Posted: Sun Jan 16, 2011 8:07 pm Post subject: Secondary beams: Horizontal or vertical |
|
|
Hello all,
See attached figure.
Here, some of the secondary beams are horizontal and some vertical.
My question is:
What is the criteria behind this? When should the secondary beams be vertical and when horizontal?
Any code rules/references will be useful.
Description: |
|
Filesize: |
133.79 KB |
Viewed: |
1178 Time(s) |
|
|
|
Back to top |
|
|
gpsarathyy ...
Joined: 28 Jun 2010 Posts: 487
|
Posted: Mon Jan 17, 2011 7:44 am Post subject: |
|
|
Dear Sefian,
The secondary beams are mainly provided to support the equipments/pumps or the gratings/chequered plates etc.,
The spacing and the direction are also governed by the same. In general for spanning the grating the spacing between the beams shall not exceed 1.2m c/c. If you exceed this span then you may have to go for next higher level grating.
Similarily for chequered plate also it is having some span constraint based on the thickness of chequered plate used and the loadings.
Its purely Engineers choice to arrange the secondary beams provided above are the constraints or which decides the arrangement.
I hope it clears your doubt.
Regards,
G.Parthasarathy.
Chennai
Email: GPSARATHYY@GMAIL.COM
|
|
Back to top |
|
|
nwalavalkar ...
Joined: 18 Nov 2010 Posts: 63
|
Posted: Thu Jan 20, 2011 7:28 am Post subject: |
|
|
System is symmetrical about axis joining J - 10.
Good arrangement. Less fabrication details.
Regards
|
|
Back to top |
|
|
gpsarathyy ...
Joined: 28 Jun 2010 Posts: 487
|
Posted: Thu Jan 20, 2011 8:30 am Post subject: |
|
|
Er. Vishal,
Have you satisfied with my reply, or still you need clarification on this?
Regards,
G.Parthasarathy
Chennai
Email: GPSARATHYY@GMAIL.COM
|
|
Back to top |
|
|
Vishal ...
Joined: 06 Aug 2008 Posts: 124
|
Posted: Thu Jan 20, 2011 10:42 am Post subject: |
|
|
Dear Er.Parthasarathy,
Thanks a lot for the reply and soorry for being late as I was in a place where internet is not accesible easily.
You said:
In general for spanning the grating the spacing between the beams shall not exceed 1.2m c/c. If you exceed this span then you may have to go for next higher level grating.
I did not follow the term 'next high level gratiing'.
What do you mean by next high level grating?
|
|
Back to top |
|
|
vikram.jeet General Sponsor
Joined: 26 Jan 2003 Posts: 3839
|
Posted: Sat Jan 22, 2011 10:30 am Post subject: Secondary beams: Horizontal or vertical |
|
|
Dear Er Vishal
Secondary beams
From the appended sketch:
The building has two blocks of similar size configuration and arrangement placed
orthogonal to each other.That is why secondary beams seem along X axis in one Block
and along Y axis in other Block.
Secondary beams are required to be introduced if rcc panels are large sized.
Providing large sized solid slab panels will consume heavy steel. Secondary beams reduce
the steel consumption.The concrete quatty may come at par including extra shuttering cost.
Secondary beams are provided resting on main beams.If functional needs donot
dictate, these are provided along short span of panel to break longer dimension
into smaller panels.
Provision of sec beams in industrial buildings is nicely explained by
Er G.Parathasarthy.
best regards
vikramjeet
-- ญญ
Posted via Email
|
|
Back to top |
|
|
gpsarathyy ...
Joined: 28 Jun 2010 Posts: 487
|
Posted: Tue Feb 01, 2011 1:58 am Post subject: |
|
|
Vishal,
Next higher level means, higher thickness grating.
Generally
25mm thick span for 1.2mc/c
30mm thick can span more than 1.2m etc.,
similarily
6 thick Chequered plate can span for 1m c/c
8 thick means it can span more
But all depends on the loading intensity and the allowable deflection criteria etc.,
Regards,
G.Parthasarathy
Chennai
GPSARATHYY@GMAIL.COM
|
|
Back to top |
|
|
Vishal ...
Joined: 06 Aug 2008 Posts: 124
|
Posted: Tue Feb 01, 2011 9:07 am Post subject: |
|
|
Dear Sir,
I don't get this; you said:
Generally
25mm thick span for 1.2mc/c
30mm thick can span more than 1.2m etc.,
What exactly you meant by 25mm thick span or 30 mm thick span?
Vishal
|
|