Posted: Sat Mar 23, 2019 7:30 am Post subject: Seeking inputs on your experience of 2016 editions of IS 1893 Pt 1 and IS 13920 |
|
|
Dear Shri Duregesh Rai,
I had drawn attention regarding the amplificationb factor of 1.5 which has been included in draft provisions of IS:1893-2016 which was earlier not adopted in IS:1893-2002 with the amendment no.1 Jan2005 as Note 2. Attached herewith pdf of Doc. comments which I sent to BIS at that time to drop this clause for 3D dynamic analysis.
Regards,
SUNIL GANDHI
Structural Engineer,
108 Amrut Commercial Centre,
Sardarnagar Main Road,
Rajkot. 360001
Gujarat(India)
Mobile : +919825147661
Office : +912812467661
E-mail : suniljgandhi@gmail.com (suniljgandhi@gmail.com)
Posted via Email
Warning: Make sure you scan the downloaded attachment with updated antivirus tools before opening them. They may contain viruses. Use online scanners here and here to upload downloaded attachment to check for safety.
|
Description: |
|
Download |
Filename: |
Doc_commnets.pdf |
Filesize: |
106.2 KB |
Downloaded: |
215 Time(s) |
|
|
Back to top |
|
|
Bivek SEFI Member
Joined: 02 Oct 2013 Posts: 2
|
Posted: Sat Mar 23, 2019 5:30 pm Post subject: Seeking inputs on your experience of 2016 editions of IS 1893 Pt 1 and IS 13920 |
|
|
Dear Sir,
I have a doubt regarding clause 7.11 of IS 1893:2002.
Does the deformation mentioned there also apply to the deflections calculations as per IS 456?
An official explanatory / commentary documents from BIS is strong felt necessary for both the revised versions of 1893 and 13920.
On Sat, Mar 23, 2019, 10:16 PM sjgandhi <forum@sefindia.org (forum@sefindia.org)> wrote:
Quote: | Dear Shri Duregesh Rai,
I had drawn attention regarding the amplificationb factor of 1.5 which has been included in draft provisions of IS:1893-2016 which was earlier not adopted in IS:1893-2002 with the amendment no.1 Jan2005 as Note 2. Attached herewith pdf of Doc. comments which I sent to BIS at that time to drop this clause for 3D dynamic analysis.
Regards,
SUNIL GANDHI
Structural Engineer,
108 Amrut Commercial Centre,
Sardarnagar Main Road,
Rajkot. 360001
Gujarat(India)
Mobile : +919825147661
Office : +912812467661
E-mail : suniljgandhi@gmail.com (suniljgandhi@gmail.com) (suniljgandhi@gmail.com (suniljgandhi@gmail.com))
Download Attachments:
Doc_commnets.pdf
|
Posted via Email
|
|
Back to top |
|
|
nykochak SEFI Regulars
Joined: 26 Jan 2003 Posts: 25
|
Posted: Mon Mar 25, 2019 10:30 am Post subject: Seeking inputs on your experience of 2016 editions of IS 1893 Pt 1 and IS 13920 |
|
|
R/s,
Please share your comments regarding exact meaning & interpretation of the issues mentioned below.
IS 1893-2017 Part I
1. Cl. no. 6.3.2.2 - orthogonal & non orthogonal criteria of lateral load resisting
elements
2. Cl. no. 6.3.3.1.e & f - criteria of long spans & large overhangs
3. Cl. no. 6.4.2 - (Z / 2) why divided by 2 ?
4. Values for shear walls and slabs have not been specified in Cl. no. 6.4.3.1
but specified in IS 16700. Why ?
5. Cl. no. 6.4.6 in relation with cl. 7.7.3.b ? Why X or Y direction EQ
is correlated with vertical EQ ? What about time period in Z direction ?
How to specify vertical EQ with out going for shell assignment to slabs ?
Why R is used ?
6. Cl. no. 7.1 & 7.11.1.2 - For which load case or load combination ? Whether
1.5 x deflection minimum is related to angle of rotation ? Whether it is prudent
to relate the same with length of the building since angle of rotation changes
as per length of the building ?
7. Fig. 3C-2 is inevitable in cities and unavoidable. How to address the same ?
8. Whether floating columns / transfer girders are permitted if they are not part of lateral
load resisting system ?
9. Aw in time period formula specified in 7.6.2.b needs modification ?
10. Whether inter storey height governs formula of time period say 3.0 m in
residential buildings and 6.0 m in industrial buildings ?
11. How to calculate CR to address Cl. 7.6.4 ? It will require two iterations
if to be calculated manually to satisfy Cl. 7.8.2.
12. Whether for height less than 15 m separate design and detailing code is
recommended ?
13. It is cumbersome to address Cl. 7.9 and to model struts. Any other way ?
14. Cl. no. 7.10.4 is a bit tricky. If one building is 10 floors having 40 m x 40 m
plan dimensions and other is 25 floors with same dimensions then wall density
is same for both i.e. 40 m x 40 m x 2/100 = 32 m2.
15. Cl. no. 7.11.3 Why R/2 ?
16. Whether lateral storey stiffness depends on plan dimensions if size and no. of
columns in two directions are same ?
17. How to derive R factor for composite structure i.e. RC columns + Steel roof,
RC slab on first floor and covered with steel roof at second floor etc. ?
18. Table 9 - 3 c - R is 4 and 4 d - R is 5 ? How to distinguish when response of the
system depends on % od ductile structural shear walls ?
19. Whether any frame that is treated as gravity frame will be subjected to lateral loads
and will fail ? It is difficult to detail and execute pin joint in practice.
With regards,
N. Y. Kochak
Posted via Email
|
|
Back to top |
|
|
nykochak SEFI Regulars
Joined: 26 Jan 2003 Posts: 25
|
Posted: Tue Mar 26, 2019 10:30 am Post subject: Seeking inputs on your experience of 2016 editions of IS 1893 Pt 1 and IS 13920 |
|
|
R/s,
Please share your comments regarding exact meaning & interpretation of the issues mentioned below.
IS 13920-2016
1. Whether it is possible to amend the clauses for single / two
storey wherein 90 % population of the country is living in ?
2. Cl. no. 5.4 - Difficult to comply in industrial structures
3. Cl. no. 6.1.1, Cl. no. 6.1.2 & Cl. no. 6.1.3 - concept behind this clauses
4. Cl. no. 6.2.6.1 c - Due to these clauses lap locates at centre in many situations
or couplers has to be mandatory. Whether staggering is necessary ?
5. Cl. no. 6.2.6.2 - Whether couplers are permitted in zone defined by Cl. no. 6.2.6.1.c ?
6. As per Cl. no. 7.2 it is necessary to design & detail a structure in totality.
No changes can be entertained at a later stage. Whether factor 1.4 can be lowered ?
7. Cl. no. 7.3.2.1.d - Whether 100 % bars can be lapped in one floor height ?
8. Cl. no. 8.1.c - Whether only spirals are sufficient or cross loops are required ?
9. Cl. no. 9.1.3 - 20 db criteria applicable to shear walls ?
10. Cl. 10.1.2 - needs to be related to height of the floor
11. Cl. 10.1.3 - Additional criteria to define shear wall is necessary ?
12. Cl. 10.1.4.c - Up to what slenderness ration Table 1 cane be used ? and thereafter ?
13. Cl. no. 10.3.1. - Whether shear wall needs to be designed for biaxial bending ?
14. Cl. 10.4.4.a, b, & c - are creating conflicting scenario
15. Cl. no. 10.4 - What should be sizing of boundry element ?
16. Cl. no. 10.4.3 - Whether reinforcement permitted needs reduction ?
17. Cl. no. 10.6 - Desirable & undesirable locations of openings ?
18. Cl. no. 10.8.3.3 & 10.8.4 - needs further clarification
19. Cl. no.11 - Gravity means pinned at both ends ? How to ignore their contribution in
the analysis if not pinned / released ? If pinned how to construct ?
With regards,
N. Y. Kochak
On Mon, Mar 25, 2019 at 3:40 PM NARAYAN KOCHAK <nykochak@gmail.com (nykochak@gmail.com)> wrote:
Quote: | R/s,
Please share your comments regarding exact meaning & interpretation of the issues mentioned below.
IS 1893-2016 Part I
1. Cl. no. 6.3.2.2 - orthogonal & non orthogonal criteria of lateral load resisting
elements
2. Cl. no. 6.3.3.1.e & f - criteria of long spans & large overhangs
3. Cl. no. 6.4.2 - (Z / 2) why divided by 2 ?
4. Values for shear walls and slabs have not been specified in Cl. no. 6.4.3.1
but specified in IS 16700. Why ?
5. Cl. no. 6.4.6 in relation with cl. 7.7.3.b ? Why X or Y direction EQ
is correlated with vertical EQ ? What about time period in Z direction ?
How to specify vertical EQ with out going for shell assignment to slabs ?
Why R is used ?
6. Cl. no. 7.1 & 7.11.1.2 - For which load case or load combination ? Whether
1.5 x deflection minimum is related to angle of rotation ? Whether it is prudent
to relate the same with length of the building since angle of rotation changes
as per length of the building ?
7. Fig. 3C-2 is inevitable in cities and unavoidable. How to address the same ?
8. Whether floating columns / transfer girders are permitted if they are not part of lateral
load resisting system ?
9. Aw in time period formula specified in 7.6.2.b needs modification ?
10. Whether inter storey height governs formula of time period say 3.0 m in
residential buildings and 6.0 m in industrial buildings ?
11. How to calculate CR to address Cl. 7.6.4 ? It will require two iterations
if to be calculated manually to satisfy Cl. 7.8.2.
12. Whether for height less than 15 m separate design and detailing code is
recommended ?
13. It is cumbersome to address Cl. 7.9 and to model struts. Any other way ?
14. Cl. no. 7.10.4 is a bit tricky. If one building is 10 floors having 40 m x 40 m
plan dimensions and other is 25 floors with same dimensions then wall density
is same for both i.e. 40 m x 40 m x 2/100 = 32 m2.
15. Cl. no. 7.11.3 Why R/2 ?
16. Whether lateral storey stiffness depends on plan dimensions if size and no. of
columns in two directions are same ?
17. How to derive R factor for composite structure i.e. RC columns + Steel roof,
RC slab on first floor and covered with steel roof at second floor etc. ?
18. Table 9 - 3 c - R is 4 and 4 d - R is 5 ? How to distinguish when response of the
system depends on % od ductile structural shear walls ?
19. Whether any frame that is treated as gravity frame will be subjected to lateral loads
and will fail ? It is difficult to detail and execute pin joint in practice.
With regards,
N. Y. Kochak
|
Posted via Email
|
|
Back to top |
|
|
|
|