IS IT POSSIBLE TO PROVIDE BOTH PILE FOUNDATIONS AND ISOLATED FOOTINGS IN A MIXED FASHION FOR A BUILDING?
renju mathew
PostPosted: Tue May 21, 2019 4:47 am    Post subject: IS IT POSSIBLE TO PROVIDE BOTH PILE FOUNDATIONS AND ISOLATED FOOTINGS IN A MIXED FASHION FOR A BUILDING? Reply with quote
I just want to know, whether it is possible to provide both pile foundation and isolated footings in a mixed fashion for a two storey Residential building?
SBC of soil is just 70kN/m2 for 1.2m wide Isolated footing and Pile foundations can bear upto 750KN load.
There are about 25 column. The column loads are ranging from 150kN to 730kN.  I found that a few columns come within the range for Isolated footings. and a few can only be supported over pile foundation.
Client can't afford the expense of 25 piles.
Thanks in Advance
R Mathew
abhio
PostPosted: Wed May 22, 2019 7:01 am    Post subject: Reply with quote
Dear Er Matthew,
Pile foundations will be substantially stiffer (in general) than spread footings, and will attract a larger share of load. This will result in your assumed load paths being disturbed - unless you carry out a proper soil-foundation-structure interaction analysis.
Hence, I would recommend that you ought not to mix piles and spread footings in the same structure.
sjgandhi
PostPosted: Wed May 22, 2019 11:30 am    Post subject: IS IT POSSIBLE TO PROVIDE BOTH PILE FOUNDATIONS AND ISOLATED FOOTINGS IN A MIXED FASHION FOR A BUILDING? Reply with quote
Dear Mathew,
If both pile foundatiion and spread footing system adopted simultaneously , the building will rest on different mass with different soil parameters which requires care of differential settlement in design of foundation and superstructure.
In the event of eathquake and wind effects, the superstructure of building may vibrate with different frequencies and amplitudes on account of different soil mass through which seismic wave propagates and transmitted to superstructure via foundations. This may create non uniform drift of the storeys at different levels under earthquake effects which may ultimately trigger distresses in rcc members after and during earthquakes.
It is advisable to separate the building in two or three parts with separate foundations and superstructure with a separation joint wherever required.
SUNIL GANDHI
Structural Engineer,
108 Amrut Commercial Centre,
 Sardarnagar Main Road,
 Rajkot. 360001
 Gujarat(India)
 Mobile : +919825147661
 Office  : +912812467661
 E-mail : suniljgandhi@gmail.com (suniljgandhi@gmail.com)
Anunay_Jain
PostPosted: Thu May 23, 2019 12:16 pm    Post subject: Reply with quote
Dear Er Matthew,
You can try to go for a mat foundation or a grid type of foundation. That would be an economical option compared to some deep foundation (pile) and some isolated ones.
If you can share the loads and the structural file with me, I can help you with designing a grid type of foundation (mat with openings at some places to save material).
Thanks,
Anunay Jain
Senior Undergraduate Student
IIT (BHU) Varanasi
rojanmathewtsy
PostPosted: Fri May 24, 2019 9:04 am    Post subject: Re: IS IT POSSIBLE TO PROVIDE BOTH PILE FOUNDATIONS AND ISOLATED FOOTINGS IN A MIXED FASHION FOR A BUILDING? Reply with quote
renju mathew wrote:
Thanks in Advance
R Mathew
Dear Renju Mathew,
I think you can go with this type of foundation if you tie the isolated footings with pile foundation using rigid beams. That may limit the difference in settlement. But u should do the proper analysis to check the load flow through the rigid beam. Simply connecting the two foundation using beam  without any calculations may leads to errors. Other wise the best option will be the raft foundation.
Rojan Mathew
mandeep_singh_kohli
PostPosted: Wed May 29, 2019 12:03 pm    Post subject: Re: IS IT POSSIBLE TO PROVIDE BOTH PILE FOUNDATIONS AND ISOLATED FOOTINGS IN A MIXED FASHION FOR A BUILDING? Reply with quote
Dear renju,
I do not concur with the views that this is not  possible and also do not concur wit the view that you have to provide grid beams to take care of differential settlement ( that will be catastrophic).
The building can be supported on two different foundation systems, but those two foundation systems and buildings need to be isolated. You will have to isolate the foundations completely and also isolate the structures. You may have to give flexible connections between the buildings or sliding connections to account for unequal drift.
Seismic load paths, like any other lateral load path will have to be separated for both the portions.
Alternatively, you may go for Stone column foundation system which will be much cheaper than piled foundations, and can offer great savings.
renju mathew wrote:
Thanks in Advance
R Mathew
renju mathew
PostPosted: Fri May 31, 2019 10:19 am    Post subject: Reply with quote
Anunay_Jain wrote:
Dear Er Matthew,
Thanks,
Anunay Jain
IIT (BHU) Varanasi
The N value is less than 5.
Please give me your EMAIL ID
ramprasad e
PostPosted: Sat Jun 01, 2019 9:47 am    Post subject: Reply with quote
Dear Safin,
Both the foundations can not mix in one structure due to differential settlement ,however you can provide the expansion joint between the pile
foundation and spread footing.
Best Regards,
Ramprasad enugula
spsvasan
PostPosted: Sat Jun 08, 2019 3:13 am    Post subject: Re: IS IT POSSIBLE TO PROVIDE BOTH PILE FOUNDATIONS AND ISOLATED FOOTINGS IN A MIXED FASHION FOR A BUILDING? Reply with quote
Dear Er.R.Mathew
The mixing of deep foundation and shallow foundation shall be avoided
Even if a separation joint is provided between the portions with deep foundation and portions with shallow foundation, the difference in settlement will introduce difference in floor levels and this is not acceptable
For a two storeyed building a properly designed mat foundation should be feasible
Economics of ground improvement may also be investigated
S.P.Srinivasan
renju mathew wrote:
Thanks in Advance
R Mathew
Yogesh.Pisal
PostPosted: Tue Jun 18, 2019 9:40 am    Post subject: Reply with quote
Dear Renju,
Considering two stories and 25 columns, I presume that you will be having lighter loads for peripheral columns. Hence isolating building to account for differential settlement may not be possible.
I will suggest to go for soil treatment (e.g. stone piles) to improve SBC and use open foundations for all columns.
Best Regards,
Yogesh Pisal