Posted: Sat May 21, 2022 7:31 am Post subject: Local Thickening of Raft |
|
|
Dear Members,
Following are the features of Raft, as per design:-
RAFT DIM - 58M x 33M.
Thickness - 800MM, satisfying displacement & SBC criteria.
Local Thickening required because :-
1. The flexure Reinforcement demand for design Strip is very high approx. 12000mm2/m (Although it's peak).
2. Shear Value for Strip it is showing failure.
The dimension of this local thk Raft would be 22M x 12M.
3. We think, increasing overall depth of raft would be uneconomical.
following are the queries:-
If we need to increase the depth of raft locally,
1. what should be appropriate:-
a. increase thickness above base Raft.(pic attached)
b. increase thickness below base Raft.
2. Structural & Construction wise, which option is better?
3. Please provide reinforcement detailing for both the options, it would be of gr8 help.
Kindly guide.
Description: |
|
Filesize: |
867.02 KB |
Viewed: |
21 Time(s) |

|
|
|
Back to top |
|
 |
vikram.jeet General Sponsor

Joined: 26 Jan 2003 Posts: 3469
|
Posted: Sat May 21, 2022 8:32 am Post subject: |
|
|
Advantages & disadvantages of two options :
Thickening at top :
Excavation easy since one level
Extra excavation to accommodate top thickening - if basement exist otherwise no extra
But there will be additional cost of sand filling at top to achieve basement floor level in caSe of basement , otherwise if no basement - no such expenditure.
Bottom thickening :
EXCAVATION to be precise to accomodate thickenings.
Both options are in practice
|
|
Back to top |
|
 |
vikram.jeet General Sponsor

Joined: 26 Jan 2003 Posts: 3469
|
Posted: Sat May 21, 2022 9:07 am Post subject: |
|
|
Just to add
Reinforcement detailing will be easy for top thickening .Since bottom bars require continuity and bottom mesh reinf bars are of larger dia than top bars.
For bottom thickening , bars need to be bent to shape .
|
|
Back to top |
|
 |
spsvasan ...

Joined: 18 Dec 2008 Posts: 360
|
Posted: Sun May 22, 2022 2:58 am Post subject: |
|
|
If membrane water proofing is being planned, it will be better to have the bottom surface in one level