PostPosted: Thu May 12, 2022 7:02 am    Post subject: STRENGTHENING OF BEAMS Reply with quote
Dear Vikram
Thank you for your response.
Is there any other options available for decreasing the deflection of the long span beam.
Thank you
_________________
Yours
Er. S.Logesh
PostPosted: Thu May 12, 2022 9:22 am    Post subject: Reply with quote
60 feet span beam
Section of 230x600 mm is grossly less from deflection as well as design oint of view - fear shear stress check may dictate increase of section.
If a T beam ,  take advantage of flanges in deflection  check , better model slabs also as plate elements. Deflection and support moments may reduce in complete model .
Other option is to make composite section of rcc 230x 600mm Plus 100x 200mm ISMB 200 , two nos one 100mm below top and other one 100mm above bottom can be composited/ fused in rcc work and advantage can be taken in design and deflection check.
PostPosted: Thu May 12, 2022 9:42 am    Post subject: Reply with quote
Further to add to above post regarding composite section :
ISMB 200 steel girders be provided one row of WEB holes at its mid depth  minimum 25mm dia  at certain intervals for concrete flow . links can be inserted thru holes to make section monolithic.
Or other wise  use 2 nos ISMB 150 , section 80x150 , it may give u a gap of 100mm in mid depth of rcc beam. But all depend on how much additional strength needed from steel combo sections.
pvgraju
PostPosted: Thu May 12, 2022 10:09 am    Post subject: Strengthening of Concrete structure after construction Reply with quote
Providing pre camber to beam will also reduce total deflection.
P.V.Gavarraju.
PostPosted: Thu May 12, 2022 10:16 am    Post subject: Reply with quote
Yes cambering is must in such long span beam as age old practice at site  and mention of same be given thru notes.
logeshcivil
PostPosted: Thu May 12, 2022 11:14 am    Post subject: STRENGTHENING OF BEAMS Reply with quote
Dear sirs
Thank you for your suggestions.
Pre cambering is not possible since the structure is already completed.
Skilled labor is not available for using composite structures an also the client is not keen on providing steel beams.
Thank you
_________________
Yours
Er. S.Logesh
PostPosted: Fri May 13, 2022 8:47 am    Post subject: Reply with quote
But steel beams are hidden in rcc beam and will provide you much needed MOI for deflection limit fulfilment as also share strength.
logeshcivil
PostPosted: Tue May 17, 2022 5:17 am    Post subject: STRENGTHENING OF BEAMS Reply with quote
Dear Vikram
Thank you for your suggestion.
Using of composite section is not possible as the structure is  already completed and only the plastering of the structure remains.
As i have explained, i have planned to decrease the span of the beam by providing the steel columns.
Is there any other options for beam deflection control.
_________________
Yours
Er. S.Logesh
PostPosted: Thu May 19, 2022 1:41 am    Post subject: Reply with quote
Providing steel column may be objected by Architect /owner in a column free space .
Steel option of strengthening is still there even if rcc beam is cast.
My view is to provide side steel plates of full span length anchored to beam web with two rows at certain spacing as per design dictate and can be painted / camouflaged to merge as rcc. Even a bottom plate can also be stitched in case design demands .
I feel col free space as planned shall be retained , but all is as per Arch / owner requirements.
logeshcivil
PostPosted: Thu May 19, 2022 12:24 pm    Post subject: STRENGTHENING OF BEAMS Reply with quote
Dear vikram
Instead of providing plates at webs can i provide it at the bottom of the beam.
If so what should be the thickness of the plate and how do i design the anchor details for example dia of anchors, spacing of anchors and depth to be embedded because i haven't had  exposure to this kind of design.
And also please tell me which should i strengthen for deflection control.