er.saurabhrshah General Sponsor
Joined: 04 Jan 2011 Posts: 38 Location: Ahmedabad, Gujarat
Posted: Wed Nov 09, 2011 8:23 pm Post subject: Staad pro v8i error in calculating earthquake forces |
Hello everybody, I recently checked the earthquake forces in staad by manual method and found that the earthquake forces generated by staad pro v8i are exactly half of what it should be.
After trial and error, I found that while we are giving parameters for earthquake it asks us for damping ration in percentage (Which should be 5% for concrete usually) but instead in calculations it takes 500% damping and as per IS 1893 Part 1:2002
If the damping value exceeds 30% earthquake forces are to be reduced to half.
So, for correct earthquake forces instead of 5% we need to give 0.05% in parameters for damping ratio and then all the forces are correct.
If same problem is being encountered by SEFI members then please specify or if i am doing something wrong then also please comment. |
Thankful People |
Naveen U Gunagi(07-01, 10:21), Thanks er.saurabhrshah for his/her post
rehan_nayeem SEFI Member
Posted: Thu Nov 10, 2011 7:22 am Post subject: EQ |
Hi Saurabh
Yes the damping ratio in staad has to be given as DM 0.05.
Rehan |
P.K.Mallick General Sponsor
Joined: 14 Dec 2008 Posts: 1098 Location: Kanpur. p.k.mallick1962@gmail.com
Posted: Thu Nov 10, 2011 8:01 am Post subject: Re: Staad pro v8i error in calculating earthquake forces |
This is a problem in STAAD PRO 2007 also. The damping ratio has to be 0.05 both in STAAD PRO V8I and STAAD PRO 2007. _________________ P.K.Mallick