Saurabh Raj SEFI Member
Posted: Fri Oct 14, 2022 9:43 am Post subject: IS 1893-2016. Cl. 7.12.3 |
Hope you are doing well.
Clarification needed for IS 1893-2016. Cl.7.12.3 for seismic effect on compound wall/Boundary wall. In my case there is boundary wall with retaining wall(With 2.5m soil retaining)
IS-1893 says that 'Ah' shall be considered for 1.25Z with I=1 and R=1 which is 3times of IRC-06 (Design of retaining wall for seismic effect) whereas, in IRC-6-2017 Cl. 214.1.2.1, Ah shall be considered Z/2 and even in IIT commentary (IITK GSDMA EQ05-V4.0, GSDMA EQ15-V3.0) it is recommended that Ah=Z/2 Cl 7.14.3.
Now, 1. what shall I consider in my design.
2. what is the reference of IS-1893 cl 7.12.3.
3. Is compound wall and boundary wall same.
Your response will be much helpful.
Thanks & Regards,
Saurabh Raj |
Posted: Fri Oct 14, 2022 12:40 pm Post subject: |
The design horizontal seismic coefficient Ah = (Z/2)*(Sa/g)*(I/R)
As per this clause boundary walls / compound walls to be designed
using I =1.0 ; R=1.0 ; Sa/g = 2.5
Putting these values Ah works out = 1.25 Z
Compound walls are free standing vertical cantilever structures .
For free vertical projections above roof tops , the Ah value is five times . ( also for horizontal cantilever projections at any floor Av*5 to be taken).
Yes , the 1.25 Z value amounts to a eq static force = 0.3g in Zone 4
In case of roof top vertical projections on a building with I=1.0 , R= 5.0 (ductile detailing) , it works out to ,
Ah = 5[( Z/2) *(1/5)*2.5] = 1.25*Z
But for Load bearing masonry Buildings , the value of Ah for free standing projections is still more since R =2.5 (masonry with rcc bands and corner bars) I.e
Ah = 5[Z/2 * (1.0/2.5) *2.5) = 2.5 *Z
(To be continued) |
Posted: Fri Oct 14, 2022 4:41 pm Post subject: |
As regards query:
Compound wall is boundary wall .
However retaining wall is retaining structure which needs to be designed under seismic condition using higher Earth pressure coefficient than normal non seismic case.
In yr case Compound wall is retaining wall (retains earth) in lower 2.5 m but a boundary wall exist on it , above .
It is better to adopt :
Ah= 1.25 Z for portion of wall acting as free standing boundary wall portion
Ah = (Z/2)*(1.0/2.5)* 2.5 = 0.5 Z for retaining wall portion
( R Value for rcc abutment wall is taken 2.5) |
Posted: Wed Nov 23, 2022 11:28 am Post subject: |
Sir your justification well explained is very clear to me.
Further, can I get the reference of ( R Value for rcc abutment wall is taken 2.5)
Thanks for your support |
Posted: Wed Nov 23, 2022 1:46 pm Post subject: |
May pl refer IRC 6 where for R value is given in table
Masonry/ pcc abutment R= 1.0
RCC abutment R = 2.5 ( without Ductile Detailing)
And R = 3.0 ( with DD) |