.335 29.43 29.43 34.335
865 TRAP JT 29.43 24.525 24.525 29.43
866 TRAP JT 24.525 19.62 19.62 24.525
867 TRAP JT 19.62 14.715 14.715 19.62
868 TRAP JT 14.715 9.81 9.81 14.715
869 TRAP JT 9.81 4.905 4.905 9.81
870 TRAP JT 4.905 0 0 4.905
873 TRAP JT 39.24 34.335 34.335 39.24
874 TRAP JT 34.335 29.43 29.43 34.335
875 TRAP JT 29.43 24.525 24.525 29.43
876 TRAP JT 24.525 19.62 19.62 24.525
877 TRAP JT 19.62 14.715 14.715 19.62
878 TRAP JT 14.715 9.81 9.81 14.715
879 TRAP JT 9.81 4.905 4.905 9.81
880 TRAP JT 4.905 0 0 4.905
LOAD 9 LOADTYPE Live TITLE WATERPRESCHANNEL
ELEMENT LOAD
634 TRAP JT 1.962 0 0 1.962
635 TRAP JT 1.962 0 0 1.962
636 TRAP JT 1.962 0 0 1.962
637 TRAP JT 1.962 0 0 1.962
638 TRAP JT 1.962 0 0 1.962
639 TRAP JT 1.962 0 0 1.962
640 TRAP JT 1.962 0 0 1.962
641 TRAP JT 1.962 0 0 1.962
642 TRAP JT 1.962 0 0 1.962
773 TRAP JT 3.924 1.962 1.962 3.924
774 TRAP JT 3.924 1.962 1.962 3.924
775 TRAP JT 3.924 1.962 1.962 3.924
776 TRAP JT 3.924 1.962 1.962 3.924
777 TRAP JT 3.924 1.962 1.962 3.924
778 TRAP JT 3.924 1.962 1.962 3.924
779 TRAP JT 3.924 1.962 1.962 3.924
780 TRAP JT 3.924 1.962 1.962 3.924
781 TRAP JT 3.924 1.962 1.962 3.924
782 TRAP JT 3.924 1.962 1.962 3.924
1063 TRAP JT 1.962 0 0 1.962
1064 TRAP JT 1.962 0 0 1.962
633 TRAP JT 1.962 0 0 1.962
643 TRAP JT -3.924 -1.962 -1.962 -3.924
644 TRAP JT -3.924 -1.962 -1.962 -3.924
645 TRAP JT -3.924 -1.962 -1.962 -3.924
646 TRAP JT -3.924 -1.962 -1.962 -3.924
647 TRAP JT -3.924 -1.962 -1.962 -3.924
648 TRAP JT -3.924 -1.962 -1.962 -3.924
649 TRAP JT -3.924 -1.962 -1.962 -3.924
650 TRAP JT -3.924 -1.962 -1.962 -3.924
651 TRAP JT -3.924 -1.962 -1.962 -3.924
652 TRAP JT -3.924 -1.962 -1.962 -3.924
763 TRAP JT -1.962 0 0 -1.962
764 TRAP JT -1.962 0 0 -1.962
765 TRAP JT -1.962 0 0 -1.962
766 TRAP JT -1.962 0 0 -1.962
767 TRAP JT -1.962 0 0 -1.962
768 TRAP JT -1.962 0 0 -1.962
769 TRAP JT -1.962 0 0 -1.962
770 TRAP JT -1.962 0 0 -1.962
771 TRAP JT -1.962 0 0 -1.962
772 TRAP JT -1.962 0 0 -1.962
1069 TRAP JT -1.962 0 0 -1.962
1072 TRAP JT -1.962 0 0 -1.962
913 TRAP JT -3.924 -1.962 -1.962 -3.924
914 TRAP JT -3.924 -1.962 -1.962 -3.924
915 TRAP JT -3.924 -1.962 -1.962 -3.924
916 TRAP JT -3.924 -1.962 -1.962 -3.924
917 TRAP JT -3.924 -1.962 -1.962 -3.924
918 TRAP JT -3.924 -1.962 -1.962 -3.924
919 TRAP JT -3.924 -1.962 -1.962 -3.924
920 TRAP JT -3.924 -1.962 -1.962 -3.924
921 TRAP JT -3.924 -1.962 -1.962 -3.924
922 TRAP JT -3.924 -1.962 -1.962 -3.924
1043 TRAP JT -1.962 0 0 -1.962
1044 TRAP JT -1.962 0 0 -1.962
1045 TRAP JT -1.962 0 0 -1.962
1046 TRAP JT -1.962 0 0 -1.962
1047 TRAP JT -1.962 0 0 -1.962
1048 TRAP JT -1.962 0 0 -1.962
1049 TRAP JT -1.962 0 0 -1.962
1050 TRAP JT -1.962 0 0 -1.962
1051 TRAP JT -1.962 0 0 -1.962
1052 TRAP JT -1.962 0 0 -1.962
1067 TRAP JT 0 -1.962 -1.962 0
1073 TRAP JT 0 -1.962 -1.962 0
903 TRAP JT 1.962 0 0 1.962
904 TRAP JT 1.962 0 0 1.962
905 TRAP JT 1.962 0 0 1.962
906 TRAP JT 1.962 0 0 1.962
907 TRAP JT 1.962 0 0 1.962
908 TRAP JT 1.962 0 0 1.962
909 TRAP JT 1.962 0 0 1.962
910 TRAP JT 1.962 0 0 1.962
911 TRAP JT 1.962 0 0 1.962
912 TRAP JT 1.962 0 0 1.962
1053 TRAP JT 3.924 1.962 1.962 3.924
1054 TRAP JT 3.924 1.962 1.962 3.924
1055 TRAP JT 3.924 1.962 1.962 3.924
1056 TRAP JT 3.924 1.962 1.962 3.924
1057 TRAP JT 3.924 1.962 1.962 3.924
1058 TRAP JT 3.924 1.962 1.962 3.924
1059 TRAP JT 3.924 1.962 1.962 3.924
1060 TRAP JT 3.924 1.962 1.962 3.924
1061 TRAP JT 3.924 1.962 1.962 3.924
1062 TRAP JT 3.924 1.962 1.962 3.924
1068 TRAP JT 0 1.962 1.962 0
1070 TRAP JT 0 0 1.962 1.962
LOAD 10 LOADTYPE Live TITLE WATERPRESBASE
ELEMENT LOAD
623 TO 632 753 TO 762 883 TO 902 1023 TO 1042 1065 1066 1071 1074 PR -3.924
1 TO 33 38 TO 43 48 TO 53 58 TO 63 68 TO 100 469 TO 472 477 TO 480 PR -24.52
44 TO 47 54 TO 57 473 TO 476 481 TO 484 PR 14.715
1203 TO 1206 PR -39.24
LOAD COMB 11 ULC, 1.5 (DEAD + LIVE)
5 1.5 6 1.5 7 1.5 9 1.5 10 1.5
LOAD COMB 12 ULC, 1.2 (DEAD + LIVE)
5 1.2 6 1.2 7 1.2 9 1.2 10 1.2
LOAD COMB 13 ULC, 1.2( DEAD + LIVE + SEISMIC (1))
5 1.2 6 1.2 7 1.2 9 1.2 10 1.2 1 1.2
LOAD COMB 14 ULC, 1.2 (DEAD + LIVE + SEISMIC (2))
5 1.2 6 1.2 7 1.2 9 1.2 10 1.2 2 1.2
LOAD COMB 15 ULC, 1.2 (DEAD + LIVE + SEISMIC (3))
5 1.2 6 1.2 7 1.2 9 1.2 10 1.2 3 1.2
LOAD COMB 16 ULC, 1.2 (DEAD + LIVE + SEISMIC (4))
5 1.2 6 1.2 7 1.2 9 1.2 10 1.2 4 1.2
LOAD COMB 17 ULC, 1.2 (DEAD + LIVE) + -1.2 SEISMIC (1)
5 1.2 6 1.2 7 1.2 9 1.2 10 1.2 1 -1.2
LOAD COMB 18 ULC, 1.2 (DEAD + LIVE) + -1.2 SEISMIC (2)
5 1.2 6 1.2 7 1.2 9 1.2 10 1.2 2 -1.2
LOAD COMB 19 ULC, 1.2 (DEAD + LIVE) + -1.2 SEISMIC (3)
5 1.2 6 1.2 7 1.2 9 1.2 10 1.2 3 -1.2
LOAD COMB 20 ULC, 1.2 (DEAD + LIVE) + -1.2 SEISMIC (4)
5 1.2 6 1.2 7 1.2 9 1.2 10 1.2 4 -1.2
LOAD COMB 21 ULC, 1.5 DEAD
5 1.5 6 1.5 7 1.5
LOAD COMB 22 ULC, 1.5 (DEAD + SEISMIC (1))
5 1.5 6 1.5 7 1.5 1 1.5
LOAD COMB 23 ULC, 1.5 (DEAD + SEISMIC (2))
5 1.5 6 1.5 7 1.5 2 1.5
LOAD COMB 24 ULC, 1.5( DEAD + SEISMIC (3))
5 1.5 6 1.5 7 1.5 3 1.5
LOAD COMB 25 ULC, 1.5 (DEAD + SEISMIC (4))
5 1.5 6 1.5 7 1.5 4 1.5
LOAD COMB 26 ULC, 1.5 DEAD + -1.5 SEISMIC (1)
5 1.5 6 1.5 7 1.5 1 -1.5
LOAD COMB 27 ULC, 1.5 DEAD + -1.5 SEISMIC (2)
5 1.5 6 1.5 7 1.5 2 -1.5
LOAD COMB 28 ULC, 1.5 DEAD + -1.5 SEISMIC (3)
5 1.5 6 1.5 7 1.5 3 -1.5
LOAD COMB 29 ULC, 1.5 DEAD + -1.5 SEISMIC (4)
5 1.5 6 1.5 7 1.5 4 -1.5
LOAD COMB 30 ULC, 0.9 DEAD
5 0.9 6 0.9 7 0.9
LOAD COMB 31 ULC, 0.9 DEAD + 1.5 SEISMIC (1)
5 0.9 6 0.9 7 0.9 1 1.5
LOAD COMB 32 ULC, 0.9 DEAD + 1.5 SEISMIC (2)
5 0.9 6 0.9 7 0.9 2 1.5
LOAD COMB 33 ULC, 0.9 DEAD + 1.5 SEISMIC (3)
5 0.9 6 0.9 7 0.9 3 1.5
LOAD COMB 34 ULC, 0.9 DEAD + 1.5 SEISMIC (4)
5 0.9 6 0.9 7 0.9 4 1.5
LOAD COMB 35 ULC, 0.9 DEAD + -1.5 SEISMIC (1)
5 0.9 6 0.9 7 0.9 1 -1.5
LOAD COMB 36 ULC, 0.9 DEAD + -1.5 SEISMIC (2)
5 0.9 6 0.9 7 0.9 2 -1.5
LOAD COMB 37 ULC, 0.9 DEAD + -1.5 SEISMIC (3)
5 0.9 6 0.9 7 0.9 3 -1.5
LOAD COMB 38 ULC, 0.9 DEAD + -1.5 SEISMIC (4)
5 0.9 6 0.9 7 0.9 4 -1.5
LOAD COMB 39 1.5(EQ+TANKFULL+NOBACKFILL)
1 1.0 2 1.0 3 1.0 4 1.0 5 1.0 8 1.0 9 1.0 10 1.0
PERFORM ANALYSIS
CHANGE
START CONCRETE DESIGN
CODE INDIAN
FC 30000 MEMB 1 TO 33 38 TO 63 68 TO 100 401 TO 505 507 TO 617 623 TO 1146
FYMAIN 500000 MEMB 1 TO 33 38 TO 63 68 TO 100 401 TO 505 507 TO 617 623 TO 1146
FYSEC 500000 ALL
MAXMAIN 16 ALL
MAXSEC 16 ALL
MINMAIN 8 ALL
MINSEC 8 ALL
DESIGN ELEMENT 1 TO 33 38 TO 63 68 TO 100 401 TO 505 507 TO 617 623 TO 1074 -
1147 TO 1170
ENSH 1 ALL
DESIGN BEAM 1075 TO 1146
END CONCRETE DESIGN
FINISH |