IS 1893-2016. Cl. 7.12.3

 
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI Web Site Problems/ Login/Registration Issues
View previous topic :: View next topic  
Author Message
Saurabh Raj
SEFI Member
SEFI Member


Joined: 14 Oct 2022
Posts: 4

PostPosted: Fri Oct 14, 2022 9:43 am    Post subject: IS 1893-2016. Cl. 7.12.3 Reply with quote

Dear All,

Hope you are doing well.

Clarification needed for IS 1893-2016. Cl.7.12.3 for seismic effect on compound wall/Boundary wall. In my case there is boundary wall with retaining wall(With 2.5m soil retaining)
IS-1893 says that 'Ah' shall be considered for 1.25Z with I=1 and R=1 which is 3times of IRC-06 (Design of retaining wall for seismic effect) whereas, in IRC-6-2017 Cl. 214.1.2.1, Ah shall be considered Z/2 and even in IIT commentary (IITK GSDMA EQ05-V4.0, GSDMA EQ15-V3.0) it is recommended that Ah=Z/2 Cl 7.14.3.
Now, 1. what shall I consider in my design.
        2. what is the reference of IS-1893 cl 7.12.3.
        3. Is compound wall and boundary wall same.
Your response will be much helpful.

Thanks & Regards,
Saurabh Raj
Back to top
View user's profile Send private message
vikram.jeet
General Sponsor
General Sponsor


Joined: 26 Jan 2003
Posts: 3903

PostPosted: Fri Oct 14, 2022 12:40 pm    Post subject: Reply with quote

The design horizontal seismic coefficient  Ah = (Z/2)*(Sa/g)*(I/R)

As per this clause boundary walls / compound walls to be designed
using I =1.0   ; R=1.0  ; Sa/g = 2.5

Putting these values  Ah  works out = 1.25 Z

Compound walls  are free standing vertical cantilever structures .


For free vertical  projections above roof tops , the Ah value is five times . (  also for horizontal cantilever  projections at any floor Av*5 to be taken).

Yes , the 1.25 Z value amounts to a eq static force  = 0.3g in Zone 4

In case of    roof top vertical projections  on a  building with  I=1.0 ,  R= 5.0 (ductile detailing) ,  it works out to ,

Ah = 5[( Z/2) *(1/5)*2.5] = 1.25*Z

But for Load bearing masonry Buildings ,   the value of Ah for free standing projections  is still more since R =2.5  (masonry  with rcc  bands and corner bars) I.e
Ah =  5[Z/2  * (1.0/2.5) *2.5) = 2.5 *Z

(To be continued)
Back to top
View user's profile Send private message
vikram.jeet
General Sponsor
General Sponsor


Joined: 26 Jan 2003
Posts: 3903

PostPosted: Fri Oct 14, 2022 4:41 pm    Post subject: Reply with quote

As regards query:

Compound wall is boundary wall .

However  retaining wall is retaining structure which needs to be designed under  seismic condition using higher Earth pressure coefficient  than normal non seismic case.

In yr case  Compound wall is retaining wall (retains earth) in lower 2.5 m  but  a boundary wall exist on it , above .

It is better to adopt  :

Ah= 1.25 Z for portion of wall acting as free standing boundary wall portion

Ah = (Z/2)*(1.0/2.5)* 2.5 = 0.5 Z for retaining wall portion
( R Value for  rcc abutment wall is taken 2.5)
Back to top
View user's profile Send private message
Saurabh Raj
SEFI Member
SEFI Member


Joined: 14 Oct 2022
Posts: 4

PostPosted: Wed Nov 23, 2022 11:28 am    Post subject: Reply with quote

Sir your justification well explained is very clear to me.

Further, can I get the reference of ( R Value for  rcc abutment wall is taken 2.5)

Thanks for your support
Back to top
View user's profile Send private message
vikram.jeet
General Sponsor
General Sponsor


Joined: 26 Jan 2003
Posts: 3903

PostPosted: Wed Nov 23, 2022 1:46 pm    Post subject: Reply with quote

May pl refer IRC 6 where for R value is given in table

Masonry/ pcc abutment  R= 1.0

RCC abutment  R = 2.5  ( without Ductile Detailing)
And R = 3.0  ( with DD)
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI Web Site Problems/ Login/Registration Issues All times are GMT
Page 1 of 1

 

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You cannot download files in this forum


© 2003, 2008 SEFINDIA, Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service. advertisement policy