I have a beam of depth 600mm which the bottom 100mm was hacked and recast to achieve 500mm depth.
The main rebars were cut and replanted to the column supports at a higher position.
The shear links however, the bottom loop was cut and was not reinstated. So now the links are in an invert 'U' shape (bottom main bars not looped by links). Kindly see attached beam section.
Will the beam still be effective in shear? Your valuable input would be highly appreciated.
Thank you very much
Niresh.
Links with no legs.pdf
 Filename:  Links with no legs.pdf
 Filesize:  9.09 KB
 Downloaded:  140 Time(s)
mjnasar
PostPosted: Wed Dec 26, 2018 6:44 am    Post subject: Reply with quote
Yes, As per AcI -314M14
Vs = Av *fyt * d
only Av*d of shear stirrups resists the Shear
and the reinforcement along the breadth only extended for development requirements
hope it will be useful for you.
Pages Aci318-2014.pdf
 Filename:  Pages Aci318-2014.pdf
 Filesize:  81.62 KB
 Downloaded:  106 Time(s)
niresh28
PostPosted: Wed Dec 26, 2018 10:31 am    Post subject: Reply with quote
Vs = Av *fyt * d
Thank you so much mjnasar. Your input has been very helpful. I will study the above and the related codes.
Thank you very much.
Niresh
abhio
PostPosted: Mon Dec 31, 2018 12:55 pm    Post subject: Dangerously wrong practice. Reply with quote
Dear Er Niresh,
Without the bottom run, the shear links won't be able to develop full stress, and will be ineffective. Also, bottom bars won't be able to develop dowel action. The concept of leaving stirrups without anchorage is dangerously wrong and a disaster waiting to happen.
Hope seniors on this forum could see this post.
niresh28
PostPosted: Wed Jan 02, 2019 10:30 am    Post subject: Re: Dangerously wrong practice. Reply with quote
abhio wrote:
Dear Er Niresh,
Dear Abhio,
Thank you for your valuable input. I would like to provide an update. We found out at site that there are excess length of link sufficient to wrap around the bottom rebar across the width of beam. We have also welded the locations where the link free ends lap each other.