A simple question about steel section properties
Robert.Nicolson at Sub...
Guest
PostPosted: Fri Nov 26, 2004 9:25 am    Post subject: A simple question about steel section properties Reply with quote
Dear Rudra, and Prof Kalyanraman,
thanks you for your useful contributions.
I am writing a spreadsheet program that works out
the section properties for a plate girder.
And was interested to know whether it was valid
to use plastic neutral axis for angles.
( I will leave the user to decide this ! )
My feelings were that you can only use these
values for bending, if :-
1) the section was compact
2) the section bends in the orthogonal directions
Thanks, Rob.
-----Original Message-----
Message From  rudra_nevatia@yahoo.com [mailto:rudra_nevatia@yahoo.com]
Sent: 26 November 2004 10:51
To: Robert Nicolson
Subject: A simple question about
Dear Prof. Kalyanraman,
Very interestingly, 'Theory of Plasticity' by J.
Chakrabarty gives orientation of plastic neutral axes
as
tan alpha1
= 2b^2/(a^2+2ab-b^2) and
tan alpha2
2a^2(1+(tan alpha2)^2)-(a+b)^2
2b^2(1+(tan alpha2)^2)-(a+b)^2.tan^2alpha2
where
2a     = length of leg along y axis
2b     = length of leg along z axis
alpha1 = angle between pna1 and z axes
alpha2 = angle between pna2 and y axes
pna    = plastic neutral axis
So, in general plastic neutral axes are not
orthogonal. Chakrabarty refers to the plastic neutral
axes as strong and weak principal axis of plastic
bending, a terminology I beg to differ from.
If the angle is constrained to bend along y or z axis
only, I suppose the neutral axis will be parallel to z
or y axis respectively and very close to the legs for
equal angles.
Prof. Trahair's paper 'Moment Capacities of Steel
Angle Sections' available at
http://www.civil.usyd.edu.au/publications/r809.pdf
deals with this topic.
Rudra Nevatia
--- kalyan@civil.iitm.ernet.in wrote:
Plastic neutral axis are calculated by equating
total area in tension to
be equal to the total area under compression about
the two principal
axes, which in the case of equal angles are UU nad
VV axes.
Kalyanaraman
rudra_nevatia@yahoo.com wrote:
Intutively, for an equal leg angle, plastic neutral
axes should be located close to the legs.
Rudra Nevatia
--- Robert.Nicolson@Subsea7.com wrote:
Can someone plese tell me whether an angle, i.e. a
L
shape has a plastic
neutral axis.
Because I have just used a program which gave me
Zpl,x & Zpl,y ( second
moment of areas ),
as both equal to 0, for an angle ?
Take Yahoo! Mail with you! Get it on your mobile
phone.
http://mobile.yahoo.com/maildemo
========powered by Reach1to1 Office
Everywhere
Yahoo! Mail - Helps protect you from nasty viruses.
Everywhere
