Posted: Tue May 10, 2016 3:19 am Post subject: Error in Staad file |
|
|
Dear all,
I have modelled a building in staad 2006 and have followed the procedures of applying load in conventional manner.
I have also applied the seismic loads, unfortunately I am not able to run the file. I am getting an error write check soft story. even though I have written I am not able to run the file.
Help me to run the file
Thank you |
|
Back to top |
|
|
AmitD SEFI Regulars
Joined: 19 Mar 2009 Posts: 21
|
Posted: Wed May 11, 2016 8:40 am Post subject: |
|
|
Hi
You need to define the Floor Heights before the definition of 1893 load and also the "check soft storey" command is to be placed at the end of the 1893 weight definitions.
The modified file is attached.
You can also use the Rigid Diaphragms to have more accurate results. |
|
Back to top |
|
|
AmitD SEFI Regulars
Joined: 19 Mar 2009 Posts: 21
|
Posted: Wed May 11, 2016 8:54 am Post subject: |
|
|
Sir,
I understand that this particular forum "SEFI Web Site Problems / Login/Registration Issues" is not a proper forum to address such engineering issues. May I request the Admin to move this thread to a proper forum. Sorry for the inconveniences. |
|
Back to top |
|
|
peednas_r SEFI Member
Joined: 07 Oct 2011 Posts: 5
|
Posted: Wed May 11, 2016 3:27 pm Post subject: |
|
|
Thank you Amit |
|