Design Loads: Foundation

 
This forum is locked: you cannot post, reply to, or edit topics.This topic is locked: you cannot edit posts or make replies.    www.sefindia.org Forum Index -> Past Discussions Year 2004
View previous topic :: View next topic  
Author Message
mc.upadhyay1
...
...


Joined: 26 Jan 2003
Posts: 134

PostPosted: Thu Sep 02, 2004 6:54 am    Post subject: Design Loads: Foundation Reply with quote

Hello
There are significant moments for foundations (if considered fixed)
in Eq. condition; due to lateral loads. Mostly this condition governs the
design of foundation due to more moment and less axial load.
Chances of the foundation; loosing the contact are there in these
cases only.

If the column-foundation joint is considered to be pinned;
chances are the DL+LL condition may govern the design.

Regards





ibarua@deguild.c                                                                                                
om                       To:      mc.upadhyay@jil.co.in                                                          
cc:                                                                                    
09/02/04 06:35           Subject: Daily Digest Wed Sep  1 23:00:03 2004                        
AM                                                                                                              
Please respond                                                                                                  
to general                                                                                                      






02 September, 2004

Re.: Design loads
------------

IS:1893 prescribes reduction of live loads during Eq. condition. For
example, no LL is to be considered on the roof. On floors, reduced LL
depending on the classs of LL is prescribed. This is based on the
assumption that max. LL and Eq. condition will not act together at the same
time. In view of this, I don't think the reductions prescribed in IS:875
will govern design, insofar as design for Eq. condition is concerned.

Indrajit Barua.

Posted via Email
Back to top
View user's profile Send private message
Display posts from previous:   
This forum is locked: you cannot post, reply to, or edit topics.This topic is locked: you cannot edit posts or make replies.    www.sefindia.org Forum Index -> Past Discussions Year 2004 All times are GMT
Page 1 of 1

 

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You can attach files in this forum
You can download files in this forum


© 2003, 2008 SEFINDIA, Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service. advertisement policy