load combinations considering earth pressure on basement walls

 
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion
View previous topic :: View next topic  
Author Message
aditya
...
...


Joined: 05 Apr 2008
Posts: 159

PostPosted: Sat Jan 12, 2019 12:11 pm    Post subject: load combinations considering earth pressure on basement walls Reply with quote

Dear Dr. N. Subramanian, Eng. S. Arun Kumar, Eng. S. Jayakumar and fellow Sefians,
I am confused about the load combinations to be used for the modelling, analysis and design of RC Buildings with basement walls. In such cases, the basement walls constructed between RC columns of the frame will have earth pressure acting all the time. IS 1893 Part 1 does not give the list of load combinations or load factors to be used in which earth pressure is included. My queries are:
1) Shall we use load combinations listed below:

1.5*Dead Load+1.5* Earth Pressure+1.5*Live Load
1.2*Dead Load+1.2* Earth Pressure+1.2*Live Load+/-1.2 EQ
0.9*Dead Load+0.9* Earth Pressure+/-1.5 EQ
1.5*Dead Load+1.5* Earth Pressure+/-1.5 EQ

2) Will earth pressure acting on walls contribute towards seismic weight or not:
3) Load combinations indicated in (1) above will affect columns in superstructure also. Is this logical? How to carry out the overall 3d modelling of the building
with regards to all,
Aditya
Back to top
View user's profile Send private message
es_jayakumar
General Sponsor
General Sponsor


Joined: 24 Nov 2011
Posts: 1205
Location: Cochin

PostPosted: Sun Jan 13, 2019 2:07 pm    Post subject: Reply with quote

Dear Er.Aditya,


I guess, the Earth Pressure being an almost permanent load, we have to consider it as a Dead Load acting in the horizontal direction. In that case, the Load Combinations indicated by you shall hold good.

Earth Pressure may not contribute to seismic weight, I hope. You may use Dynamic Active Earth Pressure for the calculation of horizontal load on the basement wall under seismic conditions. Reference may be made to the attached article and the book "Analysis and Design of Substructures" by Swami Saran.
The lateral (dynamic) EP will induce additional moments in the basement columns to which the RCC basement retaining walls are connected, which will necessitate increased reinforcement in them. This may not affect the columns in superstructure much, I think.
Experts may please throw more light on this.

Best wishes,
E.S.Jayakumar



Warning: Make sure you scan the downloaded attachment with updated antivirus tools  before opening them. They may contain viruses.
Use online scanners
here and here to upload downloaded attachment to check for safety.
Geotechnical Earthquake.pdf
 Description:

Download
 Filename:  Geotechnical Earthquake.pdf
 Filesize:  1.53 MB
 Downloaded:  112 Time(s)

Back to top
View user's profile Send private message
Display posts from previous:   
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion All times are GMT
Page 1 of 1

 

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


© 2003, 2008 SEFINDIA, Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service. advertisement policy