Regarding Column Reinforcement

 
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion
View previous topic :: View next topic  
Author Message
ramu_se
...
...


Joined: 30 Oct 2017
Posts: 111

PostPosted: Mon Aug 07, 2023 7:51 am    Post subject: Regarding Column Reinforcement Reply with quote

Dear All,
In columns, we get more axial load and less moments on the lower floor, less axial force, and more moments on the upper floors. While providing the reinforcement, can we provide less reinforcement on the lower floors and more reinforcement on the upper floors by keeping the same size of the column throughout the floor? Which is an economical solution?
Thanks & Regards,
Ramu.
Back to top
View user's profile Send private message
va
...
...


Joined: 26 Jan 2003
Posts: 93

PostPosted: Tue Aug 08, 2023 6:30 am    Post subject: Regarding Column Reinforcement Reply with quote

You can provide more reinforcement in the column at the top floor level.

 
Hemant Vadalkar.
Consulting Engineer Mumbai

Posted via Email
Back to top
View user's profile Send private message
sakumar79
...
...


Joined: 18 Apr 2008
Posts: 716

PostPosted: Tue Aug 08, 2023 9:25 am    Post subject: Reply with quote

Dear Sir,
    I would recommend keeping the higher steel required at upper floors in the lower floor also rather than increasing the reinforcement in upper floors. For one, it reduces the chance of confusion to contractor. More importantly, if the construction is unexpectedly halted at the lower level, the load and moment in that level will mimic the upper level of the completed structure and will require the higher steel quantity.

Yours sincerely
S Arunkumar
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion All times are GMT
Page 1 of 1

 

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


© 2003, 2008 SEFINDIA, Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service. advertisement policy