LINAC BUNKER / RADIATION BUNKERS

 
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion
View previous topic :: View next topic  
Author Message
husseins20
...
...


Joined: 25 Apr 2013
Posts: 62

PostPosted: Mon Apr 12, 2021 1:00 pm    Post subject: LINAC BUNKER / RADIATION BUNKERS Reply with quote

Dear Sefinians,

can someone please enlighten on the Analysis and Design of Bunkers which are used ofr Radiation purpose.

Is there any special requirements to be considered in the Design?

I undersatnd that:-

1. Wall and Floor Thickness of approx 1500mm to 2000mm or above is required for shielding purpose

2. The thickness of wall and floor is a requirement from the Physisist or Radiologist who calculates the emission of radiation and its half life etc.

3. Would the above thickness have any implication on the structure?

Since the wall thickess are such large the reinforcement requirement would be bare minimum sa 0.4%.

Kindly advise if above undersatnign and is coorect and if someone has encountered these bunkers.

rgds

Badri
Back to top
View user's profile Send private message
pvgraju
...
...


Joined: 07 Jun 2020
Posts: 66

PostPosted: Wed Apr 14, 2021 9:47 am    Post subject: LINAC BUNKER/RADIATION BUNKER Reply with quote

Dear Sir,

This type of structures requires detailed FEM analysis for stress,strain,vibration due to vehicles,earthquake,wind load etc. After evaluating these this reinforcement to be provided as per requirements. High end analysis techniques are required for these types of structures.


Regards,

P.V.Gavarraju
Back to top
View user's profile Send private message
abhio
...
...


Joined: 08 Mar 2010
Posts: 547

PostPosted: Tue May 04, 2021 9:57 am    Post subject: Reply with quote

Dear Sir,

Depending upon the radiation level, the client may specify heavy concrete (made with iron ore or even steel shot as coarse aggregate). Depending upon the type of structure, seismic loads to be considered may be extremely high, and blast load or other accidental load (Main Steam Line Break / Loss Of Coolant Accident) may have to be considered. This can result in very heavy reinforcement even in spite of thick sections.

Regards,

A S Oundhakar
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion All times are GMT
Page 1 of 1

 

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


© 2003, 2008 SEFINDIA, Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service. advertisement policy