Posted: Mon Jun 14, 2021 3:53 pm Post subject: Minimum bar curtailment length in two way Post-Tensioned Flat System as per ACI 318 or IS Code! |
|
|
Hi Fellow Engineers, I have a query on the above mentioned topic.
ACI 318-19, Fig. 8.7.4.1.3 shows the minimum extension lengths for two way (non-PT) flat slab system. (i.e., 0.33ln & 0.20 ln). Similarly IS code requires 0.33ln & 0.25ln)
Would the same extension lengths apply for two-way PT Flat slab system? If no, can anyone help with the ACI clause suggesting about it. Design is being carried out in ADAPT Builder 2019!
Thanks in advance!! |
|
Back to top |
|
 |
vikram.jeet General Sponsor

Joined: 26 Jan 2003 Posts: 3706
|
Posted: Tue Jun 15, 2021 3:36 am Post subject: |
|
|
ANALYSIS IS UNIVERSAL
DESIGN IS NATIONAL
DETAILING IS PERSONAL
MODELLING NEEDS TO BE IDEAL
Since design has to be carried as per The specific Country Code where such structure is to be constructed, for Indian sites, you need to follow IS Code recommendations.
Earlier IS 456 version for general slabs recommended 0.3L ,0.20L but 1978 code revised to 0.3 and 0.25. |
|
Back to top |
|
 |
vikram.jeet General Sponsor

Joined: 26 Jan 2003 Posts: 3706
|
Posted: Tue Jun 15, 2021 6:45 am Post subject: |
|
|
For PT slabs, please also see guidelines in 19.6 of IS 1343 , regarding transmission length. |
|
Back to top |
|
 |
pvgraju ...

Joined: 07 Jun 2020 Posts: 66
|
Posted: Thu Jun 17, 2021 3:38 am Post subject: Minimum bar curtailment length in two way Post-Tensioned Flat System as per ACI 318 or IS Code! |
|
|
Dear Sir,
Post tensioning can be done for bottom bars since bottom bending will be dominant in slabs. PT will make slab econimical. Generally top bending will be less ,it can be designed like a RC element with 0.3L extension.
These extension lengths are minimum lengths specified in the code. At 0.3l top bending will be zero. So top reinforcement is not needed after that. In case of PT also bending moment values will be same. So extension will be same.
Regards,
P.V.Gavarraju. |
|
Back to top |
|
 |
vikram.jeet General Sponsor

Joined: 26 Jan 2003 Posts: 3706
|
Posted: Sun Jun 20, 2021 4:16 am Post subject: |
|
|
For Cantilever Slabs , the hogging moment at top may require higher top bars reinforcement embedment length at back slab . Generally it needs to be around 2*L , where L is cantilever span of slab projection. This length takes care of situation ( Full LL on cantilever & No LL on back slab) |
|
Back to top |
|
 |
|
|