In refinery, we are going for blastproof control room. It is made with RCC wall with minimum of opening. The entrance should be made indirect to ensure that if there is blast near the entrance, it should not affect the control room inside resulting safety to the equipment & personnel inside the room. A detail design procedure is available in CALTEX STANDARD, Volume-VIII.I think there is BIS also but No. I don't remember, can anybody please give the same.
Regards,
AK Sinha Ray. Senior Project Manager (E&C), Indian Oil Corporation Limited, 4th Floor, Core - 2, Scope Complex, 7, Institutional Area, Lodhi Road, New Delhi - 110003.
Ph. : 011 - 24306142. Fax : 011 - 24360978.
-----Original Message----- Message From vikram.jeet@jil.co.in [mailto:vikram.jeet@jil.co.in] Sent: Wednesday, December 29, 2004 6:05 PM To: SINHARAYAK@iocl.co.in Subject: Daily Digest Tue Dec 21 23:00:02 2004
For Blast resistant Design , as a pesonal view
i) Roomm should have RCC walls / ( Brick + RCC) walls
ii) Roof slab shall have Double mesh reinforcement ie Top & Bott
iii) Slab Reinf shall be anchored into walls for full D/Length
iv)Preferrablly Roof slab shall have more fill at top in form of lime conc/ mud phuska to reduce the impact of explosion
v) RCC walls along with 230 th brick work on inside is preferrable to reduce the impact.