sub: IS 16700/2017

 
This forum is locked: you cannot post, reply to, or edit topics.This topic is locked: you cannot edit posts or make replies. Thank Post    www.sefindia.org Forum Index -> E-conference on IS 16700 13th March to 18th March 2018
View previous topic :: View next topic  
Author Message
k.gangadharan
General Sponsor
General Sponsor


Joined: 01 Apr 2008
Posts: 204

PostPosted: Sat Mar 17, 2018 6:55 am    Post subject: sub: IS 16700/2017 Reply with quote

NECESSITY for an EXPLANATORY part to Is 16700 / 2017

 
In IS codes 1893/2016, 13920/2016 and IS 875 part 3 /2015 and the new code 16700/2017,  most of the provisions are inter connected. Some of the clauses in 16700 is confusing with the provisions of the other codes mentioned above .

Generally speaking ,therefore,  in my opinion,  an explanatory addition to 16700/2017 , in the form of a Special publication,is necessary , interpreting the various clause to understand this new code  fully ,and adapt for practical application.

CLAUSE 9.4 , depth of foundation

It is stated that the ebedded depth of foundation, shall be the least of  1/5 of the ht. of bldg. in RAFT foundation and 1/20 of the ht of bldg for piled & piled Raft buildings.

If you examine some of the already constructed tall bldgs , this clause is not observed .

For example Burg Khalifa  in Dubai is 828 m high bldg and It is on a piled raft foundation; the pile cap is 3.7 m thick & the piles are 150mm dia and 43 m long and there are 193  such piles & they are not found on rock and is found on dense sandAand supported in the naturally cement cancisiltite conglomeric formations. As per per Cl. 9.4 this building must have an embedment of 828/ 20 embedment length i.e 42 meter below ground level. This  means that this building should have a min: of 10 or 12 floors below gr. level. Actually It has a few parking floors.

If you examine some of the other tall buildings already constructed elsewhere also, this is not a requirement . In my  opinion 1/15 & 1/20 is not a relevant figure for embedment legth and it may not be practical to provide such length in tall & supertall buidings.


Another important requirement in Tall Buildings is DAMPERS. 

This aspect has not been mentioned or highlighted in this code.

In almost all tall builngs, already constructed ,different types of dampers have been used to reduce drift ,lateral deflection and vibrations due to dynamic wind loads.

There are positive Visco Elastic dampers, Tuned Mass dampers, Sloshing Warer Damoers, Tuned Liquid Dampers and Simple Pedulum dampers. Most of the Tall & super tall bldgs. already constructed have  used one or other types of dampers.

This aspect needs inclusion in the new code.

thanks & regards

Gangadharan.k

structural consultant

 

Posted via Email
Back to top
View user's profile Send private message
Indra Nath Mishra
SEFI Member
SEFI Member


Joined: 22 Dec 2016
Posts: 4

PostPosted: Sat Mar 17, 2018 8:05 am    Post subject: sub: IS 16700/2017 Reply with quote

Dear Sir, FYI & N/A pls.





Regards,
I.N.Mishra





On Saturday, 17 March, 2018, 12:52:22 PM IST, k.gangadharan <forum@sefindia.org> wrote:




           NECESSITY for an EXPLANATORY part to Is 16700 / 2017


In IS codes 1893/2016, 13920/2016 and IS 875 part 3 /2015 and the new code 16700/2017, most of the provisions are inter connected. Some of the clauses in 16700 is confusing with the provisions of the other codes mentioned above .

Generally speaking ,therefore, in my opinion, an explanatory addition to 16700/2017 , in the form of a Special publication,is necessary , interpreting the various clause to understand this new code fully ,and adapt for practical application.

CLAUSE 9.4 , depth of foundation

It is stated that the ebedded depth of foundation, shall be the least of 1/5 of the ht. of bldg. in RAFT foundation and 1/20 of the ht of bldg for piled & piled Raft buildings.

If you examine some of the already constructed tall bldgs , this clause is not observed .

For example Burg Khalifa in Dubai is 828 m high bldg and It is on a piled raft foundation; the pile cap is 3.7 m thick & the piles are 150mm dia and 43 m long and there are 193 such piles & they are not found on rock and is found on dense sandAand supported in the naturally cement cancisiltite conglomeric formations. As per per Cl. 9.4 this building must have an embedment of 828/ 20 embedment length i.e 42 meter below ground level. This means that this building should have a min: of 10 or 12 floors below gr. level. Actually It has a few parking floors.

If you examine some of the other tall buildings already constructed elsewhere also, this is not a requirement . In my opinion 1/15 & 1/20 is not a relevant figure for embedment legth and it may not be practical to provide such length in tall & supertall buidings.


Another important requirement in Tall Buildings is DAMPERS.

This aspect has not been mentioned or highlighted in this code.

In almost all tall builngs, already constructed ,different types of dampers have been used to reduce drift ,lateral deflection and vibrations due to dynamic wind loads.

There are positive Visco Elastic dampers, Tuned Mass dampers, Sloshing Warer Damoers, Tuned Liquid Dampers and Simple Pedulum dampers. Most of the Tall & super tall bldgs. already constructed have used one or other types of dampers.

This aspect needs inclusion in the new code.

thanks & regards

Gangadharan.k

structural consultant

Posted via Email
Back to top
View user's profile Send private message
Pulkit Velani
SEFI Member
SEFI Member


Joined: 16 Jan 2014
Posts: 11

PostPosted: Sat Mar 17, 2018 9:59 am    Post subject: Re: sub: IS 16700/2017 Reply with quote

Dear Sir,

With due respect I would like to say regarding CL 9.4: The point you raised might be valid or need discussion, however, the example given by you for Burj Khalifa is not valid since maximum height of building consider as per IS 16700:2017 is 250 m only. Hence maximum embedded depth coming to be: Raft=16.6m (H/15) and Pile=12.5m(H/20).  

regards,
Pulkit

k.gangadharan wrote:
NECESSITY for an EXPLANATORY part to Is 16700 / 2017

CLAUSE 9.4 , depth of foundation

It is stated that the ebedded depth of foundation, shall be the least of  1/5 of the ht. of bldg. in RAFT foundation and 1/20 of the ht of bldg for piled & piled Raft buildings.

If you examine some of the already constructed tall bldgs , this clause is not observed .

For example Burg Khalifa  in Dubai is 828 m high bldg and It is on a piled raft foundation; the pile cap is 3.7 m thick & the piles are 150mm dia and 43 m long and there are 193  such piles & they are not found on rock and is found on dense sandAand supported in the naturally cement cancisiltite conglomeric formations. As per per Cl. 9.4 this building must have an embedment of 828/ 20 embedment length i.e 42 meter below ground level. This  means that this building should have a min: of 10 or 12 floors below gr. level. Actually It has a few parking floors.

If you examine some of the other tall buildings already constructed elsewhere also, this is not a requirement . In my  opinion 1/15 & 1/20 is not a relevant figure for embedment legth and it may not be practical to provide such length in tall & supertall buidings.



thanks & regards

Gangadharan.k

structural consultant



Posted via Email
Back to top
View user's profile Send private message
ssankaran
SEFI Member
SEFI Member


Joined: 26 Dec 2009
Posts: 8

PostPosted: Sat Mar 17, 2018 4:21 pm    Post subject: sub: IS 16700/2017 Reply with quote

Well said. Embedment depth can only be suggestive and not mandatory.S Sankaran


On 17-Mar-2018 12:50 PM, "k.gangadharan" <forum@sefindia.org (forum@sefindia.org)> wrote:
Quote:
           NECESSITY for an EXPLANATORY part to Is 16700 / 2017

 
In IS codes 1893/2016, 13920/2016 and IS 875 part 3 /2015 and the new code 16700/2017,  most of the provisions are inter connected. Some of the clauses in 16700 is confusing with the provisions of the other codes mentioned above .

Generally speaking ,therefore,  in my opinion,  an explanatory addition to 16700/2017 , in the form of a Special publication,is necessary , interpreting the various clause to understand this new code  fully ,and adapt for practical application.

CLAUSE 9.4 , depth of foundation

It is stated that the ebedded depth of foundation, shall be the least of  1/5 of the ht. of bldg. in RAFT foundation and 1/20 of the ht of bldg for piled & piled Raft buildings.

If you examine some of the already constructed tall bldgs , this clause is not observed .

For example Burg Khalifa  in Dubai is 828 m high bldg and It is on a piled raft foundation; the pile cap is 3.7 m thick & the piles are 150mm dia and 43 m long and there are 193  such piles & they are not found on rock and is found on dense sandAand supported in the naturally cement cancisiltite conglomeric formations. As per per Cl. 9.4 this building must have an embedment of 828/ 20 embedment length i.e 42 meter below ground level. This  means that this building should have a min: of 10 or 12 floors below gr. level. Actually It has a few parking floors.

If you examine some of the other tall buildings already constructed elsewhere also, this is not a requirement . In my  opinion 1/15 & 1/20 is not a relevant figure for embedment legth and it may not be practical to provide such length in tall & supertall buidings.


Another important requirement in Tall Buildings is DAMPERS. 

This aspect has not been mentioned or highlighted in this code.

In almost all tall builngs, already constructed ,different types of dampers have been used to reduce drift ,lateral deflection and vibrations due to dynamic wind loads.

There are positive Visco Elastic dampers, Tuned Mass dampers, Sloshing Warer Damoers, Tuned Liquid Dampers and Simple Pedulum dampers. Most of the Tall & super tall bldgs. already constructed have  used one or other types of dampers.

This aspect needs inclusion in the new code.

thanks & regards

Gangadharan.k

structural consultant

 
     



     



Posted via Email
Back to top
View user's profile Send private message
dipak_bhattacharya
...
...


Joined: 18 Jun 2011
Posts: 76

PostPosted: Sun Mar 18, 2018 1:15 pm    Post subject: sub: IS 16700/2017 Reply with quote

Dear moderators,

Whether depth of embedments have been appropriately defined in the new code IS 16700.


Though , in case of Raft foundations, embedments may be upto bottom of raft, what should be depth of embedment for buildings based on piled foundations, whether it should be upto bottom of pile caps or upto the ends pf pile lengths.


Regards,


Dipak Bhattacharya / Delhi.


On 17 March 2018 at 12:50, k.gangadharan <forum@sefindia.org (forum@sefindia.org)> wrote:
Quote:
           NECESSITY for an EXPLANATORY part to Is 16700 / 2017

 
In IS codes 1893/2016, 13920/2016 and IS 875 part 3 /2015 and the new code 16700/2017,  most of the provisions are inter connected. Some of the clauses in 16700 is confusing with the provisions of the other codes mentioned above .

Generally speaking ,therefore,  in my opinion,  an explanatory addition to 16700/2017 , in the form of a Special publication,is necessary , interpreting the various clause to understand this new code  fully ,and adapt for practical application.

CLAUSE 9.4 , depth of foundation

It is stated that the ebedded depth of foundation, shall be the least of  1/5 of the ht. of bldg. in RAFT foundation and 1/20 of the ht of bldg for piled & piled Raft buildings.

If you examine some of the already constructed tall bldgs , this clause is not observed .

For example Burg Khalifa  in Dubai is 828 m high bldg and It is on a piled raft foundation; the pile cap is 3.7 m thick & the piles are 150mm dia and 43 m long and there are 193  such piles & they are not found on rock and is found on dense sandAand supported in the naturally cement cancisiltite conglomeric formations. As per per Cl. 9.4 this building must have an embedment of 828/ 20 embedment length i.e 42 meter below ground level. This  means that this building should have a min: of 10 or 12 floors below gr. level. Actually It has a few parking floors.

If you examine some of the other tall buildings already constructed elsewhere also, this is not a requirement . In my  opinion 1/15 & 1/20 is not a relevant figure for embedment legth and it may not be practical to provide such length in tall & supertall buidings.


Another important requirement in Tall Buildings is DAMPERS. 

This aspect has not been mentioned or highlighted in this code.

In almost all tall builngs, already constructed ,different types of dampers have been used to reduce drift ,lateral deflection and vibrations due to dynamic wind loads.

There are positive Visco Elastic dampers, Tuned Mass dampers, Sloshing Warer Damoers, Tuned Liquid Dampers and Simple Pedulum dampers. Most of the Tall & super tall bldgs. already constructed have  used one or other types of dampers.

This aspect needs inclusion in the new code.

thanks & regards

Gangadharan.k

structural consultant

 
     



     



Posted via Email
Back to top
View user's profile Send private message
Display posts from previous:   
This forum is locked: you cannot post, reply to, or edit topics.This topic is locked: you cannot edit posts or make replies. Thank Post    www.sefindia.org Forum Index -> E-conference on IS 16700 13th March to 18th March 2018 All times are GMT
Page 1 of 1

 

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You cannot download files in this forum


© 2003, 2008 SEFINDIA, Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service. advertisement policy