Guidance on High Mast Lighting Pole - Analysis and Design.

 
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion
View previous topic :: View next topic  
Author Message
rohitbabje123
SEFI Member
SEFI Member


Joined: 17 Mar 2023
Posts: 1

PostPosted: Fri Mar 17, 2023 9:43 am    Post subject: Guidance on High Mast Lighting Pole - Analysis and Design. Reply with quote

Dear Fellow Members,

I want to design a 30m high mast lighting pole for Indian site conditions. I request you to guide me/ give reference book/code. I searched on the internet but could not get solid reference which could guide me. I referred IS 875(3):2015 but I am not getting clarity from it. Whether we can adopt it for high mast or not. Also code states that special literature shall be referred for dynamic response to wind loads. Your guidance over it will be helpful for me and appreciable too. Thank you.
Back to top
View user's profile Send private message
vikram.jeet
General Sponsor
General Sponsor


Joined: 26 Jan 2003
Posts: 3927

PostPosted: Sat Mar 18, 2023 3:19 am    Post subject: Reply with quote

Pl refer earlier postings on High mast foundation design,,

You can also use equivalent static forces from wind on High Mast structure and work out Moments at bottom of Mast,, sd well as bottom of Footing.
A spread footing,, square shape,  needs tk be provided at about 2.5 to 3.0m below GL with earth weight on footing protected from scourage, if any,, since it the weight of earth mainly together with self wt of footing,, stabilizing,,
Size of SQ footing must be adequate to ensure sufficient wt over it providing required Factor of safety against Overturning,, Sliding,, and Max Base pressures within permitted range of gross SBC AND upliftment of footing on Minimum pressure side not more than 67%.
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion All times are GMT
Page 1 of 1

 

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


© 2003, 2008 SEFINDIA, Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service. advertisement policy